  1. #16
    Akums Razor.... the simplest solution. Checked via a meter and small light with dental mirror but could not see the cut in the insulation from the mounting screw through the box. Had one fixture still to go when it became apparent by adding the closest then the next fixture etc. when breaker tripped. Had previously replaced the breaker and meter checked all wiring for grounds before posting this item. Was sure it had something to do with a new type transformer, and not the circuit installation.
    Really appreciate the help and realizing that others, even with care, unknowingly cut insulation.
    Now to put it all back together and on with business.

  2. #17
    Yep that is a common mishap glad you found the problem.
    Ever wonder what happens if you get scared 1/2 to death twice ?

  3. #18
    Join Date
    Nov 2009
    Location
    Sinking Spring, PA
    Posts
    881
    [QUOTE=Chris Barnett;1462294]
    Really appreciate the help and realizing that others, even with care, unknowingly cut insulation.
    QUOTE]

    When I did it as mentioned earlier, I kinda left out the "with care" part!! I fastened the clamps on the metal box with an impact driver!! Thought I finessed it enough to not cause damage, but was obviously wrong there....lesson learned!!!

    Glad you found the problem, happy ww'ing to come now!