  1. #16
    I've got a 24 aggazani with single phase, and I usually give the top wheel a few spins to help it get going. It starts OK on a 30 amp breaker.

    I think that bandsaws are made for VFDs,

    Is your supply 220 single phase, and you are trying to run 380 V three phase? What is the nameplate info, volts, amps, hz?

    I was able to put a phase converter together for my table saw for just a few hundred dollars using a idler motor.

    None of the solutions are really all that complex, depending on your willingness to scrounge.

    My initial thought is to use a transformer to go form 220 to 440, then use a vfd to run the saw. The trick is that most 400 volt class drives are only rated for three phase supply. Some Hitachis allow the use of external dc supply, where you supply rectified filtered juice to a terminal on the drive.

  2. #17
    here is a good site for three phase info.


    http://www.practicalmachinist.com/vb/

  3. Quote Originally Posted by ian maybury View Post
    ....... or do they use Felder's VFD/dual voltage trick ....
    Ian, you mentioned VFD and "Dual Voltage" twice in your postings, so I thought I would comment on that. I believe you are confusing the versatility of a dual voltage motor with something functional with the VFD. A dual voltage motor simply means that its windings can be reconfigured for the various supply voltages it may see. In the U.S. for small single phase motors, this means the same motor can be configured for either 120 volts or 240 volts. 3-phase motors can also be dual voltage and can be configured between 208 and 480, for example.

    This is a static configuration and no VFD that I have heard of is capable of switching the configuration of the motor on-the-fly as your posting seems to suggest.

    As for your tool, at 5 hp, you are in the middle of the gray area where it might be more economical to use a VFD for phase conversion (3 hp and below) versus using a rotary converter (above 5 hp). Which method to choose will depend on the cost. VFD would be the better choice, but a 7 hp VFD (you need to oversize them at or above 5 hp) gets fairly expensive.
    Quote Originally Posted by Mike Cutler View Post
    Rick Christopherson, a member here on the board, has ( or used to have ) a really nice website for understanding electrical theory as applicable to the shop. It's in pretty straight forward terms. If he still has it up, it's a good read.
    Yes, I am still alive, and the information you mentioned is located at http://www.waterfront-woods.com/

  4. #19
    Join Date
    Aug 2009
    Location
    'over here' - Ireland
    Posts
    2,532
    I'm starting to think maybe pedals wouldn't be a bad option Peter! That's quite some start up current on the RAS, and it doesn't even have the big cast iron wheels of a bandsaw.

    Good to get another reference point on current draw on a 24in bandsaw Stephen. Thank you. Giving it a twirl isn't i think such a straightforward option for me as the saw is a Euro/UK model with an electrical and not a mechanical brake, but it tends to support the previous 40A number.

    Here are the motor plate details, there's a photo of the terminal box at the top of the thread:

    Seimec Modena CE
    IEC 34-1 ICL F
    IP 54 S1
    3 09709/07 03/07
    HFV 100LA 2 B5

    Brake:
    V06 13Nm 400V 0.2A RV1/50 178

    400V (delta)+/- 5%
    6.6A (could be 5.6)
    3kW
    2900 rpm
    Cos phi 0.77

    So far it seems it's a 400V delta only motor. i.e. it's not dual voltage, and so not suitable for an inverter drive.

    The rotary converters sold over here normally have voltage step up included to give the full 380/400v 3 phase output - they unfortunately are quite a bit more expensive here than in the US. (shipping one over is too costly to make it a good deal here though)

    I've superficially toyed with the DIY route, having seen that it's fairly straightforward - even for a mech eng. It could be a runner, and thanks for the links. One factor putting me off a little is that there seems to be a sense about that the good commercial units do some smart things to ensure that the third phase is not just a crude approximation. Do you think is this a real issue, or is it just smoke by the makers? Local electrical equipment approvals regulations are also possibly a factor.

    My post on Felder's approach should have said VFD and 220V three phase motor i guess Rick - a typo as i know (superficially anyway) about dual voltage motors. Re. my motor above i'd have bought an inverter drive by now if it was a 220/400V - the 4kW Omron/Yaskawa V-1000 model is available here at decent money. The problem is that adding a new motor brings it into the same cost territory or slightly more than a rotary. It would deliver the advantage of giving better control of the start up current though. Thanks for the link to your site.

    It's starting to look like it's a case of either pay up for new stuff (rotary or inverter and motor) now, or sit and wait for something used to come up, or go a DIY converter. With a single phase conversion in the background as probably feasible too....

    ian

  5. Quote Originally Posted by ian maybury View Post
    It's starting to look like it's a case of either pay up for new stuff (rotary or inverter and motor) now, or sit and wait for something used to come up, or go a DIY converter. With a single phase conversion in the background as probably feasible too....

    ian
    You don't need the dual voltage motor, you just add a simple single-phase step-up transformer to the input of the VFD (rated for the 400V input). Autotransformers (single coil with taps) are reasonably priced.

  6. #21
    Join Date
    Mar 2007
    Location
    Corvallis, OR
    Posts
    86
    Ian,

    I would recommend seriously looking at an adjustable (variable) frequency drive - at 5 hp, you can probably get a drive specifically designed to operate on a single-phase input and produce three-phase output. If that is not available, you can get an oversized three-phase drive and operate it with only one phase on the input side - it will still produce three-phase output.

    With an AFD, all issues related to starting current can be eliminated. The drive can be adjusted to ramp up the motor and never exceed the nameplate current.

    I'm not quite clear on the voltage question. A transformer can be placed ahead of the AFD if necessary. So replacing the motor should not be necessary.

  7. #22
    Quote Originally Posted by ian maybury View Post

    The rotary converters sold over here normally have voltage step up included to give the full 380/400v 3 phase output - they unfortunately are quite a bit more expensive here than in the US.



    It's starting to look like it's a case of either pay up for new stuff (rotary or inverter and motor) now, or sit and wait for something used to come up, or go a DIY converter. With a single phase conversion in the background as probably feasible too....

    ian
    I was looking at the stepup rotary convertier idea, but I think you would need a big idler motor-- it needs to absorb enough current to run the saw on one of the low voltage windings. Maybe something like 20 HP. I'm guessing that you would look at the high voltage current rating of the motor to see what it can handle one only one winding.

    The practical machinist site I referenced earlier has a conversion specific forum, they would eat this sort of thing up (lots of knowledge there)

    http://www.practicalmachinist.com/vb...onverters-vfd/

  8. #23
    Ian, I'm probably missing something but it seems like it would be easier and less expensive to just buy a single phase motor. I'm pretty sure you can get a 5hp one for about $500 USD.

  9. #24
    Join Date
    Aug 2009
    Location
    'over here' - Ireland
    Posts
    2,532
    Rick, David. I'd love to go a VFD/inverter drive, but so far as i can see from the (UK) catalogues there's no single to three phase 400V input inverters available here.

    This is a typical listing from Omron: http://www.axiscontrols.co.uk/en-GB/...terprices.aspx (the makers don't sell the same VFD models here as in the US, and in fact there's only a couple one of which is Yaskawa/Omron doing 4kW single phase input models - most stop at 2.2KW)

    Also i'm being told by inverter suppliers like the above guys that i do need a dual voltage motor.

    There is one company selling inverters with voltage step up (presumably a transformer) to give 400V/3 phase, but they (a) cost the same as a rotary, and (b) are under heavy attack to the effect that they are not CE/regulations compliant, and that there are issues with the feeding of interference back into the mains. (see second post below) This could of course be smoke since it's mostly coming from their competition, but i've seen their rebuttal and they certainly avoid answering the question of whether or not they are compliant with the regs.

    That's just to set out the position i seem to have come to. I'm all ears regarding the possibility you both mention of placing a single phase transformer on the input of a 400V (3 phase?) VFD for the reasons you say. (soft start, speed control etc) Can you possibly explain a little more regarding how this works/is wired, and exactly what equipment is needed? Presuming it's possible does it entail any risks/problems/regulatory issues?

    I guess i have to wonder why the inverter makers are not selling voltage step up models over here as there's a definite market judging by what the rotary guys are offering, and what they are charging.

    Please pardon my coming back for second helpings...

    Thanks for the link Stephen. I'm getting a little behind on keeping up with the info i've been given now - i'll have to get reading over the weekend.

    Single phase seems like it's feasible Justin (the info tabled by some of the guys suggests that 40A cabling/breakers or a bit bigger since our voltage is a little lower should do the business with a 24in saw. I've been stalling so far on it though - (a) our incoming supply is unlike in the US fused at 80A by dictat of our service provider and runs our house as well, (b) it'd cost about the same as an inverter, (c) it involves modding the machine, (d) a three phase motor is probably a little more robust a drive - if i can find a way to swing it.

    ian
    Last edited by ian maybury; 09-03-2010 at 4:52 PM.

  10. #25
    Join Date
    Aug 2009
    Location
    'over here' - Ireland
    Posts
    2,532
    PS Warning by one (rotary converter) maker against buying step up inverters:

    POWER CAPACITORS LIMITED, 30 REDFERN ROAD, TYSELEY, BIRMINGHAM. B11 2BH
    © POWER CAPACITORS LIMITED 2009
    6
    ********* WARNING *********
    Electrical Products are covered by specific safety regulations.
    Ensure the products you propose to purchase are safe.
    MODIFIED INVERTERS OFFERING 415V 3-PHASE OUTPUT FROM 240 1-PHASE AND MOTOR CONTROL
    Manufacturers of Electrical Products have a legal responsibility to ensure their products bear CE marking if a
    company intends to sell such products in the European Union (EU) or member states of the European Economic area
    (EEA) - Iceland, Liechtenstein and Norway
    A CE mark is a manufacturer's claim that its product meets specified essential safety requirements set out in
    relevant European directives.
    The requirement for CE marking and the exact process a manufacturer will need to go through varies from product
    to product. Different types of product are governed by different European directives. Where an item of equipment
    is covered by more than one directive, it must be CE marked under all applicable directives.
    A range of “modified” single phase input inverters is available for sale on the internet, sometimes referred to as a
    “digital phase converter”. Unlike a standard inverter this type of equipment offers a 415v three phase output from
    a 240v single phase supply with the aforementioned motor control benefits.
    All inverter manufacturers offer products with a variable frequency output of 240v three phase from a 240v single
    phase supply. By limiting the output of these devices to a maximum of 3kW/4hp, manufacturers such as IMO,
    Mitsubishi, Omron, Teco, Eurotherm ABB and Siemens are able to sell CE marked equipment compatible
    with European Power Quality regulations.
    Digital Phase Converters are modified versions of three phase 415v input inverter products. Modified inverter
    products do not carry any warranty support from manufacturers of inverters and may require assessment/approval
    from your network operating company (i.e. the provider of your single phase electricity supply) prior to connection.
    The modified product has no CE Marking and therefore does not comply with EU EMC regulations. Tests on this
    equipment confirm that acceptable levels of emissions are exceeded and thus a CE mark cannot be applied
    • All TRANSWAVE Converters and IMO inverters are manufactured in a BS EN ISO9000:2000 Quality Assured
    Environment.
    • All TRANSWAVE Converters and IMO inverters are CE marked and comply with EMC Regulations, the Low
    Voltage Directive and BS EN ISO 61000-3-2:2006.
    • Certificates of Conformity are available from both Power Capacitors Limited and IMO plc.
    • NOT ALL PHASE CONVERTERS SOLD ON THE INTERNET ARE CE MARKED.
    • SOME PHASE CONVERTERS CARRY AN INVALID CE MARK AS THE EQUIPMENT HAS BEEN MODIFIED AND NO
    LONGER MEETS THE MANUFACTURER'S ORIGINAL SPECIFICATION.
    • EQUIPMENT THAT HAS BEEN MODIFIED SHOULD BE RE-CERTIFIED PRIOR TO SALE, NOT SIMPLY PUT BACK IN
    THE BOX AND RE-SOLD.
    • CE Certification and re-certification costs manufacturers such as IMO and Power Capacitors TENS OF
    THOUSANDS OF POUNDS - this is the cost of compliance.
    • BY LAW ALL ELECTRICAL PRODUCTS SHOULD CARRY A CE MARK - CONSUMERS ARE ENTITLED TO SEE A
    DECLARATION OF CONFORMITY FROM THE MANUFACTURER TO CONFIRM COMPLIANCE.
    • WE WOULD STRONGLY ENCOURAGE YOU TO SEEK WRITTEN CONFIRMATION OF SUCH COMPLIANCE PRIOR TO
    PURCHASE.
    Under the Sale of Goods Act 1979, all products must be "fit for purpose". This means that products must fulfil the
    purpose the customer has been led to expect and the reasons that led them to buy it. The Act also covers any
    purpose that a customer asks about when the product is purchased and is guaranteed by the retailer to meet that
    purpose when it is sold. If a product is not fit for purpose, the customer is within their rights to have the goods
    replaced or repaired.
    Power Capacitors Limited offers a service over and above the above requirements. We also offer a no-obligation
    money-back guarantee (less postage costs) assuming the product is returned to us in a state fit for resale.

  11. Ian,
    You're getting bad information from manufacturers, and some of it is simply badmouthing their competition.

    There is nothing about a standard VFD that requires a dual voltage motor. I suspect this is from a miscommunication. As I said previously, simply put a step-up transformer ahead of the VFD and use the existing motor. The words "dual voltage" should not be coming up in your discussions whatsoever.

    Oh, you are correct that you probably won't find a 400V single-phase VFD. That is still fine. You simply need to over-size the VFD to 7 hp. The reason why this is feasible is because the VFD takes the incoming AC power and converts it into DC power (like a battery) and then artificially generates the 3-phase output from this DC. So the only part of the VFD that cares about the incoming 1 or 3 phase is the rectifier. A 3-phase rectifier is more efficient than a single phase rectifier, so that is the reason for "de-rating" the VFD's output power.

    As for the CE listing, that vendor appears to be making more out of it than he needs to. Yes, the listing is good in that it means the device has been examined by an outside source. However, it is a VERY expensive process to go through and does not automatically mean a poor product if there is no CE listing--as long as it is a reputable company.

    For example, many of the Festool products you can buy in your country are not available to us in the U.S. simply because of the bureaucracy of the UL listing process here(similar to CE). The tools are no less safe, it is just bureaucracy.

    Does your bandsaw have a CE listing? Technically is should, but would you have not purchased it simply because it didn't? Probably not.

  12. #27
    Join Date
    Jan 2009
    Location
    Williamsburg,Va.
    Posts
    12,402
    When I planned my new shop,I had a 400 amp panel,separate from the house panel put in. Also had #6 wire run to where I might someday upgrade to a 10 h.p. metal lathe.

    At my last shop,funds were running low,so I skimped on electricity,which I regretted later. Always running around re-pluging things.

  13. #28
    Join Date
    Aug 2009
    Location
    'over here' - Ireland
    Posts
    2,532
    I do agree on the bad mouthing Rick, and have a similarly cautious attitude to the bureaucracy that much of this regulation beings - it seems to be mostly about jobs for the boys.

    That said a 7HP inverter over here is only available in three phase, and anyway costs about the same as a new 5hp rotary converter.

    I'm not sure what's going on over the dual voltage issue, but as before (a) it's absolutely clear that voltage step up inverters are not generally sold over here (it could be for marketing or regulatory rather than basic technical reasons), that (b) 4kW is the max single phase inverter normally available (presumably due to the 80A limit on domestic supplies i mentioned before) and (c) there's definitely a widely held view that a dual voltage 220/400V motor is required to enable the use of single phase inverters giving 200V 3 phase output. (that some three phase motors are not suitable for use this way)

    On the latter - I spoke to a rewinds outfit yesterday to see if they could set up my motor to run on an inverter, and they were adamant that the motor was not suitable based on the 400V delta listed on the plate.

    Despite this there's a conflicting few saying that any three phase motor can be connected to run perfectly well on 220V 3 phase too - but little hard information.

    I've arranged to have an experienced industrial electrician llok at the motor early next week, maybe he'll be able to clarify the position.

    ian

    PS George. I'm already thinking that maybe i should have bought a largish rotary converter to run my whole shop and bought 3 phase equipment, but that said 400A is simply not an option. Mains 3 phase power was in the meantime looking like costing approaching €10,000 to install, with ongoing annual charges resulting from it too.
    Last edited by ian maybury; 09-04-2010 at 2:23 PM.

  14. #29
    Join Date
    Jan 2009
    Location
    Williamsburg,Va.
    Posts
    12,402
    Ian. Not sure how it is over there,but over here I believe you have to have a minimum number of 3 phase motors in your shop to get 3 phase installed. I knew an old guy who had an open back basement workshop he could drag heavy lathes into. He used them and also sold them.

    He had a bunch of motors sitting around not being used,in order to meet the number of motors required. They didn't need to be in use,just in the shop.

    You may not need a real big converter to run your whole shop if you only use 1 machine at a time. I was looking at a 10 h.p. DSG lathe. The owner said he'd been running it on a 3 h.p. rotary converter. He wasn't doing heavy work,so was getting away with it. I wouldn't base your decisions on this info,though.
    Last edited by george wilson; 09-04-2010 at 3:17 PM.

  15. #30
    Join Date
    Nov 2003
    Location
    Katy, Texas
    Posts
    243
    Quote Originally Posted by Rick Christopherson View Post
    You don't need the dual voltage motor, you just add a simple single-phase step-up transformer to the input of the VFD (rated for the 400V input). Autotransformers (single coil with taps) are reasonably priced.
    Quote Originally Posted by Rick Christopherson View Post
    Ian,
    You're getting bad information from manufacturers, and some of it is simply badmouthing their competition.
    Rick hit it on the head.

    Mains input circuits are pretty basic for single-phase in/three-phase out inverters. Generally, either it is a purpose-built unit with a single-phase input rectifier, or it is a derated unit with a three-phase input rectifier potentially, though not always, using only 2/3 of the diodes. As compared to its full-rated sibling, the derated three-phase variety will have one less wire (or PCB trace on a small unit) on the input circuit, a different rating sticker, and potentially a software modification to allow for increased DC bus ripple. Inverters usually use single-phase control power derived from two of the three incoming mains. Warranty issues aside, in the case of a three-phase unit, if the third incoming leg has no specific current or voltage monitoring for fault purposes, it is almost certain that the inverter can be used in a derated, single-phase input scenario. You will need the help of the manufacturer's tech support line or a competent distributor or repair shop to confirm.

    Todd