Mike, the AC unit is about 13 years old, 2.5T, 10 SEER by Armstrong. Unfortunately after rechecking how this circuit runs, there is Romex from the panel through the attic, then out to a junction box at the ceiling. From there, it drops down the wall in conduit to the receptacle. I'll be re-running from the junction box out to the disconnect.
In the house, the circuit is currently a 30A breaker with 10ga romex to the disconnect where there are 25A fuses I think. Its raining so I'm not checking today.
(BTW, Ada/Ida, two different, oft confused places. DirecTV has twice scheduled our job right after someone in Ada. Unfortunately that one letter makes a 3 hour difference.
Grand Rapids area is a nice place to live though. Ada is better known so I get the short end of the stick)
Rollie, after I posted this I found some threads like the one you refered to which really confused me. But if I'm understanding correctly, the gist is that the wire is sized based on the min circuit ampacity, and then you can select a breaker based on the max overcurrent protection device? So as you are saying, you can actually use a 25A breaker on a 14g circuit, as crazy as it sounds? In that thread, the poster could actually have used a 50a breaker with a 10ga wire.
I see I can get a 25A breaker to fit my Siemens panel, which unfortunately is only available full-height so it it eats up the space that a current Q220220 breaker that provides 2 20A 220 volt circuits (one is unused currently) leaving me only a spare 15A 110 circuit out there but I guess that's life. Or I can get a triplex breaker with 2 15 or 20A 110's and the 25A 220. But I think I'll use what I've got for now and deal with it if I have problems with it tripping on hot days. Why the guy who built my house and shop chose such small panels I guess I'll never know.
Or can I get away with a larger breaker since the disconnect is fused and the breaker would only be providing short circuit protection to the wire between the panel and the disconnect?