Rob Russell
If the AHJ wants to get into derating of bundled NM, it's still not an issue until you have a lot of NM running through a single run of conduit.
From 334.80, "The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor." Using the 90 degree column and looking at Table 310.310.15(B)(2)(a) Adjustment Factors for More ThanThree Current-Carrying Conductors in a Raceway or Cable, you have to get more than 9 current carrying conductors bundled before derating becomes an issue for either #14 or #12. That means you can have (4) 14/2 or 12/2 NM through a conduit and - even with the 70% derating - you're still OK using 15 and 20 amp breakers respectively.
The issue here isn't whether or not the derating happens, it's whether or not the derating has any impact on the net ampacity of the circuit.