    Breaker size?

    What size breaker and wire do I need for a 3hp tablesaw?

  2. #2
    Join Date
    Sep 2010
    Location
    Buffalo, NY
    Posts
    60
    20 amp breaker with 12 gauge wire should be fine
    Brian E. Cosgrove

  3. #3
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    20A with 12 gauge... although personally I'd install a 30A with 10 gauge.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  4. #4
    Join Date
    Apr 2007
    Location
    Phoenix, AZ
    Posts
    1,417
    Same as Dan, 20A w/ 12 gauge, but I'd just run 10 gauge and use 30A instead. That "future growth" lesson has been learned by every guy to ever wire up his woodshop, no reason for you to re-learn it youself

    Here's a thread on motor wiring if you're interested in reading some NEC arcana to arrive at the same answer as above

    Sizing Wires and circuit breakers for 3HP and 5HP shop motor circuits
    Thread on "How do I pickup/move XXX Saw?" http://www.sawmillcreek.org/showthread.php?p=597898

    Compilation of "Which Band Saw to buy?" threads http://www.sawmillcreek.org/showthre...028#post692028

  5. #5
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    95
    "Here's a thread on motor wiring if you're interested in reading some NEC arcana to arrive at the same answer as above"

    I'll just go with what you guys said!

    Thanks everyone!

  6. #6
    I have a 20A with 12 gauge wire and every so often I will trip the breaker on start up, even though it says 18Amp max on the motor.
    Not allowed

  7. #7
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Derek,

    Could be a failing breaker... I've had some that were junk straight out of the box (even had a GFCI socket that was junk straight out... took me a while to figure that one out).
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  8. #8
    What voltage?

  9. #9
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    3 HP, I think we would agree it has to be 220 volt.
    I wired all my 220 plugs with 10 gauge, and 30 amp breakers. Wish I had run 8 guage to one of them on a 50 amp breaker for the welder, but I doubt it needs more than 30...if I ever learn to use it. Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  10. #10
    Join Date
    Jan 2007
    Location
    Davis, CA
    Posts
    278
    I ran 10 gauge wire for all my 220V except one line of 8 gauge with a 50A on it (future welder or some odd big electric draw). All of the 10 gauge have 20A breakers except the Dayton heater which has a 30A. If I ever get a machine with greater than 3 hp, then I can add 30A breakers on my 10 guage wire.

  11. #11
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Bernie May View Post
    I ran 10 gauge wire for all my 220V except one line of 8 gauge with a 50A on it (future welder or some odd big electric draw).
    If you ran individual THHN/THWN conductors in conduit, then you're fine. If you ran #8 NM cable and are in a jurisdiction that's using the 2008 NEC, your #8 is only rated for 40A.

  12. #12
    Quote Originally Posted by Rob Russell View Post
    If you ran individual THHN/THWN conductors in conduit, then you're fine. If you ran #8 NM cable and are in a jurisdiction that's using the 2008 NEC, your #8 is only rated for 40A.

    The requirement that NM cable be sized from the 60 degree column of table 310.16 predates the 2008 NEC by many code cycles, it was added that SER cable be sized at the 60 degree ampacity in the 2008 edition.