    6/3 Cable used as 6/2 - what to do with spare conductor?

    I need to run a short length (4 feet) of Romex 6/2 to a 240V 50A receptacle from my sub panel. This is for a 3-phase rotary converter.

    Inadvertently, I bought 6/3 cable, not 6/2. My options as I see them:

    1. Junk it, learn the lesson and buy some 6/2.
    2. Strip the insulation, cut the white conductor at both ends at the insulation, and presto, 6/2 red and black. In a long run, I wouldn't do this, the extra conductor might come in useful, but 4 feet from the sub panel, not so much. I'd rather not have a foot of "loose" 6ga cable in the panel.
    3. Cap the ends of the white wire and leave it intact. Still have the problem of a foot of cable inside the box though.

    What to do?

  2. #2
    "Saving" the white wire for something probably isn't practical because it's such a short piece of cable - I'd just cut it off (your option #2).

    Alternatively, parallel it up with one of the other wires. Won't hurt anything, and then you can save it without having it dangling around inside the box.

  3. #3
    Join Date
    Mar 2009
    Location
    Seabrook, TX (south of Houston)
    Posts
    3,093
    Blog Entries
    3
    +1 for #2

  4. #4
    Join Date
    Mar 2003
    Location
    Southport, NC
    Posts
    3,147
    I'm not an expert but I don't think you can do #2. I don't believe that the wires inside Romex are insulated or labeled for stand-alone use. Could be wrong.

    I think #3 is the best option. Just put a wire cap on each end, coil it up neatly and put it it a corner.
    Howie.........

  5. #5
    Join Date
    Dec 2007
    Location
    Battle Ground, WA.
    Posts
    594
    Mark
    Put a cap on both ends. Install a couple of plastic tie-wraps to hold white lead along edge of your box with the other neutrals. Tom

  6. #6
    Join Date
    Jan 2010
    Location
    LA & SC neither one is Cali
    Posts
    9,447
    #3 and I would label it just so nobody ever is confused.
    Of all the laws Brandolini's may be the most universally true.

    Deep thought for the day:

    Your bandsaw weighs more when you leave the spring compressed instead of relieving the tension.

  7. #7
    Quote Originally Posted by Howard Acheson View Post
    I'm not an expert but I don't think you can do #2. I don't believe that the wires inside Romex are insulated or labeled for stand-alone use. Could be wrong.

    I think #3 is the best option. Just put a wire cap on each end, coil it up neatly and put it it a corner.
    You definitely can't do #2 unless the conductors are individually labeled. For starters, 110.3B requires you install a product per the listing and labeling, and you wouldn't be doing that (there are other code provisions this violates, but let's start there :P).


    #3 is definitely the right option here.

  8. #8
    Join Date
    Jan 2010
    Location
    westchester cty, NY
    Posts
    796
    +1 for #3. if you ever need a neutral, it's right there. cap both ends. that's what the licenses do in my jurisdiction.

  9. #9
    Thanks guys. it turns out I can return the 6/3, and the job is now down with the correct 6/2.

  10. #10
    Join Date
    Jan 2007
    Location
    Davis, CA
    Posts
    278
    I have done this exact thing (maybe three feet from outlet to panel) by just pulling the fourth, unneeded wire out of the sheathing.