    It should also be mentioned that if the length of this raceway exeeds 24 inches, you must derate the ampacity of each conductor by a factor given in NEC table 310.15(B)(3)(a). As an example, where NM is installed, this would start causing problems with #12s at five 2 conductor cables (over 9 current carrying conductors), or with #10s at three 2 conductor cables (over 6 current carrying conductors). At 10 current carrying conductors, a #12 would need to be derated to 50% of 30 amps (15 amps), as per 90C column of 310.15(B)(16). At 7 current carrying conductors, the ampacity of a #10 must be derated to 70% of 40 amps (28 amps), as per the 90C column of table 310.15(B)(16). You would then be in violation by installing the #12s on a 20 amp breaker, or the #10s on a 30 amp breaker.
    Last edited by Matt Marsh; 07-22-2012 at 1:52 AM. Reason: additional info and clarification

  2. #17
    Quote Originally Posted by Matt Marsh View Post
    It should also be mentioned that if the length of this raceway exeeds 24 inches, you must derate the ampacity of each conductor by a factor given in NEC table 310.15(B)(3)(a). As an example, where NM is installed, this would start causing problems with #12s at five 2 conductor cables (over 9 current carrying conductors), or with #10s at three 2 conductor cables (over 6 current carrying conductors). At 10 current carrying conductors, a #12 would need to be derated to 50% of 30 amps (15 amps), as per 90C column of 310.15(B)(16). At 7 current carrying conductors, the ampacity of a #10 must be derated to 70% of 40 amps (28 amps), as per the 90C column of table 310.15(B)(16). You would then be in violation by installing the #12s on a 20 amp breaker, or the #10s on a 30 amp breaker.
    I think I did bring it up in post #3
    Building Inspector, CBO

  3. #18
    Join Date
    Dec 2011
    Location
    North-central Minnesota
    Posts
    318
    Scot,

    Why are you being so confrontational here? Do you feel threatened? Or what is the deal?

    Because this is common practice where you live, doesn't make it the best way, nor does it make it code compliant. Steve pointed out the clamping requirements earlier in the post, and your reply to him implied that he was incorrect, when in fact his answer was more accurate than yours was. The exception to clamping that you alluded to only applies to surface mounted enclosures, and only after all the conditions of a through g are met.
    Last edited by Matt Marsh; 07-22-2012 at 7:42 AM.

  4. #19
    Join Date
    Nov 2003
    Location
    Olathe Kansas
    Posts
    431
    My Dad told me severals years ago about electricity this; PAY YOUR BILLS ON TIME AND DON'T MESS WITH IT, IT CAN KILL YOU.
    Randy

    Don't worry abuot tommorrow, it may never arrive
    Don't fret over yesterdays mistake, you can't undo them
    Just live today the best you can.

  5. #20
    Join Date
    Dec 2011
    Location
    North-central Minnesota
    Posts
    318
    Quote Originally Posted by Randy Moore View Post
    My Dad told me severals years ago about electricity this; PAY YOUR BILLS ON TIME AND DON'T MESS WITH IT, IT CAN KILL YOU.
    Where is that "LIKE" button LOL.

  6. #21
    Quote Originally Posted by Matt Marsh View Post
    Scot,

    Why are you being so confrontational here? Do you feel threatened? Or what is the deal?

    Because this is common practice where you live, doesn't make it the best way, nor does it make it code compliant. Steve pointed out the clamping requirements earlier in the post, and your reply to him implied that he was incorrect, when in fact his answer was more accurate than yours was. The exception to clamping that you alluded to only applies to surface mounted enclosures, and only after all the conditions of a through g are met.

    Sorry, I didn't mean to come across as confrontational at all. As I posted above, it would be a good idea to check with his AHJ.
    Last edited by Scot wolf; 07-22-2012 at 10:30 AM.
    Building Inspector, CBO

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •