My new-to-me house has a central air system that isn't working very well. When I purchased the house I was told the temperature drop over the coil was about half of what it should be (about 8 degrees instead of 15). I was told that it was probably low on refrigerant.
I called an HVAC person out to take a look, they made sure the filter was clean, and that the coils on the compressor outside were clean. They checked the temperature drop and agreed that it might be low of refrigerant.
He hooked his manifold to the unit, and added two pounds. At that point, he said there was too much pressure on the pressure side. Actually, this is what the invoice says:
08/27/13: A/C NOT COOLING DUE TO LOW REFRIGERANT CHARGE- CLEANED OUTDOOR COIL &
CHANGED (OWNER PROVIDED) FILTER WHILE WAITING FOR EVAP COIL TO THAW. ADDED
PURON TO SYSTEM AS NEEDED. UPON ADDING PURON, THE HIGH SIDE PRESSURE SPIKED,
AND LOW SIDE DROPED INDICATING A BAD TXV
S - SERVICE CALL 1.00 45.00 45.00
I do not believe the coil was actually frozen. While the unit has been running constantly, I'm getting water out the drain. My coil froze at my previous residence and it stopped dripping altogether.
I also took pictures of his manifold gauges. Unfortunately, I could not read the actual settings, but the blue (left side) was at approx. 10 o'clock, and the red (right side) was at about two o'clock. I did notice he could make the needles go up/down by adjusting the valves on the manifold, though.
I'm including a picture of the manifold, and of the tag from the unit. He said it would likely cost hundreds of dollars (as much as $800 to $900) to evacuate the system, replace the value, and then pump the system back up to the correct level. He said the unit may be overcharged by the two pounds he put in there, that it may not have needed more coolant, and that we should switch it off until it can be fixed.
I did find another thread at another forum where a member was given almost this exact same diagnosis, and had the repair done (it only cost him $550), but it didn't help, and there was no follow-up after that.
Any ideas on how to make sure this is the right fix? Will continuing to run the unit hurt it?