    What size breaker/wire did you use for your PM66?

    Had a electrician come last week who was recommended to wire up my new shop as well as my new PM66 5hp. From the #s on the saw he said a 30amp breaker would do just fine. I found the manual so he could see it and he pointed out that the manual suggested a 40amp breaker and 10g wire. He said you can't do a 40amp breaker with 10g wire, has to be 8g and had no idea why the manual would have it as 10/40 instead of 8/40.

    He thinks 10g 30amp will be fine, but figured I would ask what you guys did on yours before it is done. Should be calling me this week or next to setup a time to do all this.

    Thanks
    Matt


  2. #2
    I have my 3 hp Shop Fox saw wired on a 30 amp breaker, using 10 gauge wire. Works just fine.

    BTW, if you look at the power cord for you saw, you'll probably find it to be just 12 gauge. Most are.

  3. #3
    Join Date
    Feb 2003
    Location
    Collin County Texas
    Posts
    2,417
    Hi Matt, how are things in "the rubber capital?"

    A 3 hp motor running at 240v, under full load, will draw around 18 to 20 amps. A 5 hp will draw about 30 amps under full load. So take your choice, 30 amp breaker and 10 ga wire, or 40 amp breaker and 8 ga. wire. Don't need to worry about start up current as breakers are built to understand a large current surge for less than a second, that is enough to get your motor up and running.

    BTW, I grew up in south Akron. It is a good place to be from.
    Best Regards, Ken

  4. #4
    Join Date
    Mar 2003
    Location
    odessa, missouri
    Posts
    1,931
    Blog Entries
    2
    Matt if hes a licensed electrician i think id just take his advise .

    i ran a 3hp unisaw on a 15 amp breaker/10 guage wire for a couple yrs and only had one trip and that was when a buddy from the cabinet shop thought he could push lumber through the saw like he did on the 5hp three phase at the cab shop....jack

  5. #5
    Join Date
    Feb 2003
    Location
    Chappell Hill, Texas
    Posts
    4,741
    I've been using a 30amp / 10gauge wire on my PM66 5HP since '97 with no issues.

  6. #6
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    Matt, for what it's worth, the GE load center box I looked at after work said motors 1 1/2 to 3 hp 30 amp curcuit. It didn't talk about wire size. Sounds like either way you go will be fine. I'm like Jack, though. Take the electrician's advise. If nothing else, you have a little headroom, and if you ever upgrade to a 5 hp..... Again, me with the "bigger is better" syndrome. It's a sickness I tell my wife, a sickness! ;-) Jim.

  7. #7
    Join Date
    Feb 2005
    Location
    Sterling CT
    Posts
    2,474
    I haven't looked at the code recently, but when I worked as an electrican 10 gauge romex was only rated for 30 amps as your electrician indicated.

    lou

  8. #8
    Quote Originally Posted by Todd Burch
    I've been using a 30amp / 10gauge wire on my PM66 5HP since '97 with no issues.
    Ditto Except I have a Uni and only since 03

  9. #9
    Join Date
    May 2005
    Location
    Upstate South Carolina
    Posts
    92
    Your electrician is dead right about #10 wire not being allowed on a 40 A breaker! I just checked the manual on-line and they are wrong!!!

    To be sure you are right about what you do use:
    1)Remove the motor cover on the left side of the saw and read the actual motor nameplate amps.
    2) multiply that rating by 1.25
    3) select a breaker rating equal to or higher than that number and select the wire according to the breaker rating.

    for instance:
    A motor nameplate of 24 amps X 1.25 = 30 Amps: therefore, a 30 amp breaker and # 10 wire works fine and meets all codes for a 230volt single phase motor rated at 24 amps or less.

    A motor rating of 24.1 amps or higher will require you go to a 40 amp breaker and # 8 wire.

    In some cases, when the length of the wiring is very long (say 200 feet or so), you would increase the wire size in order to reduce the voltage drop in the conductors. But NEVER use wire that is rated less than the breaker or fuse that protects it. That's what burns down houses and shops!

    Sounds like you've got an electrician that knows what he's doing. I believe I'd keep him.
    The less you know, the less likely you are to be subpoenaed.

    Fred

  10. #10
    Join Date
    Sep 2003
    Location
    Grand Marais, MN. A transplant from Minneapolis
    Posts
    5,513
    I hard wired a 40 amp breaker and #8 wire. A 60 amp disconect at the saw.
    TJH
    Live Like You Mean It.



    http://www.northhouse.org/

Similar Threads

  1. Maximizing your table size
    By mike wallis in forum Laser Engraving General Topics
    Replies: 10
    Last Post: 05-30-2005, 1:41 PM
  2. HTC Roller Table on PM66 - Install Update (Long)
    By Doug Shepard in forum General Woodworking and Power Tools
    Replies: 13
    Last Post: 03-27-2005, 10:18 PM
  3. What size should roof rafters be?
    By Bob Weisner in forum General Woodworking and Power Tools
    Replies: 15
    Last Post: 10-22-2004, 1:47 PM
  4. What the size of your workshop?
    By Jim Ketron in forum General Woodworking and Power Tools
    Replies: 77
    Last Post: 10-02-2004, 10:17 AM
  5. Wire size for new shop sub panel
    By Jim Ketron in forum Off Topic Forum
    Replies: 1
    Last Post: 08-21-2004, 6:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •