I'll bet you a nickel that there is a wire pierced by a nail somewhere in the run. It probably was there from day 1 when the electrician installed the wiring and it finally caused a problem due to temperature change, and or breakdown. I think new wiring is the best fix unless you want to rip down the Sheetrock to confirm the failure. Given what you said about it being new construction I would insist on warranty replacement at no charge to you.
I agree with Pat, if it's new construction, let the contractor pull his hair out over it
I remember decades ago when we had problems at work with communication cables we would use a time domain reflectometer to find where the problem was. I'd hate to think that you would need to those lengths to find a house wiring problem.
One time I got dragged into repairing a home intercom system in a newly constructed house. I don't think there was a cable anywhere that didn't have a staple sunk through it. A true nightmare to repair.
If the contractor is at fault he needs to be leaned on to make it right.
-Tom
So if you have a leg from the load center to a box for a receptacle (for example), and with both ends detached you find continuity. And you also have a leg from that receptacle box to (for example) a box with a switch, and with both ends detached you also fine continuity. And if you have yet another leg (same as the other two) and you're finding continuity on THAT one, then I'd guess maybe you're using your fingers to hold the probes to the wires and the continuity is your body?
I can't imagine you're going to have multiple bad legs.
+1. As someone who maintains and uses $100,000 or so of fairly sophisticated test equipment (electrical substation testing) I'm thinking that there is probably some user error creeping in here. I'd personally put everything back together, put a regular breaker in the panel, and measure current on the circuit with everything turned off (with the breaker on). Depending upon what model Fluke you're using you may already have what you need but you do need a fairly sensitive ammeter to test the circuit this way (a Fluke 289 for example will measure micro-amps) . If there is leakage it will be easily evident; if there is no leakage you've been chasing your tail.
I have continuity both directions. I'm definitely sure I have an issue between the breaker box and the light switch box because there isn't anything there but the wire. It can't be more than 20' feet between the two. Then I have continuity somewhere down stream of the light switch box, but I don't know where. I know how to use a Ohmmeter. I was an electronics tech for 25 years in the Air Force and I'm using a high $$ Fluke meter with clip leads. I'm not an electrician however.
Last edited by Dennis McDonaugh; 07-02-2014 at 3:50 PM.
Dennis
My first guess would be a bulb in a light socket.Then I have continuity somewhere down stream of the light switch box, but I don't know where.
How many ohms your meter is reading tells the story. If it is in the 10-30 ohm range it may be a light. A bathroom fan motor may be higher. A high resistance could be pierced insulation. It may not be a problem until a little heat expands the wires and the resistance drops enough to open the breaker.
This could be something caused by an inexperienced sheet rocker.