My previous post regarding 30ga metal duct pipe was if 30ga would work. Some yes, some no. Searching the Internet there were a couple of possible solutions. One was to leave a gate open all times, one to put plywood rings around the pipe, and one to make a vacuum relief. Since I hadn't dismantled the DC I decided to test all three before I put all this up and had a failure. I measured the thickness of my pipe and it was 0.011 (0.001 under nominal ). My DC is a 3hp Jet 1900. Specs say 1900 CFM, 5629 FPM, 12.5 static pressure @ 8". My test set up was three 5' sections with a wye on the end so I could incorporate my vacuum relief. There were blast gates at the end and before the wye. I used flex hose to connect to the DC. I made three 6" plywood rings and placed them around the pipe center of the joints. My vacuum relief was only about 20% effective with the springs I had on hand. My testing sequence was A) plywood rings, open gate open vacuum, B) plywood rings closed gate, open vacuum, C) plywood rings closed gate, closed vacuum. Then repeat without the rings. The results were with the plywood rings there was no failure. When I tested without rings and the vacuum open and gate closed the pipe collapsed. Not totally, but significantly. It didn't collapse completely as there was some vacuum relief and it did bounce back when the DC gate was open. The first photo is the test set up. The next two photos are with the DC running. The second tries to show the pipe distortion. The third picture shows 1/2 of my wood ring to give an idea of the distortion. I will use this pipe with the plywood rings. The rings work. The vacuum relief is not worth the effort.
image.jpgimage.jpgimage.jpg