    Lesson Learned: Check Your Remotes!

    We had some strange things happening in our bedroom recently. More specifically, strange things with the lights and ceiling fan. We'd come home and find the lights on and the fan spinning, even though we were sure we''d turned them off. More than once. I'd check to be sure before going out to the shop, then later they would be on again. It followed no discernible pattern. We concluded that the cats were walking across the hand-held remote control on the nightstand.

    Night before last, I went out to check something in the shop and a short while later my phone rang.

    "Did you just do something out there?"

    "All I did was turn the dust collector on and off."

    "You also turned the bedroom light off. Twice."

    My engineer's mind went for everything but the obvious. The startup surge on that new 3hp Leeson motor is big enough to make the wires vibrate in the conduit. Could it be generating some sort of spurious emission that could affect the light controller? Fortunately, good sense returned after a moment, I pulled the wall plug on the cyclone and called her back.

    In a moment, we confirmed my second instinct. The stop button on the cyclone remote also toggled the state of the bedroom lights. The two systems used RF remote controls that were on the same frequency and used the same code.

    Since the code on the cyclone is non-changeable, I fixed the problem the next day by changing the code on the bedroom light controller. A simple fix (except for having to pull the fan down to get to the receiver and its dip-switches). But it's haunted me ever since.

    What if the "start" function on the cyclone had been the same as one of the buttons on the light controller? The Cyclone might have started at random while I was working on it. And what if that had happened when I wasn't in the shop? Before I had the ductwork attached? With no resistance on the inlet, the motor could have burned up if left running. I'm not advocating paranoia, just due caution.

    The moral of the story is twofold.

    First Lesson: When you get a new remote control for a machine in your shop, know what you're getting and check for conflicts.

    If it's an infrared remote (like my Jet air filter or my window AC unit) the remotes can't interfere with something outside your field of vision--they require line-of-sight to work. Just make sure that the new remote doesn't activate any of your other remote controlled stuff in the shop.

    You can verify if your new remote is the RF variety by going outside or into another room where there's no line of sight and trying the remote. If it still works, it's the RF variety. Next, check every remote in your premises and make sure your new remote doesn't control anything it shouldn't and no other remotes can control your newly controlled shop device. If you find a conflict, consult the manufacturer's instructions for how to change codes.

    If you live close to your neighbors, it wouldn't hurt to check with them, too. It's surprising how much range these little things can have at times.

    Second Lesson: I have one more thing to do before I can declare my new cyclone complete. A cutoff switch in a location where it won't be bumped but is still within reach. Just like I did on my table saw and lathe to prevent unwanted startups when not in use (or when curious hands are roaming your shop).

    Okay, I'm stepping down from the soapbox now. As you were.

    D.
    I finally figured out how to deal with sawdust in my hair.

    I shaved my head.

  2. #2
    Join Date
    Dec 2009
    Location
    El Dorado Hills, CA
    Posts
    1,311
    I am not sure what brand your remotes are, but most RF remotes have switches or jumpers inside the battery compartment that allow you to change frequencies. Some allow you to select A, B, or C. Others have a 4 switches that allow you to pick one of 16 different frequencies.

    You might be able to pick different frequencies that don't interfere with the others. It's still a good idea to have a cutoff switch for your cyclone so it doesn't run all night because of a stray RF signal. Some people tie it to the shop lights, so it can't run after you shut off the lights and head back to the house.

    Steve

  3. #3
    Join Date
    Sep 2009
    Location
    Midland MI
    Posts
    887
    I have a lamp in my livingroom that randomly shuts off, I think the neighbors have something on the same frequency.

  4. #4
    Join Date
    Dec 2009
    Location
    El Dorado Hills, CA
    Posts
    1,311
    Quote Originally Posted by cody michael View Post
    I have a lamp in my livingroom that randomly shuts off, I think the neighbors have something on the same frequency.
    They are probably wondering why their ceiling fan is haunted.

    Steve

  5. #5
    Join Date
    Feb 2003
    Location
    Yorktown, VA
    Posts
    2,756
    My dust collector remote turns on one of the fans in the family room. When I turn off the collector, the fan light goes on. We have just gotten used to it

  6. #6
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Quote Originally Posted by Dan Case LR View Post
    The startup surge on that new 3hp Leeson motor is big enough to make the wires vibrate in the conduit.
    Huh?

    .........
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  7. #7
    Join Date
    Nov 2012
    Location
    Southwestern CT
    Posts
    1,392
    Now if it turned my teenagers mobile devices off ...

  8. #8
    Join Date
    Dec 2010
    Location
    NW Arkansas
    Posts
    1,957
    Blog Entries
    1
    When I moved in present home 5yrs ago, I had to use garage as shop. Added x10 remote for dust collector and couple of outlets. Came home one day and found DC running, hadn't used in a week, and no one else home. Changed settings and hasn't read occurred. Assume neighbor had one too.
    Woodworking, Old Tools and Shooting
    Ray Fine RF-1390 Laser Ray Fine 20watt Fiber Laser
    SFX 50 Watt Fiber Laser
    PM2000, Delta BS, Delta sander, Powermatic 50 jointer,
    Powermatic 100-12 planer, Rockwell 15-126 radial drill press
    Rockwell 46-450 lathe, and 2 Walker Turner RA1100 radial saws
    Jet JWS18, bandsaw Carbide Create CNC, RIA 22TCM 1911s and others

  9. #9
    Join Date
    Dec 2008
    Location
    Northern Michigan
    Posts
    5,011
    Reminds me of a scene in Grumpy Old Men.....

  10. #10
    Join Date
    Dec 2011
    Location
    Little Rock, AR
    Posts
    344
    Quote Originally Posted by Steve Peterson View Post
    I am not sure what brand your remotes are, but most RF remotes have switches or jumpers inside the battery compartment that allow you to change frequencies.
    The DC remote is from Oneida and isn't switchable. I'm sure it could be changed by changing jumpers in the remote, but not worth the hassle. Fortunately booth of the remote controlled fan/light units on our house have dipswitches and are easily changed.

    I've got to admit that I'm surprised -- and disappointed -- that Oneida used such a low-end wireless remote unit. I guess that's why they're so ready to throw them in free when you order a cyclone.

    D.
    I finally figured out how to deal with sawdust in my hair.

    I shaved my head.

  11. #11
    Join Date
    Mar 2012
    Location
    Taylors, SC
    Posts
    223
    This thread has me worried that when I get the system up and running I'll go into the shop one day to find the DC running... possibly for days. Yikes.

  12. #12
    Join Date
    Dec 2011
    Location
    Little Rock, AR
    Posts
    344
    Quote Originally Posted by Dan Hintz View Post
    Huh?

    .........
    Every AC motor draws higher current when it's first energized, a fact referred to by the terms "starting current," "startup surge" or "inrush current." Different motor designs behave differently in this respect, and High-Efficiency motors like the 3hp Leeson on my new cyclone are especially fond of high inrush current. I read somewhere that the inrush current on these high-efficiency motors is roughly equal to the locked-rotor current, which in the case of my Leeson is around 100 Amps (vs 10-12 amps in normal operation). Because the inrush lasts only a few seconds, the #12 wire that supplies this motor handles it fine--with one little exception.

    During that inrush period, the higher current flow through those wires generates strong 60 Hz magnetic fields that interact with the steel (EMT) conduit where they reside. In many cases where the wire tension is just right the result is audible vibration inside the conduit that can get louder than you might think--loud enough to to scare the whatever out of you the first time you fire it up.

    There are several factors that affect how audible this phenomenon is, including size and type of conduit and what else is in it. The biggest factor is how tight the wires are pulled and how full the conduit is, which determines how much they can vibrate. If the electrician that did the install is one of those stingy types who never uses an inch more wire than required and wouldn't upsize a conduit if his life depended on it, the sound will tend to be less prominent. I'm a Service Loops kinda guy who hates overstuffed conduit right at its fill limit, so in my case it's quite audible.

    But of course, since I understand what's happening I've learned to ignore that first second or two when the cyclone starts. I usually don't even notice it now, but it's fun to show it to other guys.

    D.
    I finally figured out how to deal with sawdust in my hair.

    I shaved my head.

  13. #13
    Join Date
    May 2009
    Location
    N.W. Missouri
    Posts
    1,564
    The wires resonate at 60 Hz., right? What frequency do the remotes operate at?


    John

  14. #14
    Join Date
    Dec 2009
    Location
    El Dorado Hills, CA
    Posts
    1,311
    Quote Originally Posted by John McClanahan View Post
    The wires resonate at 60 Hz., right? What frequency do the remotes operate at?
    There are only a few frequencies available for RF remotes that don't require special transmit licenses. Most operate at 315MHz or 434MHz in the US. Europe might use 868MHz. More expensive devices could be using 2.4GHz. All frequencies are way outside the 60Hz resonance in the wires.

    Steve

  15. #15
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Quote Originally Posted by Dan Case LR View Post
    Every AC motor draws higher current when it's first energized, a fact referred to by the terms "starting current," "startup surge" or "inrush current." Different motor designs behave differently in this respect, and High-Efficiency motors like the 3hp Leeson on my new cyclone are especially fond of high inrush current. I read somewhere that the inrush current on these high-efficiency motors is roughly equal to the locked-rotor current, which in the case of my Leeson is around 100 Amps (vs 10-12 amps in normal operation). Because the inrush lasts only a few seconds, the #12 wire that supplies this motor handles it fine--with one little exception.

    During that inrush period, the higher current flow through those wires generates strong 60 Hz magnetic fields that interact with the steel (EMT) conduit where they reside. In many cases where the wire tension is just right the result is audible vibration inside the conduit that can get louder than you might think--loud enough to to scare the whatever out of you the first time you fire it up.

    There are several factors that affect how audible this phenomenon is, including size and type of conduit and what else is in it. The biggest factor is how tight the wires are pulled and how full the conduit is, which determines how much they can vibrate. If the electrician that did the install is one of those stingy types who never uses an inch more wire than required and wouldn't upsize a conduit if his life depended on it, the sound will tend to be less prominent. I'm a Service Loops kinda guy who hates overstuffed conduit right at its fill limit, so in my case it's quite audible.

    But of course, since I understand what's happening I've learned to ignore that first second or two when the cyclone starts. I usually don't even notice it now, but it's fun to show it to other guys.

    D.
    I'm trying to imagine the magnetic field of a single, straight, solid-conductor wire running at 120V that's strong enough to make the cable move within conduit... and I can't.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •