Originally Posted by
Dan Case LR
Every AC motor draws higher current when it's first energized, a fact referred to by the terms "starting current," "startup surge" or "inrush current." Different motor designs behave differently in this respect, and High-Efficiency motors like the 3hp Leeson on my new cyclone are especially fond of high inrush current. I read somewhere that the inrush current on these high-efficiency motors is roughly equal to the locked-rotor current, which in the case of my Leeson is around 100 Amps (vs 10-12 amps in normal operation). Because the inrush lasts only a few seconds, the #12 wire that supplies this motor handles it fine--with one little exception.D.
If you had 100 amps for several seconds through a breaker that was rated at say 20 amps, it would trip the breaker. The inrush current on a motor decays with the rotation speed. On a normal unloaded motor of less than 5 HP you're probably talking milliseconds of really high current (a few Hz), with a very rapid decay. By one second the current should be pretty close to unloaded running current. I know the motors in my shop "jump" to speed in no more than a second.
Like Dan, I cannot imagine a single wire, in the kind of voltage and amperage we're talking about for woodworking tools, generating sufficient magnetic field to move the wire.
Mike