Originally Posted by
Anthony Whitesell
Lighting circuit is run. DC circuit is a single outlet home run.
One thing I failed to elaborate on is that since it is a basement shop, the power feeds are all over head (due to door ways, concrete walls, and slab floor). The idea of running up and down each wall seems like it would take a whole bunch of extra wire. As Phil mentioned, I was thinking of doing a trunk line-drop line design with boxes at the ceiling line dropping to the outlets. Unless someone knows of a better way.
Why not run conduit from box to box on the walls? If you don't want to mess with conduit, then yes, place an occasional junction box on the ceiling to minimize how many cables run into a given box, and drop down from those. You shouldn't be running more than 4-5 cables into a standard 1900 box anyway. Most municipal codes around here don't allow more than (4) conduits in a 1900, (5) in a deep 1900 and (6) in an 11-B box. (There are also rules regarding the size of the conduits but no need to get into that here.)
You definitely don't want to stuff the box with wires. It introduces problems like shorts and overheating. Distributing junction boxes along the ceiling (if you don't run conduit on the walls) reduces the amount of cables entering a box and makes terminations easier, as well as tracing out problems later. If you keep the number of cables entering a given junction box to 4-5, your life will be easier.