Thread: Filtering fresh air furnace intake

  1. #16
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Quote Originally Posted by George Bokros View Post
    Years ago houses were not any where near as tightly sealed as they are today. This combined with the fact that the newer furnaces draw their combustion air from outside thus not creating a negative pressure in the house. With the reduced negative pressure inside less fresh air enters when you open a door so the air in the house is not refreshed. The vent bringing the fresh air into the supply air keeps the air in the house fresher with out introducing cold air as you would get if you opened a window. If you introduce this fresh air upstream of the normal house air filter it will be filtered for particulate but not odors. You may have to change your HVAC filter more often though.

    Do you know how nice it smells in the house when you open a window for the first time in the spring?
    Combustion air coming from outside is fine, and it allows the house to remain as sealed as you want... but I still can't comprehend a (efficient) system that expect fresh air on the intake side. It just defeats the entire purpose of a closed system. It would be like standing in front of a window-style A/C unit while you're in the middle of a park... you'll get cool, but only as long as you stand directly in front of the unit. It's not going to cool the park around you.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  2. #17
    Join Date
    Jun 2006
    Location
    The Hartland of Michigan
    Posts
    7,628
    I have 35 years experience with HVAC. If you want to argue the topic, it's not going to be with me.

  3. #18
    Join Date
    Feb 2003
    Location
    McKean, PA
    Posts
    15,649
    Blog Entries
    1
    Quote Originally Posted by ryan paulsen View Post
    Code required installation of the fresh-air intakes to displace the accumulation of indoor pollutants/toxins.
    Any chance you can get a copy of the code section that requires this type of vent?
    Lee Schierer
    USNA '71
    Go Navy!

    My advice, comments and suggestions are free, but it costs money to run the site. If you found something of value here please give a little something back by becoming a contributor! Please Contribute

  4. #19
    Move the fire (burning leaves) to another area away from the intake.

  5. #20
    Join Date
    Jun 2006
    Location
    The Hartland of Michigan
    Posts
    7,628
    Quote Originally Posted by Bill Orbine View Post
    Move the fire (burning leaves) to another area away from the intake.
    It's his neighbor that is burning leaves.

  6. #21
    Myk is correct. I have twenty years hvac experience. A lot of local codes require a 4" fresh air vent on the return air. We wire them with a damper to shut it off when the furnace isn't running. If an air exchanger is installed the vent isn't required. As much as you don't understand it Dan, fresh air is required in a building.

  7. #22
    Join Date
    Oct 2006
    Location
    Minneapolis, MN
    Posts
    5,456
    I know here in Minnesota either a fresh air intake or an air exchanger is required. It seems silly to me to have a high efficiency furnace, but then run a 4" or 6" duct to to the outside that brings in cold air in the winter. Everyone says to insulate and seal against air infiltration, but then the utility room has an intentional air leak that defeats all the other air sealing. A friend of mine had a new furnace installed in a really old house and the installers put in a fresh air intake. My friend plugged the intake as soon as the installer left. He said the house was fine without it for 60+ years and the house has plenty of air leaks.

    I had a complete forced air system put in last year to replace electric baseboard heat. The HVAC company said I was right on the edge of needing a air exchanger.

  8. #23
    Join Date
    May 2013
    Location
    Liberty, SC
    Posts
    613
    Brad & Myk,
    Are we applying the 5% fresh air intake to home systems like the commercial systems have been doing for years?
    You never get the answer if you don't ask the question.

    Joe

  9. #24
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,277
    Quote Originally Posted by Brad Adams View Post
    Myk is correct. I have twenty years hvac experience. A lot of local codes require a 4" fresh air vent on the return air. We wire them with a damper to shut it off when the furnace isn't running. If an air exchanger is installed the vent isn't required. As much as you don't understand it Dan, fresh air is required in a building.
    Very interesting Brad.

    I've only seen combustion air vents that open into the furnace room, not the return air duct.........Thanks for the info..........Rod.

  10. #25
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Quote Originally Posted by Myk Rian View Post
    I have 35 years experience with HVAC. If you want to argue the topic, it's not going to be with me.
    I'm not trying to argue the topic, but so far no one has offered a logical explanation as to why you would want a link between the inside and outside air (claiming a health benefit is too homeopathic-like in its reasoning). Claiming many local codes require it is also not an explanation of what problem it solves, just an explanation of why its required on a build. Providing such a vent near a combustion source (propane, oil, etc.) makes complete sense to avoid asphyxiaton, but I'm not seeing a valid reason yet for making a connection between inside and outside. Following the reasoning provided so far (it's required in certain jurisdictions) can be easily applied on the other side... it's NOT required in many jurisdictions and it's NOT used. I know my 3-year-old house doesn't have it on any of the three A/C system in the house (one of which is propane), and the system in the last 40-year-old home didn't, either.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  11. #26
    Join Date
    Sep 2010
    Location
    Livonia, Michigan
    Posts
    780
    First off, no, I don't know a solution to Ryan's problem. I don't see a HEPA filter keeping smoke out.

    The reason the inlet is there is is because of code.

    With houses being sealed tighter now the problem wasn't just a negative pressure, it was also mold. According to a Minnesota seminar (I didn't go to the seminar, I just saw the PowerPoint) that stated that mold went from essentially zero to 5% of all housing failures. No, nothing was cited to support that claim, don't ask me what they mean by housing failure or how they conjured the 5% figure.

    What Ryan has is a passive air inlet. If he had a exhaust fan larger than a certain size an active make up air system would be required. That is an fan interlocked with the exhaust fan. As far as size the number 400 CFM and larger comes up a lot.

    I first found out about this when a relative built a house. He needed the vent. Plus the bathroom was on an outside corner but he couldn't have any windows in it and still have the windows he wanted in the living and bedrooms. He couldn't have a window to open but he had to have a vent.

    And don't bother asking why after paying dearly to carefully seal up a house that you're then required to poke big holes in it. That's already been done on many of the builder's forums, in triplicate.

    -Tom

    "Well meaning idiots are still idiots." -By too many to list.

  12. #27
    Join Date
    Dec 2014
    Location
    Lake County, IL
    Posts
    147
    Thanks everyone for the information, and the lively discussion regarding the merits of a fresh air intake. I think I am going to try an inline filter box and use a charcoal filter to see if it helps. Good news is the leaves are done falling, so burning season is about over, so I have some time. Any thoughts on a product like this:

    http://www.amazon.com/dp/B003E5U8BO/...uwb19VNN84#Ask

    with a filter like this:

    http://www.airfilterusa.com/astro-so...d-10x20x1.html

  13. #28
    Join Date
    Aug 2010
    Location
    USA
    Posts
    5,582
    Quote Originally Posted by Brian Elfert View Post
    I know here in Minnesota either a fresh air intake or an air exchanger is required. It seems silly to me to have a high efficiency furnace, but then run a 4" or 6" duct to to the outside that brings in cold air in the winter. Everyone says to insulate and seal against air infiltration, but then the utility room has an intentional air leak that defeats all the other air sealing. A friend of mine had a new furnace installed in a really old house and the installers put in a fresh air intake. My friend plugged the intake as soon as the installer left. He said the house was fine without it for 60+ years and the house has plenty of air leaks.

    I had a complete forced air system put in last year to replace electric baseboard heat. The HVAC company said I was right on the edge of needing a air exchanger.
    I had a high efficiency furnace installed last year and they vent in outside air through a 1 1/2" PVC pipe, not a 4 or 5" duct. This is combustion air, not going in to the cold air return AFAIK

  14. #29
    Join Date
    Aug 2010
    Location
    USA
    Posts
    5,582
    Quote Originally Posted by ryan paulsen View Post
    Thanks everyone for the information, and the lively discussion regarding the merits of a fresh air intake. I think I am going to try an inline filter box and use a charcoal filter to see if it helps. Good news is the leaves are done falling, so burning season is about over, so I have some time. Any thoughts on a product like this:

    http://www.amazon.com/dp/B003E5U8BO/...uwb19VNN84#Ask

    with a filter like this:

    http://www.airfilterusa.com/astro-so...d-10x20x1.html
    Yes it will work, yes it will also hamper the flow of air into the furnace from outside. Your fresh air intake may be oversized in which case it won't be a problem to put restriction inn the line. Just keep in mind that the more you filter the incoming air the less air you will get and you could end up causing problems

  15. #30
    Join Date
    Dec 2014
    Location
    Lake County, IL
    Posts
    147
    Quote Originally Posted by Dan Hintz View Post
    I'm not trying to argue the topic, but so far no one has offered a logical explanation as to why you would want a link between the inside and outside air (claiming a health benefit is too homeopathic-like in its reasoning). Claiming many local codes require it is also not an explanation of what problem it solves, just an explanation of why its required on a build. Providing such a vent near a combustion source (propane, oil, etc.) makes complete sense to avoid asphyxiaton, but I'm not seeing a valid reason yet for making a connection between inside and outside. Following the reasoning provided so far (it's required in certain jurisdictions) can be easily applied on the other side... it's NOT required in many jurisdictions and it's NOT used. I know my 3-year-old house doesn't have it on any of the three A/C system in the house (one of which is propane), and the system in the last 40-year-old home didn't, either.
    Here is my understanding, based solely on the research I've done as well as discussing with my builder and HVAC contractor. The house is typically in a condition of negative pressure, due to appliances, hoods, and exhaust fans venting to the outside. So, outside air will go from higher pressure (outside) to lower pressure (inside) either through gaps/failed seals around penetrations, or whenever doors or windows are opened. This is unconditioned air entering the house. By adding a fresh-air line to the return plenum, the air is conditioned before entering the house. This air will also put the house in a position of positive pressure, so conditioned air will push out of the house to the outside as opposed to the other way around.

    I have also read the benefits of replacing the indoor air to decrease the buildup of contaminated air via off-gassing, CO buildup, etc but as far as that goes I'd just as soon open a window.

    Quote Originally Posted by Pat Barry View Post
    Yes it will work, yes it will also hamper the flow of air into the furnace from outside. Your fresh air intake may be oversized in which case it won't be a problem to put restriction inn the line. Just keep in mind that the more you filter the incoming air the less air you will get and you could end up causing problems
    Thank you. The furnace system was balanced before the fresh-air lines were added, they were added during final inspection. I am not opposed the restricting those lines slightly, so hopefully this does the trick.