Several months ago, I purchased the Super Dust Gorilla 5 HP from Oneida. Previously, I had a Jet 1.5 HP which was just not doing enough to pull the fine dust from my tools.
The specifications on the OneidaSuper Dust Gorilla were:
· 5 HP US made Baldor motor
· Max Performance 1860 CFM at 2.5” SP
· 8” Inlet
· HEPA MERV 16+ Filter
Given my new tool, I wanted to see how well it really performed compared to the Oneida performance curve.
I did the testing using tools borrowed from John Lanciani. I give my thanks to John for loaning very nice tools to do the testing. He has also offered to loan them to others. It would be great to see some others do the testing and have some comparison data from a variety of dust collectors.
The tools were a Dwyer 471 Digital Thermal Anemometer, UEi 151 Digital Manometer, and a clamp ammeter.
To do the testing, I installed two 24” lengths of 8” duct to the 8” inlet of the dust collector. I also built a cone to insert into the end of the duct using an 8” funnel mounted on a ½” threaded rod with a handle on the end. It was easy to use this to change the flow from zero to over 1800 cfm. One note about the testing. It would have been better to have a longer length of pipe to increase the distance between the funnel and the measuring point and to the inlet of the dust collector. Unfortunately, with the way my dust collector is installed in my garage, there was not enough room to do this.
P7170004 Funnel Crank 2 M.jpg
I took a set of measurements at full open and full close and at 1” SP intervals in between. The position of the measurements was based upon suggestions in the literature. In order to make the positions of these measurements reproducible, keep the probe steady and keep it properly oriented, I built a stand for the digital anemometer probe. This allowed the probe to be raised and lowered to specific heights in the duct.
I have attached pictures of the stand, the thermal anemometer and the anemometer tip. There are two holes in the tip. One is the hot wire anemometer and the other measures temperature. The probe must be kept perpendicular to the air flow to get accurate readings.
P7170017 Probe Stand M.JPG20160721_DW471 M.jpg20160721_DW471 Tip M.jpg
The graph shows the flow for the averaged measurements and the squares in the graph are the data from the Oneida website.
The data was plotted on a graph along with the data from the Oneida website. My measurements (diamonds) were slightly lower than those provided by Oneida (squares) but within about 10% and therefore within the accuracy of the instruments and the measurements.
Duct Graph 3 M.jpg
Velocity measurements in the pipe ranged from 1100 fpm to 4700 fpm in the 8” duct.
Current measurements were made with the clamp ammeter for maximum air flow and for no air flow.
· Fully closed with minimum air flow - 7.2 amps
· Fully open with maximum air flow of 1650 cfm – 12.5 amps
In addition, measurements were made of the filter pressure at static pressure and various flow rates. Filter pressure ranged from about 0.5” at high static pressure with low flow rates and about 3.0” at low static pressure with high flow rates. This suggests that one needs to monitor filter condition at about the same flow or static pressure level.
Filter Pressure M.jpg
OK, why go to all this effort to test the dust collector even though it does not represent actual operating conditions.
· I wanted to determine if I got what I paid for in terms of performance and the answer is yes.
· I wanted to provide actual data so anyone could see actual data not provided by the dust collector company.
· I am hoping that several people will decide to borrow the instruments from John Lanciani and provide actual data on other dust collectors.
· I would like to see data on some of the 1.5 hp dust collectors and the HF collector.
I did some measurements of my Jet 1.5 HP Vortex Canister dust collector. My measurement of static pressure was made using a homemade manometer gave 10.25” and very close to the specs. However, the CFM measured using a digital anemometer gave only about 670 cfm at the 6” port on the collector and about 450 cfm at the 4” port at the collector. This is no where near the Jet claimed 110 cfm.
I have another post that I am working on which details the measurements made in my shop with the actual 6” and 4” piping, blast gates and hooked up to a couple of my machines. This data is much more useful as it shows exactly what type flow rates I am achieving to pull the dust out of my shop.