    You could do all the hard work stringing and mounting everything. Then hire an electrician to connect to the real power and inspect your work. It will cost less since you did most of the work.

  2. #47
    Just to muddy your water a bit...

    Why not use 12/3 in a multiwire branch circuit configuration?

    That would give you 2 separate 20amp 115volt circuits plus a 230volt with one run from the box and one less space in your panel.

    If you still want/need a dedicated 230 you could still do a second run...

    But now you'd have 2x115v circuits plus 2x230v circuits with minimal extra cost and work and only one more space in your box...