    Be Careful About Back Feeding Power Panel From Generator

    Most larger (4000 watt +) generators have a 220 outlet. Unless your outlet is a four prong (including ground,) then you don't have a neutral. This means what goes out on one leg of 220 has to come back on the other. As an example, coffee pot is on one leg, and alarm clock is on the other, without a neutral, it's good bye alarm clock. You may substitute anything that draws less current than device on other leg (big screen, control board for fridge, computer, etc.) They will become a TOAST, and in short order. DAMHIK Please don't consider making a "suicide cord," the kind with male plugs on both ends. Remember that power company will pull meter from any house that has generator running and doesn't have it fed through a transfer switch. Better safe than sorry!

  2. #2
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    I agree that backfeeding an outlet is a bad idea. There are just too many things that can go wrong. But I am not sure this is one of them if your generator has a bonded ground.
    The neutral and ground of your house are connected at the panel. If the ground is connected to the ground of your generator, then you effectively have a neutral in your generator.

  3. #3
    Generators generally don't have a bonded ground, due to the nature of their windings. They have two sets of 110 windings which are connected together to make 220, with no neutral between them.

  4. #4
    Join Date
    Nov 2005
    Location
    Mid Michigan
    Posts
    468
    My welder/generator states on the front panel "neutral bonded to frame".

    Ed

  5. #5
    Quote Originally Posted by Ed Labadie View Post
    My welder/generator states on the front panel "neutral bonded to frame".

    Ed
    "Welder / Generator" key words. Not a dime store generator

  6. #6
    Join Date
    May 2005
    Location
    Highland MI
    Posts
    4,521
    Blog Entries
    11
    Quote Originally Posted by Bruce Wrenn View Post
    "Welder / Generator" key words. Not a dime store generator
    Dime store, now there is a blast from the past...
    NOW you tell me...

  7. #7
    Join Date
    Apr 2005
    Location
    Central MA
    Posts
    1,588
    Quote Originally Posted by Bruce Wrenn View Post
    Generators generally don't have a bonded ground, due to the nature of their windings. They have two sets of 110 windings which are connected together to make 220, with no neutral between them.

    http://www.generlink.com/files/123356851.pdf. Actually, if you look on this list which is fairly comprehensive, it is about a 50/50 split between generators with a bonded neutral and a floating neutral.

  8. #8
    Best I can remember NEC doesn't allow ground to serve as a neutral. Older dryers and stoves did though. Basically unless your generator has a four prong 220 plug, I wouldn't use it to feed thru a 220 breaker/outlet. I converted one of my generators to a four prong outlet, but requires some understanding of how wiring in generator works. Because I own several hundred feet of cords, I just use cords to connect up desired appliances. This way when power comes back on, the lights that were left on tell us "power's back!"