    Wiring my heater

    Can anyone tell me what gauge wire I need to hook up my 5000 watt overhead heater ? I have 2 open 220 volt outlets and want to use one of these as a junction box to hardwire the heater. They each have their own breaker. The heater says it is 20.5 amps so the 30 amp breakers are okay but the installation instructions don't specify wire size. I guess they assume an electrician will install. Thanks
    Any day I wake up is a good day.

  2. #2
    Join Date
    Feb 2007
    Location
    Oglesby,Il.
    Posts
    73
    You'd use #10 for a 30A Circuit or #12 for a 20A Circuit. Code states #12 is good for 25A but generally use for up to 20A. if ya figure the % ratings it starts to be fun.. But yeah #10 will be the size wire you'd use for a 30A Circuit....
    I can sure make a mean pile of Saw Dust !!!

  3. #3
    Join Date
    Jan 2007
    Location
    Northeast of Baltimore, MD
    Posts
    228
    Thanks Terry, it has warmed up enough here for me to finally be able to work in my shop without heat.
    Any day I wake up is a good day.

  4. #4
    Join Date
    Oct 2006
    Location
    Mid Michigan
    Posts
    3,559
    Roy,
    I agree with Terry. To be on the safe side I would use #10 wire. I will run 220 volt 5000 watt items for short periods on #12 but if it is something that will be on frequently like a heater I feel safer with #10.
    David B

  5. #5
    Join Date
    Feb 2003
    Location
    Leesville, SC
    Posts
    2,380
    Blog Entries
    1
    Roy,

    Use #10 wire on a double 30 amp breaker.
    Army Veteran 1968 - 1970
    I Support the Second Amendment of the US Constitution

  6. #6
    Join Date
    Dec 2006
    Location
    Porter,TX
    Posts
    1,523

    wire size

    Just remenber PIE. P=IxE P-watts,I-20amps,E-220V.20amp#12 wire and 30amp#10 as stated by others.Most items in the average woodshop don't draw more then 30amps.Unless you have a welder.

Similar Threads

  1. Buying a water heater?
    By Rick Potter in forum Off Topic Forum
    Replies: 5
    Last Post: 03-04-2007, 12:50 PM
  2. Shop Heater is too noisy
    By Kevin Johnson in forum General Woodworking and Power Tools
    Replies: 10
    Last Post: 02-17-2007, 9:22 AM
  3. Wiring in cutoff switch/box for future compressor
    By Jim O'Dell in forum General Woodworking and Power Tools
    Replies: 11
    Last Post: 11-01-2006, 10:23 PM
  4. Update on Dimplex Heater
    By RichMagnone in forum General Woodworking and Power Tools
    Replies: 2
    Last Post: 03-02-2006, 8:45 AM
  5. gas heater
    By Mike Evertsen in forum General Woodworking and Power Tools
    Replies: 3
    Last Post: 08-14-2003, 10:01 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •