Thread: Is 20 amp outlet on 30 amp circuit legal?

  1. #16
    Join Date
    Feb 2003
    Location
    Shoreline, CT
    Posts
    2,923
    You should use the 20 amp breaker if you want to use a 20 amp outlet. NEC section 210.21(B) is the cited section that says the receptacle shall have an amp rating not less than that of the circuit. You can use 15 amp outlets on a multi-outlet 20 amp circuit, but that's spelled out specifically in that code section. No problem using a 20 amp breaker with 10 gauge wire.

  2. #17

    More horse beatin'

    Pigtailing puts the receptacle in parallel with the rest of the circuit instead of in series. If the receptacle is interrupted (but doesn't short), then the rest of the ckt remains operational. But, I'm not convinced that the receptacle itself is still protected from surges above its rating just by being in parallel.

  3. #18
    Join Date
    Oct 2006
    Location
    Minneapolis, MN
    Posts
    5,456
    It looks I need to go with a 20 amp breaker then. This is only going to be a single outlet on the circuit.

    I am pretty sure I have a spare 20 or 30 amp double pole breaker. I'll just have to break down and buy a 20 amp breaker if I only have a 30 amp breaker.

  4. #19
    Join Date
    Jun 2007
    Location
    Wichita, Kansas
    Posts
    1,795
    Quote Originally Posted by Brian Elfert View Post
    ... Can I put a 20 amp receptacle on a 30 amp circuit and be legal?
    Haven't read the other responses yet, but the short answer is _NO_!!! If you want to use that circuit, install a 30amp receptacle and replace the plug on the compressor with the a 30amp plug.

    The code folks would probably be concerned about the 5 or 6 feet of 20 amp cable from the compressor to the receptacle not being protected.
    Code folks aren't concered with what's beyond the receptacle. They have no way of knowing or controlling what load the consumer plugs into the circuit. The breaker is there to protect the circuit, not what might be beyond the receptacle.

    As far as the power cord is concerned, it only carries what the compressor is drawing and that sounds like a <20 amp load under non-fault conditions. Under fault conditions with a load >30 amps, the breaker should trip long before the power cord vaporizes.

    The only problem you might see would be a fault condition that draws more than 20 amps which would not trip the breaker and less than 30 amps which would trip the breaker. That is a low probability situation, and I seriously doubt that the power cord would present a problem even should that occur. If it concerns you to the point of interfering with your sleep, replace the cord with a heavier gauge cord.
    Tom Veatch
    Wichita, KS
    USA

Similar Threads

  1. Using 3-wire 220V dryer outlet for tablesaw
    By Tom Henderson2 in forum WorkShops
    Replies: 9
    Last Post: 05-13-2008, 7:51 PM
  2. Amperage for Circuit to Run 3250B
    By Jesse Bushman in forum Turner's Forum
    Replies: 10
    Last Post: 03-03-2008, 10:59 PM
  3. Running a 220V saw from a dryer outlet
    By Tom Henderson2 in forum General Woodworking and Power Tools
    Replies: 9
    Last Post: 06-03-2007, 12:13 PM
  4. 120v Off of 240v Circuit?
    By Russ Filtz in forum General Woodworking and Power Tools
    Replies: 29
    Last Post: 01-02-2007, 2:06 PM
  5. Is there such thing as a 240V branch circuit?
    By Tom Jones III in forum General Woodworking and Power Tools
    Replies: 5
    Last Post: 07-18-2006, 4:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •