    New shop lighting questions

    Hi everyone,

    This is my first post here, so I'll start with a quick introduction. Then on to the questions.

    I'm a novice woodworker and I'm putting together my first shop. That is if you don't include my driveway.

    I built (with help from friends and family) a garage with a second story for my shop. I originally wasn't planning on finishing the shop interior, but it has become apparent to me that I need to. Here are some pictures from about 6 months into the construction. These were taken about a year and a half ago:




    I am an avid DIY'er and I took on all aspects of the building, with the exception of the concrete foundation and floor and excavation. I began this project with a HUGE stack of books from the library and read every one from cover to cover. I designed and drew up the plans on my computer, which took about 6 weeks part time. The building exterior is complete and I've started the interior.

    The shop wiring is nearly complete, except for the lighting. Before I hang my insulation and OSB, I thought I'd better get my lighting planned out - which brought me (again) to this forum for some lurking around.

    I downloaded the "Lighting for the Workshop" by Jack Lindsey article from FWW and read it. I would base my plan entirely off that article except for a couple of "issues."

    Issue #1, I already have the tubes I'll be using.
    I work in a large office area. My company recently began "upgrading" the lighting in my area from 32 watt T8 bulbs to 24 watts. This change is being made in the interest of energy savings - not due to bulb failure. I struck up a conversation with the facilities guy about what was going on and the next thing I knew, I became the owner of 60 four foot 32 watt t8 bulbs to light my shop with. I guess this would be a gloat. They were going to recycle them so they thought it was great that someone could use them until they quit working. Here is a pic of the bulb:



    The other issue is that these tubes came from an area that doesn't have as many fixtures per sq. ft. as recommended by Mr. Lindsey. These bulbs came from an area with about an 11' to 12' high ceiling. There are 3 bulbs per fixture and each fixture covers an 64 sq. ft. area (8x8). The fixtures have are recessed into a drop ceiling and have a mirror finish reflector. They also have a diffuser grid that is also mirror finish. I find this lighting to be adequate for working at night, and I'm 46 years old.

    My shop is 28x40, has 8' walls with a vaulted ceiling by virtue of scissors trusses. The ceiling has a 3/12 pitch giving it around 11' 9" height at the center.

    Mr. Lindsey would have me install somewhere around 36 fixtures (for my T8 four footers) in my shop. Using my office as a guide, I end up with 26 fixtures. That is a pretty big difference! I understand that I'm using different fixtures than in my office, but I'm guessing that the output will be similar - although the office fixtures are more directed than the planned shop lights. My lighting will be strip fixtures of commercial grade mounted to an OSB ceiling that is painted flat white. I'm also planning on putting OSB on the walls and painting them white, with a satin or semi-gloss sheen.

    So far, I've found the online woodworking community to be very friendly and helpful so I'm putting up my plans in the hope that I can get useful feedback that would prevent me from making a time consuming and/or expensive mistake.

    I bought a fixture so I could get a look at it. It seems pretty good. Here is the ballast:


    Since I've already got 4 images in this post, I'll continue this in another post.

    Continued....

    Dave Zeigler
    Last edited by Dave Zeigler; 08-25-2008 at 10:03 PM. Reason: clarify the stated "issues", I hope :)

  2. #2
    Join Date
    Jun 2007
    Location
    Vestal, NY
    Posts
    28

    Continued...

    My plan is to run four rows of light fixtures parallel to the roof ridge. Each row will have seven fixtures, six feet on center. There are two locations where I won't be installing a fixture since they will be over a planned lumber storage area.

    I am planning six single pole switches located near the entry door. The switches will be supplied by two 15A circuits. There will be two sets of three gang boxes, one above the other on the wall. Each box will be supplied with a 14/2 romex feed from the breakers. EMT conduit will come out of the boxes and a single conduit run of 1/2" size will house six hot conductors, two neutral conductors and a ground. All conductors will be 14 AWG and be rated at least 90 deg. C.

    The conduit will run to four junction boxes which will be located directly over a fixture for each row of fixtures.

    The fixtures will be tied together with 1/2" EMT to route the appropriate conductors.



    My apologies to those who may be colorblind. Each color represents a different light switch. There are three zones and each zone is broken into two circuits. Two switches will control light in each zone. Most of my time will be spent in the center of the building, so that area gets the "extra" fixtures. Note that the fixtures next to the left and right walls will be brought in towards the center however much is required, around 4.5 inches. The upper right area is where the planned lumber storage is.

    Ok, that's it for now. Thanks in advance for your constructive comments. Questions are welcome.

    Regards,
    Dave Zeigler

  3. #3
    Join Date
    Dec 2003
    Location
    Mountainburg, AR
    Posts
    3,031
    Blog Entries
    2
    Others may disagree with me but I don't quite get the six switches. I have a shop of similar size and I also have 4 rows of fixtures. However I only have 2 switches and have yet to find an occasion where I left one set off. Recently I had a ballast go out and I noticed it being out. So even the absence of 1 fixture made a difference in the lighting. I am just wondering why you would want that many switches.

    Oh, yeah! Welcome to the creek!
    Larry J Browning
    There are 10 kinds of people in this world; Those who understand binary and those who don't.

  4. #4
    Join Date
    Oct 2006
    Location
    East Brunswick, NJ
    Posts
    1,475
    Here's how I calculated my lighting needs when I was setting up my shop.

    I wanted 100 foot candles of light at my work surface. Multiply that by the area of my shop (11' x 20') means that I need a total of 22000 lumens. Multiply that by some fudge factors to account for the distance of the bulbs to the height of the work surface, loss of light as the bulb ages, and the effect of dust building up on the fixtures, and that number pretty much doubles to 44000 lumens. The bulbs that I picked up (4 foot T8 bulbs) put out 2200 lumens each, so I needed enough fixtures for 20 bulbs.

    My initial thought was that was way too many bulbs. As it turned out, I wasn't able to put in enough fixtures for 20 bulbs in my shop, due to pipes running across the ceiling in my basement shop in inopportune places, and now I wish I had more light, so my guess is that Mr. Lindsey is not too far off in his article.

    In your case, the same calculations comes out to about 224000 lumens for your shop. Googling your bulbs gave me 2800 lumens per bulb, so that's 80 bulbs, or 40 two bulb fixtures. Luckily, you have windows, so that will help a lot in the daytime.

  5. #5
    Join Date
    Jun 2007
    Location
    Vestal, NY
    Posts
    28

    Hmmm

    Quote Originally Posted by Larry Browning View Post
    Others may disagree with me but I don't quite get the six switches. I have a shop of similar size and I also have 4 rows of fixtures. However I only have 2 switches and have yet to find an occasion where I left one set off. Recently I had a ballast go out and I noticed it being out. So even the absence of 1 fixture made a difference in the lighting. I am just wondering why you would want that many switches.

    Oh, yeah! Welcome to the creek!
    I'm tight with a dollar. I pay nearly 14 cents/kwh for power. I can't exclusively put in task lighting since I don't know how the shop will evolve or where I will end up putting some tools. The idea is that usually I will use only the center lighting zone. During the day, I'll use half of that. When I need to use the "ends" of the shop, I'll turn on the lights there. So, three zones and a day/night capability = six switches. Also, I want two circuits for redundancy at night, in the unlikely event that a lighting breaker trips.

    The windows do let in a lot of light. The front of the building faces due South.

    I was thinking that I could add task lighting as needed, in a semi-temporary way to assist the general lighting plan I've outlined. Folly?


    Wilbur,
    Thanks for the data. I guess the lighting at my workplace is terribly inadequate! The article does state 100 foot candles for the over 40 crowd and 50 for the under. Interesting how you planned for the losses from dust, age and distance. I'll need some time with google tomorrow.

    Thanks again,
    Dave

  6. #6
    Join Date
    Jan 2004
    Location
    Lewiston, Idaho
    Posts
    28,504
    Dave,

    I used that article to design the lighting in my shop. I'm pushing age 60 real hard. My shop is 32' x 24'. I installed 11 8'-4 bulb fluorescent fixtures using similar bulbs to what you have. Everyone who comes into the shop likes the lighting, even my friends over 60.

    I wouldn't hesitate to use what Jack Lindsey recommends. As far as the switches go....whatever the # of circuits you want to have is purely personal choice.
    Ken

    So much to learn, so little time.....

  7. #7
    Join Date
    Sep 2005
    Location
    Lewisville, NC
    Posts
    1
    Dave,

    I have an approximate 20'x20' garage shop lit by 32W T8 tubes for the past five years. There are 4 fixtures with 4 tubes in each for a total of 16 tubes. My ceilings are about 8.5' and I think that the lighting levels are probably similar to the original conditions of your hand-me-down tubes (Congrats!).

    I've been very satisfied with the light levels even though I thought that I was putting in more than I needed when I installed them. In hindsight i should have probably put in two more fixtures but task lighting has helped when I need additional light for specific work. For most of the day to day work when I can make it into the shop I find the lighting more than adequate.

    I think you have a good layout and the switch pattern you've setup should allow some control over how you light the shop when you're working in isolated areas. I think you'll be happy with the layout you've posted and with the density of fixtures I doubt you'll need task lighting as much as you expect.

    Good Luck!

  8. #8
    Join Date
    Dec 2003
    Location
    Mountainburg, AR
    Posts
    3,031
    Blog Entries
    2
    Dave,
    I still work a day job, so much of my shop time is in the evening, and I only have 1 window in the main shop. (I wanted the wall space) So my situation may be a little different than yours. BTW, I do have 2 circuits for the lights as well.
    Here is a piece of advice that took me a long time to learn. Don't over engineer or analyze stuff. I try to follow the KISS principle pretty closely when ever I can. It usually works out the best in the long run.
    Just do what you think will work best for you. If you think you need a switch of every fixture, do that! At the end of the day you will be happier.

    One more BTW: I have no idea what I pay per KWH. I just know that my shop is on a separate meter from the house that has a minimum charge and I hardly ever go over that, even in the summer when I run a window AC unit, so electric usage is really not an issue for me.
    Last edited by Larry Browning; 08-26-2008 at 9:28 AM.
    Larry J Browning
    There are 10 kinds of people in this world; Those who understand binary and those who don't.

  9. #9
    Join Date
    Jun 2007
    Location
    Vestal, NY
    Posts
    28
    Quote Originally Posted by Larry Browning View Post
    Dave,

    Here is a piece of advice that took me a long time to learn. Don't over engineer or analyze stuff. I try to follow the KISS principle pretty closely when ever I can. It usually works out the best in the long run.
    LOL! Yep, you got me pegged!

    I'm not bored enough to do the math, but I bet it would take years to pay for wiring six switches vs. two or three. Copper isn't cheap after all. If I have all the lights on in the shop, It may cost me 25 cents/hour. Not a bank buster.

    I'm always turning off lights when I leave a room in the house. Now that we've upgraded most lights to CF's, it doesn't have the same impact to the bill. Old habits die hard I guess.

    I've done more research and it looks like I should put in more fixtures. I'll post another drawing or two when I get done.

    Thanks to all for the input.
    Dave

  10. #10
    Join Date
    Jun 2007
    Location
    Vestal, NY
    Posts
    28

    New plans

    Since I need more light fixtures, I became concerned about routing my dust collection duct. Here are two designs I came up with. Instead of the 40 fixtures Wilbur came up with, I have 36. It should get me in ballpark of 100 foot candles, as long as the tubes are clean.

    With this one, I don't worry where the duct will cross the lights. I'll have to hang it below the tubes, but since it crosses the tubes at a right angle, the loss of light should be minimal.




    With this one, I can keep the duct flush with the ceiling, but I'm somewhat constrained with where I branch off. I would want to keep the duct near the middle of two light runs.



    Here is what the shop cross section looks like.



    Decisions, decisions...

    Dave

  11. #11
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    I vote for the second plan. I have a 20 X 24' shop and I planned for 28 bulbs. I have mine in 2 zones on 2 circuits. But I have another switch on one circuit that allows me to have only the lights above my work bench on, plus the other circuit. That's all I really used. In the middle of my shop I have more lights than the rest of the shop. And I actually need 3 more fixtures to have all 28 lights up and running. So I guess I'm running about half most of the time unless I need to work on the other side of the shop. I also have 5 pair of task lights. The only ones I really use are at the DP (on the side of the shop that stays darker) and sometimes the ones at the BS (on the fringe area in the middle). My wife thinks it's overkill, but the older I get (52) the more light I have to have. So if it's overkill now, it might not be in a few years.

    And nice shop! You have done well. I'd love to see some pictures of the interior! Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  12. #12
    Join Date
    Apr 2006
    Location
    Phoenix AZ Area
    Posts
    2,505
    I have nine 4 bulb fixtures with 40w bulbs and my shop is amazingly bright. I don't know that I would go with less, but I would not ever put more in a future shop.

    My shop is a 3 car garage measuring 20 by 30 with a 9 foot celing. the walls and ceiling are painted white. The fixtures are installed in three rows of three.

  13. #13
    Hi, I recently built a new shop also, Mt shop is 28 x 40 like yours. I have 10' ceilings. I ran my 4 ft floros very similar to your first plan. I hung them on chains so the DC ducting would be above the lights. I centered up 20 fixtures total on 2 switches, FWIW I have NO regrets. I can see just fine I would layout my fixtures the same way if I were to do it again.

  14. #14
    Join Date
    Jun 2007
    Location
    Vestal, NY
    Posts
    28

    Thanks for the input

    Thanks for the input guys. Great ideas coming in. I still haven't made up my mind yet, but I'm leaning towards the the 6 rows of 6 fixtures. I'll likely use the 8' four tube fixtures where possible. I may buy one tonight to get a good look at it. If I don't use it in the shop, there's always the garage.

    Could those of you who post your specific lighting setup please include your age (or at least over/under 50, 40 etc). I'm 46. While I am sensitive to bright light such as direct sunlight, I find I need more light than I did just a few years ago. I also need bifocals and I get eyestrain quicker. It seems the lighting requirements for woodworkers requires a tailored-to-the-individual approach.

    I found this table doing some research on the subject:
    http://www.elec-toolbox.com/usefulinfo/lighttip.htm

    It has good information on lighting requirements. While 50 to 100 foot candles is good general lighting for our shops, extensive detail work such as using a scrollsaw should have up to 500 foot candles of task lighting. I imagine a gooseneck fixture on the saw would be fine.

    Dave

    P.S. Jim O'Dell, I think you've seen some pic's of the inside of my shop already. I have an active thread on the Clearvue forum (userid "fullmetal") about designing and prototyping a CMS dust hood - which you also posted on.
    You can get a peek here of the shop inside:
    http://www.gallery2.clearvuecyclones...ps/fullmetal3/

    Not much to look at really. All unfinished, but the saw is cool.

    I'll be taking down the duct to insulate and hang OSB. I'll be moving the cyclone as well.

    I will post some inside pic's on this thread as I progress through the lighting.

  15. #15
    Join Date
    Oct 2005
    Location
    Helensburgh, Australia
    Posts
    2,700
    Why would anyone use flouros when you can buy COMPACT flouro bulbs. They don't take up anywhere the space, they don't use ballasts or starters, the tubes don't burn out in 12 months etc. With that number of lights in a shop you would be forever working on them when they get a bit old. I threw all mine out and have b\never regreted it.
    Chris

    Everything I like is either illegal, immoral or fattening

Similar Threads

  1. New shop lighting
    By John A. Scott in forum WorkShops
    Replies: 24
    Last Post: 05-11-2008, 8:13 AM
  2. Couple of questions about my small shop
    By Jared Minor in forum WorkShops
    Replies: 8
    Last Post: 03-05-2008, 1:36 PM
  3. Lighting for low headroom basement shop?
    By Wes Billups in forum General Woodworking and Power Tools
    Replies: 15
    Last Post: 09-20-2006, 11:00 PM
  4. Shop door design questions
    By Jim O'Dell in forum Design Forum
    Replies: 8
    Last Post: 04-25-2005, 6:31 PM
  5. Shop Lighting with Flourescent Floods
    By Bob Aquino in forum General Woodworking and Power Tools
    Replies: 13
    Last Post: 04-30-2004, 8:52 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •