Wes,
You never said what the circuit breaker is that's protecting this. If it's a 30A breaker, using 12/3 SO/SJO is a no-no - you need 10/3 SO/SJO.
Rob
Type: Posts; User: Rob Russell; Keyword(s):
Wes,
You never said what the circuit breaker is that's protecting this. If it's a 30A breaker, using 12/3 SO/SJO is a no-no - you need 10/3 SO/SJO.
Rob
Rollie,
I would agree that, given John's desire to leave the factory cord uncut, the best way in that situation is to remove the factory cord, save it, and install a cord with proper 240v plug. ...
Actually, the NEC has nothing to do with extension cords. The cord isn't part of the building wiring.
While it might sound odd, rewiring the connection at the saw's motor and building a special...