    Breaker capacity

    I just purchased a new 5 hp tablesaw and the motor is rated at 19.8 amps. The current wiring is 12 gauge on a 20 amp breaker. Will this be sufficient to start this tablesaw?

    I wasn't sure if the in-rush of power needed to start the saw will trip the breaker. If I need to correct the wiring I'd rather do it now than down the line.

    Thanks,
    Wes

  2. #2
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,281
    Hi Wes, unless the line voltage drop is excessive, you should be OK.

    If it starts, you're fine, and for home use I wouldn't bother going to a higher capacity circuit.

    Regards, Rod.

  3. #3
    Um, is that 19.8A at 220v? If yes, then you'll need to rewire yr feeder from the box. 5hps running 110v I think'd be a rare thing...

  4. #4
    Join Date
    Dec 2003
    Location
    SF Bay Area, CA
    Posts
    15,332
    Breakers are designed to not trip with "start up" or "inrush" high current situations. The large current draw lasts for a very short period of time (less than a second, usually) and that isn't long enough to heat up the circuit breaker thus causing it to trip.

    I'm with Rod, try it out first and see how it goes.
    Wood: a fickle medium....

    Did you know SMC is user supported? Please help.

  5. #5
    Join Date
    Feb 2003
    Location
    Topeka, KS
    Posts
    356
    I used 12/3 when I wired the shop. I'm only 8' from the subpanel so based on Rod's comments I think I'll go with what I've got.

    Thanks,
    Wes

  6. #6
    Join Date
    Dec 2003
    Location
    SF Bay Area, CA
    Posts
    15,332
    Wes,

    Shawn has a good point: is this 20 A circuit 240 V or 120 V? Still, give it the old college try and see how it goes.
    Wood: a fickle medium....

    Did you know SMC is user supported? Please help.

  7. #7
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    I've always heard that 5hp 220 motors need 10/2 wiring on a 30 amp (25 would work if it's available)breaker. Don't have a clue how the NEC reads for 5 hp motors. Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  8. #8
    Join Date
    Feb 2003
    Location
    Leesville, SC
    Posts
    2,380
    Blog Entries
    1
    Wes,

    For a 5 HP saw, you need to run #10 copper on 30 amp breakers... (Retired Electrician)
    Army Veteran 1968 - 1970
    I Support the Second Amendment of the US Constitution

  9. #9
    Join Date
    Feb 2003
    Location
    Commerce Township, MI
    Posts
    702
    "If it starts, you're fine, and for home use I wouldn't bother going to a higher capacity circuit."
    Electricity is not something to play with. Switch to a 30 amp breaker and #10 copper wire!

  10. #10
    Join Date
    Jun 2007
    Location
    Wichita, Kansas
    Posts
    1,795
    Quote Originally Posted by Wes Billups View Post
    ...
    I wasn't sure if the in-rush of power needed to start the saw will trip the breaker. If I need to correct the wiring I'd rather do it now than down the line...
    As others have said, table saws are easy starting and the startup load is normally of such a short duration that you're not likely to have any problem with nuisance trips from that cause.

    The FLA of the motor, 19.8 amps, is awfully close to the breaker rating, but you should be OK since you're not likely to be using the full 5HP for any extended period in a hobbiest application. If you do start making heavy cuts that use the saw's full power, then you might start seeing some nuisance tripping, but if you take it easy with the saw, you should be fine.

    I'm assuming that you'll be plugging the saw into an existing branch circuit. If you're hardwiring the saw into a dedicated motor circuit, I'd expect the local jurisdiction and inspectors to insist on a 30 amp circuit based on the saw's maximum HP rating.
    Last edited by Tom Veatch; 05-06-2009 at 11:03 AM.
    Tom Veatch
    Wichita, KS
    USA

  11. #11
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,281
    Quote Originally Posted by Chris Damm View Post
    "If it starts, you're fine, and for home use I wouldn't bother going to a higher capacity circuit."
    Electricity is not something to play with. Switch to a 30 amp breaker and #10 copper wire!
    That wasn't a sentence based upon no understanding of electricity. I'm an Electrical Technologist.

    A 30 ampere circuit is not needed for a motor with a load profile like a home table saw.

    If the 20 ampere circuit will start the motor reliably, the user is fine.

    Regards, Rod.

  12. #12
    Join Date
    Dec 2005
    Location
    Du Bois, PA
    Posts
    69
    A 20 amp circuit is only to be loaded to 16 amps, this is to protect the wire from intermitent spokes in current such as the starting current of a motor. I would change to a 30 amp curcuit with #10 wire.
    Last edited by Chris Padilla; 05-06-2009 at 4:06 PM.

  13. Quote Originally Posted by Bill Brady View Post
    A 20 amp circuit is only to be loaded to 16 amps, this is to protect the wire from intermitent spokes in current such as the starting current of a motor. I would change to a 30 amp curcuit with #10 wire.
    No. That's not what code states, and the rationale you listed is also incorrect. A circuit can be loaded to 100% of its rating with non-continuous loads. This is a design issue behind the code so that you don't deliberately load a circuit breaker to 100% capacity continuously. However, if the circuit breaker is listed for 100% capacity, then you are permitted to load it to 100% for its entire life. The circuit breaker is there to protect the wire, and the thermal trip curves take into account the applicable heating aspects of the wire so that it will always trip before the wire exceeds its thermal rating.

    Furthermore, a tablesaw is not considered continuous, and moreover, even when it is running, it rarely sees its full rated load.

  14. #14
    Quote Originally Posted by Rod Sheridan View Post
    That wasn't a sentence based upon no understanding of electricity. I'm an Electrical Technologist.

    A 30 ampere circuit is not needed for a motor with a load profile like a home table saw.

    If the 20 ampere circuit will start the motor reliably, the user is fine.

    Regards, Rod.
    My 5HP General seems to run fine on it's 20 amp 220 circuit.

  15. #15
    Join Date
    Oct 2006
    Location
    Mid Michigan
    Posts
    3,559
    I agree with Von on the #10 wire and 30 Amp breaker. I try to add that little margin for protection against error. If the breaker is only 8 feet from the tool why not just change the wiring and breaker unless it is a major amount of work. I also have a tendency to agree with folks that have been in the trade (retired electrician) and have had the experience.