I got my friend's 16" Zefam jointer running today with the upgraded static phase converter he bought for it. It comes up to speed in 3 seconds now and seems to run very smoothly. I wired it so we could use the machine's normal on/off switches. This SPC replaces a lower rated unit. When I installed that one I couldn't get power to the motor and traced it to a thermal overload on the contactor. I bypassed the contactor, temporarily, and the contactor closed when I pushed the start button and the motor started. I didn't fool with the overload today when I installed the new SPC, but I'd like to resolve the issue for peace of mind.
The contactor is a Telemecanique, made in USA which I didn't expect with that name:
Attached at the bottom of the contactor is this overload relay:
Which has this label on one side:
What's confusing to me is that the relay is rated for a normal range of 5.5 to 8 amps (now set at 8 amps, as I found it), but the motor has a FLA rating of 11.2 amps and draws around 10 amps when running with no load except turning the cutterhead. There is a reset button on the relay, the red button at the right in the photo, but it won't reset when I push it. The wires now connected to T1, T2, and T3 on the contactor were connected to the 3 lugs on the overload relay until I bypassed it.
The former owner ran it on 230 V 3 phase power. We're running it on 220V single phase power through a static phase converter. He claims it ran fine. If so, the relay must have been the appropriate size, though it seems undersized to me. This is a new motor, but of the same 5 HP rating and amp. draw (actually, marginally lower) as the one it replaced.
Anyone have any ideas of what's going on here? Any input is appreciated. Thanks in advance.