    Electrical Service - How Much is Enough?

    It looks as if my wife and I will be moving into a new house, which would allow me to expand my workshop from its current one-car garage size to an over-sized 2 car garage, and I will be hiring an electrical contractor to bring electrical service to the garage. (We are trying to finalize the purchase of a short sale house that has taken FOREVER, but that's another story!) If we are successful, and it now appears that we will be, I will need to decide if I should get 200 amp service or if a 100 amp will suffice.

    Following is a list of the larger stationary tools I either already have or plan on having some day. Of course, not listed, are all the smaller hand held tools and accessories most of us have in our shops. I am not yet aware of the amp requirement for the ductless HVAC I will have installed or that for the overhead lighting.

    Any opinions on the size of service I might require for a one man hobby shop? The total here is 158 amps not including the HVAC, the overhead lighting, the air filter, or the portable hand tools.

    Thanks.

    18" Bandsaw 10a 220v
    20" Planer 30a 220v
    12" Jointer 18a 220v
    Osc Edge Sander 18a 110v
    Oneida Cyclone 14.5a 220v
    TableSaw 13a 220v
    Drill Press 9a 110v
    Performax Drum Sander 9a 110v
    16" Bandsaw 11.5a 110v
    Air Filter ?
    Air Compressor 15a 110v
    Mitsubishi Split HVAC ?
    Lighting ?
    Festool Dust Extractor 10a 110v
    Regards,

    Glen

    Woodworking: It's a joinery.

  2. #2
    Join Date
    Feb 2003
    Location
    Commerce Township, MI
    Posts
    702
    It depends on how many machines you will be running at a time. My shop has 60 amp service and it the 14 years I have been working in it I have never had a problem. I have 9 8' 2 bulb lights, radio, 3 HP dust collector, 2 HP tablesaw, and a 1500 watt heater running maximum at any one time.

  3. #3
    Join Date
    Nov 2007
    Location
    Hot Springs, VA
    Posts
    765
    I agreed with Chris. Just recently I moved in a new shop and I have 80Amps subpanel. For an one man shop this is more then enough. My maximum load when I run air filtration system, DC 2hp, split AC, lights and one of the big tool are much less then my panel has.

    Ed.

  4. #4
    Join Date
    Oct 2007
    Location
    New Hill, NC
    Posts
    2,568
    100A should more than cover your needs. The mini-split ac consumes less than 15A (and as I recall less than 10).

    Typically in a home shop your "minimum" size would be based upon having your lighting, HVAC, compressor, dust collector, and largest equipment motor running simultaneous, plus a little bit extra.

    Personally I like having some good growing room, and would prefer the 100A over a 60 or 80A service.
    Last edited by Scott T Smith; 04-23-2010 at 8:28 AM.

  5. #5
    Join Date
    Jan 2008
    Location
    Bradenton, Fl
    Posts
    499
    It's better to add surplus power now than try to add it later! I have 150 amps now in a 1000 sq ft shop and I'm going to add another 300 next month. I'm glad I put in the 150 when I did as I won't have to worry about adding electric to the new area.

  6. #6
    Quote Originally Posted by Glen Blanchard View Post
    The total here is 158 amps not including the HVAC, the overhead lighting, the air filter, or the portable hand tools.
    No need to look at it this way Glen. Total amperage of the tools in your shop is generally irrelevant due to the fact that you'll never draw anywhere even close to 158 amps in your shop. Residential electrical systems are designed and installed based on realistic loads that will be drawn, not total capacity of the system itself.

    For example, I can legally put 42 circuits in a 200 amp panel. If each of those circuits has 20 amp breakers, that's a total of 840 amps! In a residential application there's just no way each of those circuits will be utilized at its maximum ampacity at the same time, therefore it isn't an issue.

    You've got a lot of 220v equipment, which draws less amperage since the load is shared between two phase conductors. That's good from a "total ampacity" standpoint. But it also requires two slots in the panel (A and B phase) for each receptacle you install, and that is the major consideration. Unless you only want to install one or two receptacles, you're going to need a heck of a lot of slots in that panel for all those 220v receptacles. My advice would be to have your electrician set a 100 amp subpanel in your garage, get one big enough that it has plenty of room for breakers, fed off your main panel. You really probably don't need 100 amps in my opinion, but it sure isn't going to hurt.

    200 amps would be ridiculous gross overkill.

  7. #7
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,278
    As others have stated, add up your lighting, HVAC, air compressor, cyclone and largest machine, then add a little more.

    I have a 35 ampere feeder for my shop,

    Cyclone 8.5A

    Saw/shaper 16A

    Since my shop is in the basement, lighting is fed from the main panel, compressor is in the garage so it's fed from the main panel.

    The tendancy is to go overboard on shop power, if you're like me you'll only run one machine plus the cyclone at a time.

    Plan for one machine that's larger than what you have, plan for the HVAC, compressor, cyclone, lighting, and add a little.

    Don't go crazy................Regards, Rod.

  8. #8
    Join Date
    Dec 2008
    Location
    Gibsons British Columbia Canada ( near Vancouver )
    Posts
    693

    Power needs

    Gentlemen:

    I have to chime in here.

    As an HVAC guy ( I understand electricity for the most part ) and the worst thing you can do is under power a shop.

    While you can say '' I will only be running XXXX , YYYY and maybe ZZZZ at the same time, and they only consume a total of 23 amps, a 50 amp service should suffice, right? Remember, this is a new installation that is subject to being inspected, and must be in compliance with all local codes etc., not a cobbled together shop.

    It is a total of the loads to some degree; however, another ( MAIN ) consideration is space in the panel! A 200 amp panel is usually relatively inexpensive to install ( the electrical contractor has to be in the loop as well as the distance to the main ) . You have at least 20 spaces spoken for in your initial assessment, and the electrical Inspector will add up the TOTAL load as well as spaces in the panel required when assessing the situation. The arguement of, '' I will only be using 23 amps at one time '' does not wash.

    As for the HVAC unit - it really depends on the tonnage required - it WILL be a 220v circuit, and it may easily be a 20 or 30 amp breaker required.

    My opinion would be to price both 100 and 200 amps, see what the difference is, and decide from there. Remeber, to upgrade later will be a whole lot more hurt than shelling out a couple hundred bucks now.

    Remember as well - allow a method to add wiring later - i.e.; don't finish around the panel with drywall all nice and neat. Have a removeable panel so you can get into the panel later, better yet, pull a few extra PVC drops into the panels so wire can be fished in later if need be.

    JMHO

    Dave Beauchesne

  9. #9
    Join Date
    Feb 2003
    Location
    Richland Wa.
    Posts
    784
    "200 amps would be ridiculous gross overkill".

    While this may be true, why not? I just recently went through this. My detached shop/garage was fed from the house through a 30 A sub panel. I was continuously tripping breakers, and whether it was or was not a safety problem, it just always bothered me that the house and garage were connected this way. The connecting wires were under ground, and under about 20' of concrete patio ran through ridiculously small conduit. Too small to pull larger wires through. So for peace of mind I decided the garage had to be on it's own service. The city ran new wires, and installed a meter on the garage and a licensed electrician installed a 200A breaker panel, and did some extensive inside wiring for me. I now have plenty of dedicated 220V circuits and a "ridiculously grossly overkill" worth of extra breaker room in the new panel, but so what. If I do ever need them they are there. Also the 200A service just wasn't that much more expensive than the 100.

  10. #10
    Join Date
    Sep 2007
    Location
    Bucks County, Pennsylvania
    Posts
    940
    If you add up the maximum load you will be using at any give time I think you will be surprised at how little it is.

    But, you get into a cost factor with labor being the major cost and in my case the ridicules permitting costs. A 60 amp panel will likely be more power than you will ever need but the relative cost of bumping up to a 100 amp panel is small because it is a very common size. It also allows you many more spaces than the smaller amp panels to provide individual breakers for various machines - if that is the way you want to go. My electrician thought I was crazy to want the 100amp panel - I felt the extra spaces were worth the cost.

    In my case I did not have to run the line all that far and by purchasing copper I was able to get in place with out any problem. Getting an aluminum feeder for a 200amp panel would have been impossible and overkill. And downrating the 100amp panel to 60amp service was a very small savings.

    My last work area had a 40amp panel -- and I never had any problem other than I had no extra spaces.

  11. #11
    I would like to chime in on a few things....I dont know if you can run a wire from your main to a sub at 200 amps?? I think you have to run a separate meter which means separate bill with sep taxes and fees every month.

    I have a 100 amp panel in a 1200 sq foot shop with 14 foot ceilings with LOTS of receptacles. LOTS of 220's and LOTS of lights. DC, 8in Jointer, 15 in 3 hp planer, 18 inch Bandsaw, did I mention LOTS of lights. I work alone for the most part but I did have my friends come over and work in the shop all together and I was able to run planer, DC, table saw, sander and all lights at the same time with no problem. Thats at 100 amp sub panel.

    BEst of luck...It is fun having ample power and receptacles where its needed...Much better than extension cords stretched everywhere.

    John G

  12. #12
    If it is permittable by your situation, get 400 A. You can easily do either a metered main or a simple sub panel and split all the non-shop motor loads (HVAC and don't forget dehumidification - helps keep that EMC where you want it).

    All that assumes you can't get 3 phase 120/208 V or any form of 480 V. If you can, you can safely drop the mains to 200 A.

    On my present shops I changed service 4 times. Total cost in excess of $20K. My fault. Stupid thoughts about saving some money. With a 400 A 3 phase 120/208 V Wye, I am in good shape for motors as large as 15 HP (planar and wide belt). Even then, it took some engineering to do the load balancing (that cost $500).

    What I am trying to say is get the biggest main you can and set it up as a metered main to keep your build costs lower.

    This site is great: http://www.allaboutcircuits.com/

    You can download the individual chapters. The one you need is: http://www.allaboutcircuits.com/pdf/AC.pdf


    Have fun.
    Last edited by Foras Noir; 04-23-2010 at 1:47 PM.

  13. #13
    Join Date
    May 2009
    Location
    Boston
    Posts
    1,740
    Easiest way is to ask the electrician when he comes over to see what he thinks. Since he will know the local codes, etc he'll be able to help you.

    My 2 cents is use a full panel instead of a sub-panel. More slots for breakers, etc.

  14. #14
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    The biggest thing I've seen in this is how many circuits/breakers are you going to use? I went to a 200 amp service to get the number of slots I needed. I would be fine with 100 amps, but I couldn't find a box with enough slots. I wanted a separate circuit for each of 8 220 runs, and 5 110 runs. And the 220 circuits take 2 slots each if you use full size breakers. I might have been able to get a 100 amp main breaker for this box, but since I had the power, (separate service from the pole) I went ahead and got the 200. I have a few slots available if I need to add anything. Unfortunately, no floor space to put it!! Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  15. #15

    Rant on Residential Contractors doing Shop Work

    I don't respond to posts on posts. But, I can't let this one go.

    If you ask a residential electrician what to do, make sure they know they will not get paid if you need to upgrade your service when the in-rush current from your HVAC trips your mains anytime your shop is in use. Seriously, non-shop motor loads will totally wipe out all your shop calculations.

    The problem with shops is not FLA (fully loaded amp draw) which is what people on this board talk about day in and day out. It does not matter in shop builds. The problem is in-rush current from low speed (say 1,700 to 3,500 RPM), high torque shop motors. I junked a 7.5 HP 3 phase 208 V air compressor because it pulled 150 A in-rush for 7 seconds every time it kicked. We changed the motor out to a single phase 208 V 5 HP motor frame equivalent and it drew 173 A for 9 seconds. That is not at all uncommon in home shop tools. Anything, I mean anything at all, which is single phase and over 2 HP will have insane in-rush. Please read the reference material I posted.

    Electricians without actual industrial motor control experience will not know how to even measure in-rush. Make them show you their test gear. Make them do a 48 hour logging run. If their approach is to read the motor plate (which is how residential electricians are trained), you will be back on this board asking how to upgrade the service.

    Residential electricians are not qualified for this job. They know nothing about low speed, high torque motors on shop tools. Your power company (if they work like the three I know well) will do the logging and help project your in-rush. They can size the service based on vastly greater experience. They also get no "bonus" income by coming back to upgrade your service.

    One last time, get the largest service you can. Make sure it is a metered main with at least two feeder breakers (one for shop loads, one for the rest). Everything else will get safer and less expensive.

    Your local "time and materials" electrician is the last guy I would ask about this problem. This entire line of argument is valid for all residential contractors. They know nothing about shop infrastructure. I speak from experience.

    Ok - I will go back to my Grey Goose and FOX news channel. I think Beck is on.