    I need to get my 220 volt Gast pump (Surplus Center) hooked up to a switch, but Home Depot didn't appear to have any 220v switches. What should I be looking for? Thanks

    Dan
    Eternity is an awfully long time, especially toward the end.

    -Woody Allen-

    Critiques on works posted are always welcome

  2. #2
    Join Date
    Dec 2006
    Location
    Fort Pierce, FL
    Posts
    225
    Dan,

    i am using a gast 220 pump and a 20A Double Pole Switch is all i needed.

    jim

  3. #3
    Join Date
    Jul 2005
    Location
    East of the Mississippi
    Posts
    3,807
    I got mine from McMaster-Carr
    941.44 miles South of Steve Schlumph

    TURN SAFE

  4. #4
    Join Date
    Oct 2006
    Location
    Harvey, Michigan
    Posts
    20,804
    Dan - got mine from Menards - 20A Double Pole Switch, # 3637535.
    Steve

    “You never know what you got til it's gone!”
    Please don’t let that happen!
    Become a financial Contributor today!

  5. #5
    Join Date
    Mar 2005
    Location
    Spokane, Washington
    Posts
    4,021
    Thanks for the quick replies.

    No Menard's out here, does it matter if it's only rated to 110v, or is it just necessary to have 20 amp double pole? Thanks

    Dan
    Eternity is an awfully long time, especially toward the end.

    -Woody Allen-

    Critiques on works posted are always welcome

  6. #6
    Join Date
    Jul 2005
    Location
    East of the Mississippi
    Posts
    3,807
    Dan, I don't know the answer to your question but wanted to offer one other thing I did. My lathe is 3 hp, 220 v so rather than running another 22o v circuit I added an additional outlet off of the existing outlet for the pump. It works without any problem. (Don't know about any code though)
    941.44 miles South of Steve Schlumph

    TURN SAFE

  7. #7
    Join Date
    Oct 2006
    Location
    Harvey, Michigan
    Posts
    20,804
    Dan - not sure how they are going to label it - but you are only going to have 120 volts per pole anyway.

    Also - I did the same thing as Keith - piggy backed another outlet off the 220 VAC for the lathe. Works fine.
    Steve

    “You never know what you got til it's gone!”
    Please don’t let that happen!
    Become a financial Contributor today!

  8. #8
    Join Date
    Jan 2008
    Location
    New Port Richey, FL
    Posts
    197
    a 110v double pole is 220v. just make sure it is a 20 amp switch. thats what 220v is, it is (2) 110v legs of power. thats why sometimes people think their clothes dryers heater is broken, in fact, one of their legs of power has gone down. when you go to wire it, NORMALLY with 220v, there are 2 hot lets, NORMALLY black and red, and a ground white. good luck, Chris

  9. #9
    I don't believe you really need a 20A switch for the Gast pump, but I think that's about all you'll find in a double pole single throw wall switch. I had to do some searching through the display, but I did find one at Lowes when I built my vacuum rig. If my math is right, that pump will only be pulling about 1 amp or less when running, so the 20A switch won't even be breathing heavy.

    And like the other guys above have done, I've got both my lathe and pump running on the same 220v circuit. I've got a single outlet on the wall, then use a 15' or so #10 AWG extension cord with a dual box and two outlets to accommodate the lathe and pump.

  10. #10
    Join Date
    Jan 2008
    Location
    New Port Richey, FL
    Posts
    197
    i have been talking to a lot of electicans on jobs i've been on, now i'm not saying that i wouldnt run an extension cord with (2) 220v outlets on the end, but it was explained to me that each 220v outlet has a dedicated breaker because if there is a short in the box with the 2 outlets in it, then the breaker at the box could possibly not trip therefore it could possibly burn your house down. this was explained with many technical terms i cant repeat, and i really dont know if i'm explaining it correctly, but basically to do it right, all 220v outlets need to have there own breaker in order to pass code.

    like i said, not saying i wouldnt use a 220v splitter, but i dont think it is the safest

    not an electrican, just picked a couple of their brains. good luck.

  11. #11
    Join Date
    Mar 2005
    Location
    Spokane, Washington
    Posts
    4,021
    Thanks for all of the replies. Fortunately, I have several 220 outlets in my shop, so as long as I'm not using all of the big machines at once, I will be in good shape.

    Dan
    Eternity is an awfully long time, especially toward the end.

    -Woody Allen-

    Critiques on works posted are always welcome

  12. #12
    Join Date
    Nov 2006
    Location
    Southwest Missouri
    Posts
    185
    I don't know about code, but to seems to me that by "piggy backing" on the same circuit you have a bit of a safety factor in that if the vacuum pump looses power so does your lathe and thus reduces the chance of a flying bowl. As was stated the vacuum pump has a low current draw so it's unlikely to overload the circuit.

  13. #13
    Join Date
    Sep 2009
    Location
    Blairsville GA
    Posts
    2,105

    Likewise, I also got my switch from HD

    I had to look also, but did find the double pole switches at HD. I'm pretty sure they did say on the switch that it was rated for 220, which is standard role of a double pole switch.

    Another option, one that I just purchased as a modification for my 3520, is one of several switches that Grizzly sells. I got an H8243 as a remote shutoff for the lathe...perhaps overkill and 'too easy' to accidently shut off for a vac system. A different option that would work well is like I got for my drill press... H8238. Search on Grizzly and that part number to see what they look like.

    I have no stock or other interests in Grizzly...just found that they have some good options on some stuff.

    By the way...if you go the route with the Grizzly switches...they fit real nicely on one of the metallic (or plastic if preferred) boxes that are used for mounting exterior floodlights, and available from most big-box hardware stores. They have a better capacity inside than the typical steel utility boxes, and have a clean exterior. If you need a pic...let me know.