    I am running a 5hp Delta dust collector (50-765) in a separate part of the building controlled by a remote control transmitter. The remote will turn the dust collector off, but I have to hit the remote again and physically turn the machine back on to get it running. Can I disable the magnetic starter so that I can turn the machine both on and off using the remote transmitter?

    John

  2. #2
    Join Date
    Apr 2013
    Location
    Okotoks AB
    Posts
    3,500
    Blog Entries
    1
    You need the mag starter to control the motor. The remote transmitter/receiver controls the mag starter. Does your remote have 2 buttons? If so, you need to wire the transmitter so 1 channel closes a start contact & the other opens the holding contact circuit. If your remote has only 1 button, you can use a toggle relay that switches to the on position on 1 pulse & then switches to the off position on the next pulse.

  3. #3
    Join Date
    Oct 2006
    Location
    Bloomington, IL
    Posts
    6,009
    What coil voltage is on the dust collector's contactor?
    Glad its my shop I am responsible for - I only have to make me happy.

  4. #4
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    It can be done, but it is tricky. Much easier would be to put the remote between the starter and the DC.

  5. #5
    Join Date
    Oct 2006
    Location
    Bloomington, IL
    Posts
    6,009
    You will have amperage issues going between the contactor and the 5hp motor Wade. That is not recommended
    Glad its my shop I am responsible for - I only have to make me happy.

  6. #6
    Join Date
    Aug 2009
    Location
    Lawton Oklahoma
    Posts
    512
    The remote is the Woodcraft Remote control transmitter switch and only has one button. I apologize for the ignorance on the Contactor voltage, the Dust collection system is 220v (I am not up to speed on electrical motors and contactors). This remote system is one in which the dust collection system plugs into the remote sensor and then that into the wall.

  7. #7
    Join Date
    Apr 2013
    Location
    Okotoks AB
    Posts
    3,500
    Blog Entries
    1
    I know exactly what your problem is, but a fix is probably beyond your level. Call an electrician & he will be able to wire the remote controller into the mag starter coil circuit. The power will need to go directly to the starter. None of the remotes that Woodcraft carries will safely handle a 5 HP motor.

  8. #8
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    Quote Originally Posted by Mike Heidrick View Post
    You will have amperage issues going between the contactor and the 5hp motor Wade. That is not recommended
    You can get them for 5hp on ebay for $20. Most are 3 phase, but there are few single phase mixed in. I put one on my 3hp activated by a X10 remote; worked fine for years. (good thing I didn't know it wasn't recommended)

    I presume he could use the Woodcraft thing to run it.
    Last edited by Wade Lippman; 07-21-2016 at 9:49 PM.

  9. #9
    Join Date
    Aug 2009
    Location
    Lawton Oklahoma
    Posts
    512
    Oddly enough it worked fine for a while. I had a separate issue with the drive rod in the motor. I had that fixed and since then it has not worked.