    Band saw power question

    I have a question about providing power to my 220/20A band saw. Can I change the plug to plug into a 220/30A electric clothes dryer outlet? Any issues? I recently moved and have had to set up in the basement of property that we are renting. Where I dont know how long we will be here (6 months or 6 years) yet, I was thinking this might be a good temporary solution. Any thoughts or feedback would be greatly appreciated.
    Willing to consider trades for Native American Artifacts (arrowheads and such) - Peace!

  2. #2
    Join Date
    Feb 2009
    Location
    Fort Collins, CO
    Posts
    946
    No problem doing that. Before my shop was wired, I used the clothes dryer outlet for 220 power. You might consider swapping the 30a breaker for a 20a breaker - just be sure to put it back when you move again so the next guy has enough amps to run a dryer. Never exceed the breaking amperage for a given wire gauge - you can go down but not up.
    Man advances just in proportion that he mingles thought with his labor. - Ingersoll

  3. #3
    Join Date
    Mar 2009
    Location
    Leominster MA USA
    Posts
    49
    Super! Sounds like a plan! Thanks
    Willing to consider trades for Native American Artifacts (arrowheads and such) - Peace!

  4. #4
    Join Date
    Feb 2003
    Location
    Washington, NC
    Posts
    2,387
    Quote Originally Posted by Jon McElwain View Post
    No problem doing that. Before my shop was wired, I used the clothes dryer outlet for 220 power. You might consider swapping the 30a breaker for a 20a breaker - just be sure to put it back when you move again so the next guy has enough amps to run a dryer. Never exceed the breaking amperage for a given wire gauge - you can go down but not up.
    Why should he consider changing the breaker? That is totally unneccessary.

    To avoid changing the plug on the bandsaw, make a adapter- a box with a 220V receptacle that matches the bandsaw plug and a dryer plug pigtail.

  5. #5
    Join Date
    Nov 2007
    Location
    Mid Missouri (Brazito/Henley)
    Posts
    2,769
    What Alan said! Leave the breaker as-is! The 20A (5 hp) load calls for a 30A circuit. Starting a motor cause an inrush surge that must be compensated for. A 20A breaker would no doubt constantly be tripping on the bandsaw's startup, or under heavy usage conditions.

    As to mating plugs, if the saw is close to the dryer receptacle, save time and money with a dryer pigtail to match. (for now)
    [/SIGPIC]Necessisity is the Mother of Invention, But If it Ain't Broke don't Fix It !!

  6. #6
    Howdy:

    One word of caution. Most dryers are 220V, yes, but they also have 120V control circuits and the motor.
    The dryer has connections for both 220V and 110V. If your saw is 220V only, you won't need the neutral wire, just the two line hots.
    Just be aware when you wire up the pigtail or temporary box.