    Twice in the past couple weeks I've tripped the 100A breaker that feeds my shop from the house panel. On the first trip, I assumed it was a power outage since we've been having them rather frequently this year. I was home alone and it was light enough out to do some cleaning so I did that for an hour or so then went in the house and noticed a ceiling fan running and found the tripped breaker. After resetting I went back out and resumed work without issue. The second time I went in the house right away and found the breaker itself was almost too hot to touch, and obviously wouldn't reset. After allowing it to cool while I ordered a new breaker (see below), I reset it and resumed work without further issue. Both times, I've been running my 3HP cyclone, using AC (2.5T central AC), lights on, and I've been using a power tool. Its possible the trip occurred on AC startup but I don't know. It was pretty hot out both days it happened and the AC seems like its been on more than off.

    The house panel is a Westinghouse (now Cutler Hammer) BR series. The breaker the guy before me installed is a Siemens or GE, forget which and I realized a while back it isn't rated for a CH panel. It been on my list to replace it but I haven't gotten around to it. I've ordered the proper replacement which I expect to get today. The shop panel also has a 100A main breaker. I hadn't thought to check if it was hot when I found the other.

    I do plan to stick a clamp on meter on there when I've got the cover off and start up everything to get an idea. But I'm wondering--is it likely that the breaker is the problem or am I just pulling too much through it? I've never noticed a breaker that is hot before which bugs me. If I'm just pulling too much I'll have to start leaving the air off when I'm actually working.


  2. #2
    Join Date
    Feb 2008
    Location
    Wake Forest, North Carolina
    Posts
    1,981
    Blog Entries
    2
    Matt,

    Any idea what was running when it tripped?

    100 Amps worth? If not, sounds like a problem with the breaker at the house or the feeder to the subpanel.

    Just re-read your post, It sounds like you might have been pretty close load wise.

    If you've got a clamp on amp meter, It would be easy enough to turn all that stuff on and amp out the feeder.

    PHM
    Last edited by Paul McGaha; 08-04-2011 at 3:03 PM.

  3. #3
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    A hot breaker screams fail to me... they do go bad, sometimes they're bad right out of the box.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  4. #4
    Join Date
    Mar 2003
    Location
    Monroe, MI
    Posts
    11,896
    The second time I know I was running the cyclone (22A rated), AC (25A fuses), lighting, (? but I'd guess <20A), and my drill press which has maybe a 1/3HP motor. All of this was on (AC may not have been running) for a while before the breaker tripped. I can't remember for sure what I was doing the first time but know I had the cyclone, AC and lights on. And again, it was after the cyclone had been on for a while.

    I definitely plan to check load with a clamp-on meter when I change out the breaker. I suppose one possibility is I have more 110 stuff on one leg than the other.

    Edit: Me too Dan--hopefully that's it but I knew it should be changed anyway. The breaker came in today's mail so now I just need to find the time to shut everything down and change it out. The one in the panel is >7 years old because it was there when I moved in. Probably 15 or so from when they built the barn.
    Last edited by Matt Meiser; 08-04-2011 at 3:17 PM.


  5. #5
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,287
    Matt, I'll buy you a beer if it's not a loose connection on the line or load side of your breaker.........Regards, Rod.

  6. #6
    Join Date
    Dec 2008
    Location
    Evanston, In
    Posts
    290
    What is the wire size from panel #1 to panel #2? Also distance?

  7. #7
    Matt,

    I had this problem years back , it turned out to be aluminum wire, I change the feed to cooper and with the same breaker and never had a problem again. You may want to check what type of wire was used.

    Rich

  8. #8
    Join Date
    May 2009
    Location
    Knoxville iowa
    Posts
    136
    I agree with loose connection, Check all connections, loose connection under load equals heating.

    Ive wired many motors and terminals the last 15 yrs at the power plant I work at, and seen alot of burned up connections and terminals due to heating of a loose connection

  9. #9
    Join Date
    May 2005
    Location
    Highland MI
    Posts
    4,527
    Blog Entries
    11
    Correct me if I am wrong, but don't breakers heat up as they get close to design load, and isn't it the heat generated in a bi-metallic strip at the design load that will trip them, as well as use of a magnetic coil to detect a short circuit? Not to say that Matt may have another issue as he doesn't seem to be near the design amperage. Feel your breakers on a heavily used circuit like your DC and they should feel warm if the load has been on long enough to heat up not just the bimetallic strip, but the rest of the breaker as well.

  10. #10
    Join Date
    Mar 2003
    Location
    Monroe, MI
    Posts
    11,896
    Well, I'll be retorting the connections when I change out the breaker. And since the existing breaker is the wrong type, it could very well have a bad connection on the buss in the panel, not to mention the load side. I'm not sure what the feeders are, but I'd guess aluminum on a 100a circuit run to an outbuilding.

    I'd rate this as "hot" not "warm".


  11. #11
    I think Rod is right on with the loose connection at the breaker...have seen it many times albeit most often on the old buss fuses. But I'd tell Rod it was a faulty/worn out breaker just so I could get that beer.


    Cheers, Mark.

  12. #12
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,287
    Quote Originally Posted by Mark Major View Post
    I think Rod is right on with the loose connection at the breaker...have seen it many times albeit most often on the old buss fuses. But I'd tell Rod it was a faulty/worn out breaker just so I could get that beer.


    Cheers, Mark.
    Mark, I would too, however I'm betting that Matt has more integrity than me..................Regards, Rod.

  13. #13
    Wires being aluminum, don't forget the "no-ox."

  14. #14
    Join Date
    Nov 2010
    Location
    Anchorage, Alaska
    Posts
    1,617
    Alimonum wire has a much larger thermal expansion coefficient than copper. The resulting deforming of the wire during heating and shrinkage of the wire during cooling has been traced to many house fires. Quite a number of years ago in Alaska aluminum wiring was outlawed and I remember hearing the trend was speading nationwide but I have no idea how far or how fast it went.

    As for me, I'd look hard at replacing the aluminum with copper, but YMMV.

    Jim Neeley, EE
    One can never have too many planes and chisels... or so I'm learning!!

  15. #15
    Join Date
    Mar 2003
    Location
    Monroe, MI
    Posts
    11,896
    Replacing is not an option for the sake of replacing. Its underground to the shop. I'd look at separate service before doing that because it could run from the pole to the shop without tearing up sidewalk, etc.