    Floor loading question

    I have a new house built to code. To make more room in my shop, I want to move my commercial weightlifting machine into my 3rd bedroom, which has a standard joist/plywood floor. The
    machine footprint is 4' x 4' and, with the weights, I estimate that it weighs 500-600 lbs. Since I weigh 240, the floor loading might be around 800 lbs when I am using it. Will this overload the floor?

  2. #2
    40 pounds per square foot is standard design loading on most residential floors. So we are looking at 800/16=50 pounds per square foot. Without your weight, you are looking at 600/16=less than 40# psf. Water beds tend to weigh about 40# psf. You may want to build a platform with 2 X 6 joist running perpendicular to floor joist to span more joist, and thus spread the load.

  3. #3
    Join Date
    Oct 2010
    Location
    N.Y.
    Posts
    325
    Is it a "real" bedroom - or an attic or loft converted into a bedroom ?
    If it was an attic converted, i personally would do more research on how the "floor" joists are constructed. If it was a normal bedroom then i would go by current floor load (or since Bruce Wrenn already did the math, follow that). You could also double check at your local building inspector, floor loads might be different around the country... If they have the time, they might stop out and give you a curtice look and their opinion.

    _

  4. #4
    Join Date
    Aug 2010
    Location
    Grants Pass, Oregon
    Posts
    57
    Quote Originally Posted by Joe Watson View Post
    Is it a "real" bedroom - or an attic or loft converted into a bedroom ?

    _
    It's a real bedroom on the first floor in the corner, so it rests on two outside foundation walls. If I locate the weight machine in this room, I'll put it about 2' from the corner of the outside walls on each side. Since I am an economist and not an engineer, I'm thinking about it this way. When we have a party, four guys that probably weigh 800 lbs. together stand in a four foot diameter circle talking and we don't go
    through the floor. Probably something wrong with this logic.
    Last edited by Andy Margeson; 10-02-2011 at 1:50 AM.

  5. #5
    Join Date
    Mar 2010
    Location
    Grottoes, VA.
    Posts
    905
    Quote Originally Posted by Andy Margeson View Post
    It's a real bedroom on the first floor in the corner, so it rests on two outside foundation walls. If I locate the weight machine in this room, I'll put it about 2' from the corner of the outside walls on each side. Since I am an economist and not an engineer, I'm thinking about it this way. When we have a party, four guys that probably weigh 800 lbs. together stand in a four foot diameter circle talking and we don't go
    through the floor. Probably something wrong with this logic.
    It'd be real easy if you had a basement.... However, you could still add additional bracing under that area in the craw space. Doing so would eliminate any potential saging of the floor, or worse.

  6. #6
    Join Date
    Jun 2004
    Location
    Middleton, Idaho
    Posts
    1,018
    Andy,

    You say your new house was built to code... Just remember "code" is minimum standards...

  7. #7
    Join Date
    Jun 2011
    Location
    Panama City FL
    Posts
    72
    It really depends on the layout of the room, span of the floor joist, other loads in the room, etc. The 40 psf is an unfactored live load, it is not the actual structural capacity of the floor. I highly doubt you will have a problem, as most residential structures end up over-designed, but without knowing the layout, dimensions, other loads, and framing member sizes, it is impossible to calculate the deflection of the floor.

  8. #8
    Quote Originally Posted by Sam Layton View Post
    Andy,

    You say your new house was built to code... Just remember "code" is minimum standards...
    From an inspectors' standpoint, all I can add to that is a big AMEN............

    Rich
    *** "I have gained insights from many sources... experts, tradesman & novices.... no one has a monopoly on good ideas." Jim Dailey, SMC, Feb. 19, 2007
    *** "The best way to get better is to leave your ego in the parking lot."----Eddie Wood, 1994
    *** We discovered that he had been educated beyond his intelligence........
    *** Student of Rigonomics & Gizmology

    Waste Knot Woods
    Rice, VA

  9. #9
    Join Date
    Feb 2003
    Location
    McKean, PA
    Posts
    15,649
    Blog Entries
    1
    For less than the cost of your insurance deductable you can hire a structural engineer to review your siyuation and give you an answered based on fact and calculation. Without details of how the foors and walls are actually structured any ideas offered sight unseen are purely speculation.
    Lee Schierer
    USNA '71
    Go Navy!

    My advice, comments and suggestions are free, but it costs money to run the site. If you found something of value here please give a little something back by becoming a contributor! Please Contribute