All, I was hoping I could pick your brains, as I have become rather confused about what is required. Here's the facts:
The tool: Vintage Unisaw
The Motor: Baldor WWL3606 3hp 230v single phase, 15.5FLA, 5.x no load amps.
The current starter (that I already had when the 1hp bullet motor was installed): Square D NEMA size 00, 240v coil, with heaters rated at about 9FLA if I am remembering correctly.
Current status: I did a lot of research on various sites that led me to believe my current NEMA size 00 starter was not appropriate and that I needed a new Size 0 or Size 1 starter with the appropriate heaters. However, in my excitement I wanted to give the new Baldor a test run so I decided to give it a go with my current starter (figuring the worst that would happen is I would trigger the overload). Well I started and stopped the saw probaby 20 times, and made several test cuts in 4/4 white oak and she just kept humming along.
The question: Am I just asking for trouble running this with the size 00 starter? This is one of the Square D units that are way overbuilt, and retailed for $300+ when new, not one of the low dollar modern asian specials. This saw is used in a hobby shop setting for only an hour or so per week at the most. I'm fine with spending the money on a new (used) starter and the required heaters, but I find myself wondering if it is truly required.
Thoughts?