    Lights Dimming?

    So I am throughly confused right now as to why lights are dimming when I turn on one of my tools.

    I just moved into a new house and this is my first experience with a subpanel.

    The subpanel is running off of a 60 amp circuit breaker on a main panel which is rated for 200 amps.

    My bandsaw is hooked up to a 15 amp circuit breaker on the 60 amp subpanel.

    All of the wiring inside the house is coming off of the main panel. The garage is only hooked up to the subpanel.

    When I turn on the bandsaw, the lighting in the house slightly dims for a second. Any ideas as to why? Any ideas on how to remediate this?

  2. #2
    Join Date
    Feb 2003
    Location
    Auburn, WA
    Posts
    135
    What is the HP rating of your bandsaw motor? Does this occur when you turn on another tool? What else is hooked into that 60 amp circuit? Are you turning on a DC when the bandsaw motor turns on?

  3. #3
    Join Date
    Mar 2008
    Location
    Palatine IL
    Posts
    257
    I am just setting up the shop, so the bandsaw is the only thing that is being turned on. I have not tried another tool. It is only a 14" bandsaw.

    There is technically a heater on that 60 amp line, but it wasn't running at the time.

    At most there was 600W of lighting running and the 14" bandsaw.

    Also, interestingly enough, the lighting in the shop (on another 15 amp circuit) does not flicker or get affected by the bandsaw being turned on.

  4. #4
    Join Date
    Jun 2010
    Location
    Beaverton, OR
    Posts
    444
    I have a similar setup except that my lights are from the sub panel too. Pretty much any 120V 1.5HP motor load turned on will cause a slight dimming of the lights for just a moment. I don't think there is any getting around it without installing some monster capacitors.

  5. #5
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,295
    Hi Adam, let's do some basic calculations assuming your bandsaw motor draws 10 amperes at full load.

    Depending upon the motor, the starting current could be in the 70 to 150 amperes range for a second or two.

    Adding 70 to 150 amperes load to your electrical service will cause the voltage to dip, in proportion to the increased current.

    So your band saw motor starting current is causing the voltage to dip, on the supply carrying that bandsaw.

    If your kitchen lighting is on that same pole, it will dim, your shop lighting may be on the other pole and it won't experience the voltage reduction.

    Regards, Rod.

    P.S. Convert your bandsaw to 240 volts and the voltage reduction will 1/4 of the percentage it is now.

  6. #6
    Join Date
    May 2008
    Location
    MA
    Posts
    2,264
    And when that surge hits, all of the current gets redistributed via 'path of least resistance'. Meaning that its easier for it to route to the bandsaw or garage lights, than it is for it to route to the house lights. It doesnt necessarily have to be two different poles.

    Its ironic - because it likely means larger wires and easier path to the garage lights than it means to the main lights.

    Another explanation might be the type of light? Are there differences in the type of light in the house vs the garage? Some lights might tolerate a voltage drop more easily than others (Im imagining a flourescent, with a ballast/transformer having the ability to hold better than a pure incandescent)

  7. #7
    One way to think about it is with a plumbing analogy. If you have tubing that is too small in your house, when someone flushes the turlet while you are in the shower, the water goes hot.

    It's about the same thing with the wires. If you try to get too much juice through the wires, the voltage drops. Also, everyone thinks about what size wire is good for a certain number of amps. This prevents heating and fires. There is also the length issue; as the wires get longer, the resistance goes up, causing greater voltage drops during an inrush.

  8. #8
    Join Date
    Mar 2008
    Location
    Palatine IL
    Posts
    257
    Quote Originally Posted by Rod Sheridan View Post
    Hi Adam, let's do some basic calculations assuming your bandsaw motor draws 10 amperes at full load.

    Depending upon the motor, the starting current could be in the 70 to 150 amperes range for a second or two.

    Adding 70 to 150 amperes load to your electrical service will cause the voltage to dip, in proportion to the increased current.

    So your band saw motor starting current is causing the voltage to dip, on the supply carrying that bandsaw.

    If your kitchen lighting is on that same pole, it will dim, your shop lighting may be on the other pole and it won't experience the voltage reduction.

    Regards, Rod.

    P.S. Convert your bandsaw to 240 volts and the voltage reduction will 1/4 of the percentage it is now.

    Here is a diagram of how the wiring is laid out:

    Drawing1.jpg

  9. #9
    Join Date
    Nov 2007
    Location
    Glenelg, MD
    Posts
    12,256
    Blog Entries
    1
    Adam,

    I'm going to take a stab at it and say the workshop lights are on one phase, and the bandsaw and kitchen lights are on the other... hence, the kitchen lights dim when the bandsaw kicks in, but not the workshop lights.
    Hi-Tec Designs, LLC -- Owner (and self-proclaimed LED guru )

    Trotec 80W Speedy 300 laser w/everything
    CAMaster Stinger CNC (25" x 36" x 5")
    USCutter 24" LaserPoint Vinyl Cutter
    Jet JWBS-18QT-3 18", 3HP bandsaw
    Robust Beauty 25"x52" wood lathe w/everything
    Jet BD-920W 9"x20" metal lathe
    Delta 18-900L 18" drill press

    Flame Polisher (ooooh, FIRE!)
    Freeware: InkScape, Paint.NET, DoubleCAD XT
    Paidware: Wacom Intuos4 (Large), CorelDRAW X5

  10. #10
    Quote Originally Posted by Dan Hintz View Post
    Adam,

    I'm going to take a stab at it and say the workshop lights are on one phase, and the bandsaw and kitchen lights are on the other... hence, the kitchen lights dim when the bandsaw kicks in, but not the workshop lights.
    Instead of phase, the word should be "other side of neutral." A three wire service has a hot, neutral and another hot in addition to a ground, all of which are SINGLE phase. I have a 1/2 HP water pump that dims only some of the lights when it kicks in. There is no 14 ga stuff anywhere in my place.

  11. #11
    Quote Originally Posted by Bruce Wrenn View Post
    Instead of phase, the word should be "other side of neutral." A three wire service has a hot, neutral and another hot in addition to a ground, all of which are SINGLE phase. I have a 1/2 HP water pump that dims only some of the lights when it kicks in. There is no 14 ga stuff anywhere in my place.
    All just what you want to call it, but there are two phases with respect to neutral or ground in a "single phase" supply- the two hots are 180 degrees out of phase to each other when referenced to ground, if they were not when you measure between the hots with a juice meter you would get 0 volts, and there would be no reason for the juice to flow.

  12. #12
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,295
    Thanks Adam, that's what I understood.

    As I said, I expect that your bandsaw and kitchen lights are on one pole, the shop lights on another............Perfectly normal occurence.......Rod.

  13. #13
    Join Date
    May 2005
    Location
    Highland MI
    Posts
    4,528
    Blog Entries
    11
    And you might notice a bit more dimming with the bandsaw than other tools as you need to spin up those 2 heavy wheels, so the high starting current lasts a bit longer than with other tools. Probably just a flicker with your TS.

    I understand the phase thing, I just wish it worked out that convention said that 120 is single phase, 240 is two phase and three phase wye or delta is, well, three phase. It would just make sense in discussions like this. I mean 240 is two 120s out of phase with each other, so it would make sense to call it 2 phase. I'm sure an EE could chime in with a full discussion as to why it is not 2 phase.
    Last edited by Ole Anderson; 12-06-2012 at 9:34 AM.

  14. #14
    Join Date
    Dec 2010
    Location
    NW Arkansas
    Posts
    1,957
    Blog Entries
    1
    So, I agree with the above posters, kitchen lights and BS are drawing power from same side of the main panel. Solution is to live with it, or if motor can be changed to 240V change it and add receptacle if you don't have one, or at the sub panel (assuming it has 240 coming in) change wiring sides for the outlet you are using. If only 120V coming in, you would have to change at the main breaker, this may make your garage dim, but your SO may not give you as much grief if her lights are not dimming One thing to look at is to see if your main box is evenly distributed. In other words, are there close to the same number of breakers on both sides.

  15. #15
    Join Date
    May 2008
    Location
    MA
    Posts
    2,264
    Quote Originally Posted by Rod Sheridan View Post

    As I said, I expect that your bandsaw and kitchen lights are on one pole, the shop lights on another............Perfectly normal occurence.......Rod.
    Laughing at myself Rod. By 'pole', I took this to mean the physical pole at the street and couldnt understand what you meant!

    'Leg' worked better for me. Or 'phase', or spelling it out as 'other side of neutral' got me clued in.....

    In any event, a highly likely culprit.

    If he just switched which side the bandsaw breaker was snapped into, would this be a simple way to test this theory?