Thread: 220V electrical lines, what amperage?

  1. #1
    Join Date
    Jul 2008
    Location
    Gaithersburg, MD
    Posts
    84

    220V electrical lines, what amperage?

    I was working on two 20A 110V circuits in my shop for some time. It is not
    that bad but I always felt limitations in choosing my tools. Finally, I need new
    cyclone dust collector and needs on better electrical lines. Even those (CD)
    which will be enough for me require 30A because they suck too much power on
    start up. I am deciding on getting two 220V circuits. Will 20A be
    enough? I know it is enough for DC, but what if I decide to buy, let say
    Hummer 4HP table saw, will it work on 20A? I do not want overspend (who
    does?) for overkill, but definitely would be good to have some room ...
    What your thought? My shop is small one car garage and I do not run many
    machines simultaneously. Basically, one machine + DC.

  2. #2
    Join Date
    Mar 2012
    Location
    Taylors, SC
    Posts
    223
    Hi Yuri,

    When I built my shop last year, I put several 20A 220v circuits in for tools. One of them was dedicated for dust collection, which I have not purchased yet. In the little bit of research I've done on dust collection so far, I've realized my options would be far greater if I had made that dedicated circuit 30A. 3hp is about the limit of 20A. You'll still have decent options but they'll be somewhat limited.

    Hope this helps.

    [EDIT] Oh, and I forgot to mention that #10 wire is not that much more than #12 cost wise. Of course this depends on how much wire you need. The breakers should be the same cost. You can have 10 gauge wire and use a 20amp breaker on the circuit but not 12guage wire with a 30A breaker. That would be bad.
    Last edited by John Donofrio; 01-18-2013 at 3:17 PM.

  3. #3
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    There is no way to be sure.
    Rule of thumb is that 3hp will run on 20a, but not always.
    My new Griz 3hp Cyclone says it requires a 40a circuit, though most people get away with 30a.
    Highly unlikely a 4hp will work on 20a, but maybe.
    The safe bet is to ask the manufacturer.

    Assuming you have adequate power (and it is prudent to check that first...) A 30a circuit isn't much more work than a 20a circuit. You can always put in #10 with a 20a breaker and change to a 30a if you need to later on. A 40a circuit IS more work; #8 just isn't user friendly.

  4. #4
    Join Date
    Jul 2008
    Location
    Gaithersburg, MD
    Posts
    84
    Yes, I know that cost wise #12 vs #10 wire is not is not big, but ... If I will use 30A, I need to put corresponding receptacles, conduits has to be bigger, #12 wire is already stiff and #10 will be even worse, and that lead to additional difficulties. In the end it really makes it harder. I know for sure that one line used for DC (thinking Grizzly G0449 2 HP) will be enough. As for other, dedicated for machinery ...
    Strangely, I checked spec on Hammer K3 saw, and they do not provide numbers on amperage, just say 4HP.

  5. #5
    Join Date
    Dec 2005
    Location
    Central Ohio
    Posts
    336
    If you're thinking 4 HP+ tools might be a possibility, I'd just go ahead and run #10 gauge wires for 30A/240v. Might as well put 30A breakers in too, since the wire is rated for that.

    Tearing out #12 gauge wiring and replacing it will be more expensive than just running #10 gauge in the first place.

    Edit:
    See for an amp draw/HP chart: http://frentzandsons.com/Hardware%20...onsHdweRef.htm

    Edit2:
    Even more detailed and precise: http://www.cerusind.com/catalog/docu...ngFormulas.pdf
    Last edited by Andy Fox; 01-18-2013 at 3:41 PM.

  6. #6
    Join Date
    May 2008
    Location
    MA
    Posts
    2,260
    Quote Originally Posted by Andy Fox View Post
    If you're thinking 4 HP+ tools might be a possibility, I'd just go ahead and run #10 gauge wires for 30A/240v. Might as well put 30A breakers in too, since the wire is rated for that.

    [/url]
    This was my solution. I started out running a mix of 20a and 30a. But then added a 5hp upgrade option. Then thought, what if I rearrange, then I no longer have the 30a in the spot I need it. So I just pulled #10 and put 30a on everything.

    Then there was a question on whether the cord from the machine to the wall was protected....... (i can sometimes do this with a breaker, but only if I have the 220 stuff on a separate breaker each, which I do not)

    We will see what Mr Inspector thinks......

  7. #7
    Join Date
    May 2008
    Location
    Central Square, NY
    Posts
    243
    For what it costs, I use 10 gauge for all 220 circuits and 12 gauge for all other circuits. My thought is it will meet my needs now and in the future; electrical safety aspect and over all just a good investment.

  8. #8
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    I did the same thing Bud did. I even have my 1 1/2 HP contractor saw on a 30 amp line. I'd go ahead with the 10 gauge and go ahead and use 30 amp fixtures. The breaker is for safety of the wiring so you don't burn the house down right? It isn't sized for covering a problem that might crop up in the motor. Do it once, do it right. Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  9. #9
    Running 10 gauge sounds great, until you buy a tool that requires 8 gauge.

  10. #10
    Quote Originally Posted by Carl Beckett View Post
    ...........Then there was a question on whether the cord from the machine to the wall was protected....... (i can sometimes do this with a breaker, but only if I have the 220 stuff on a separate breaker each, which I do not)

    We will see what Mr Inspector thinks......
    If the machine is pre-wired with a cord-and-plug, Mr. Inspector doesn't have anything to do with it. The presence of whatever equipment you wish to utilize is not mandatory.
    *** "I have gained insights from many sources... experts, tradesman & novices.... no one has a monopoly on good ideas." Jim Dailey, SMC, Feb. 19, 2007
    *** "The best way to get better is to leave your ego in the parking lot."----Eddie Wood, 1994
    *** We discovered that he had been educated beyond his intelligence........
    *** Student of Rigonomics & Gizmology

    Waste Knot Woods
    Rice, VA

  11. #11
    Join Date
    May 2008
    Location
    MA
    Posts
    2,260
    Quote Originally Posted by Richard Jones View Post
    If the machine is pre-wired with a cord-and-plug, Mr. Inspector doesn't have anything to do with it. The presence of whatever equipment you wish to utilize is not mandatory.

    Well of course the equipment is not all pre wired with 30a plugs. Some is 2hp. Some is 3hp. A 4.5 hp. A 5 hp. (5hp is the biggest on these circuits). So all the plugs had to be changed to 30a to plug in anywhere. In order to protect this section, the machines would all need the wiring between the plug and the motor upgraded, no? Or maybe since these are not buried in and insulated wall, the insulation factor is different and still ok for the higher current?

    (now to be clear, I wired all 110 with 12ga, and all 220 with 10, and changed the 220 machine plugs to 30a. But I don't actually know if this is legit)

  12. #12
    Join Date
    Apr 2005
    Location
    Central MA
    Posts
    1,591
    You're doing fine Carl, don't over think it. The function of the breaker ends at the face of the outlet, the code does not cover cord and plug equipment. For what it's worth, I run my 5 hp bandsaw on a circuit protected with a 20 amp breaker and I have never had a trip. The breaker does complain a little sometimes (it buzzes on startup) and I should probably change it out to a 30 (the circuit is wired with #10) but then I'd have to change the receptacle and all of the cord caps on the other machines that share the outlet. I like 6-20 cord caps, no twist locks in my shop ever.

  13. #13
    Join Date
    Jan 2007
    Location
    Davis, CA
    Posts
    278
    Similar to several above, I used 10 gauge for all my 220 lines. I use 20 A breakers and outlets for all equipment 3 hp or less. For the electric heater I used 30 A. For the line that has multiple outlets on it I used bigger boxes where there is a line in and a line out to make it easier to work with the heavier gauge wire. I plan on upgrading to a bigger bandsaw and bigger jointer/planer and will switch out those breakers and outlets when i do. Doing it over again I would have used 30 A breakers and outlets everywhere.

  14. #14
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,278
    [QUOTE=Yuri Sadykov;2041675]Yes, I know that cost wise #12 vs #10 wire is not is not big, but ... If I will use 30A, I need to put corresponding receptacles, conduits has to be bigger, #12 wire is already stiff and #10 will be even worse, and that lead to additional difficulties. In the end it really makes it harder. I know for sure that one line used for DC (thinking Grizzly G0449 2 HP) will be enough. As for other, dedicated for machinery ...
    Strangely, I checked spec on Hammer K3 saw, and they do not provide numbers on amperage, just say 4HP.[/QUOTE

    Yuri, I have a Hammer B3 Winner and an A3-31 J/P.

    In Canada, they are limited to a 20 ampere feeder, I happen to run mine on a 15 ampere feeder, it's been 4 years, some day I may upgrade to a 20 ampere circuit...............Rod.

  15. #15
    Didn't even consider that I might need more than a 30 amp circuit when I got my G9983 widebelt sander, it is 5 hp, but the book said I needed a 40 amp circuit, so had to install a 40 amp breaker, #8 wire, to run the thing. According to the gauge, it never approaches 40 amps.