Hi all,
I acquired a new old stock VFD recently, and have everything wired up. But, I'm having a few difficulties.
Make/Model: Dana / Warner Electric Nextdrive, model SC4202, 2HP, 1ph or 3ph in, 3ph out
I'm attempting to wire some controls for easier control. I have a forward-off-reverse switch, and a 10k pot. These controls are the same components as I've used in my other VFD setup.
My connections are as follows:
Switch
right (forward) terminal = terminal 9 (run)
centre terminal = terminal 6 (digital common)
left (reverse) terminal = terminal 11 (reverse)
10k Potentiometer
Right terminal = terminal 4 (+10V supply)
Wiper (centre) = terminal 3 (VIN - Spd Ref)
Left terminal = terminal 2 (Analog common)
In addition, there are 2 notes in the manual:
Note 1: Connection between terminals 6 (digital common) and 7 (external trip) is required for any drive operation. When the drive is running, opening this connection results in a drive fault (External trip)
Note 2: Connection between terminals 6 (digital common) and 8 (stop) is also required to run the drive. Install any stop interlocks that are required. Opening the stop circuit when running will cause the drive to ramp to a stop.
To address these, I connected an SPST on-off switch, with the following connections:
Left terminal = digital common AND external trip (Giving the required electrical connection between these two terminals - see note 1 above. I think this might be wrong, but I'm not sure how it should be wired instead)
Right terminal = stop
When I switch on, I can tell the VFD to start the motor on the keypad, but the forward-off-reverse switch does not work (I have changed the setting in the VFD to tell it to accept a control signal from other than the keypad). The potentiometer does vary the speed, but it goes through the entire range from 0rpm to 1800rpm within about 1/10 of a turn.
So, a few questions for this electrical numptie:
1) I'd prefer to lose the SPST on-off switch altogether, but I'm not sure how to do that while satisfying notes 1 and 2 above?
2) Can anyone suggest what's wrong with my wiring? I'm guessing that something with digital common, external trip and stop is preventing the on-off-on switch from working properly.
3) Can anyone suggest how to fix the potentiometer speed control, to use a full turn of the dial?
Thanks in advance,
Lee