    Yet another Electrical question/request for advice

    The new shop is coming along nicely. Basically it is a brick, one car garage about 12 feet wide by 24 feet long, 10 feet from the house, and maybe 20 feet from the houses service panel.

    The service panel on the house is 100 amp service. The garage has no service yet. I am looking at putting a sub panel in the garage to handle the shop requirements, which are as follows....

    1) 110/220 table saw

    2) 110/220 Inca Jointer planer.

    3) 6 new outlets evenly spaced around the perimeter of the shop for various smaller tools.

    4) Power for shop lighting, say 4 8' floresents?

    So I know that a subpanel is needed. My question is, If I am pulling power from the house, how do I configure the set up?

    Is the 100 amp service at the house, enough to also power the shop requirements? (two 220 vac circuts, shop lighting, and multiple shop outlets?)

    I will go into the code issues and permitting etc, once I get an electrition out to give bids. But what I am trying to do here with this post, is to get a feel for what I might be up against.

    Is a 100 amp service panel, that does have space left in it, enough to power the shop safely?

    If so, what does that configuration look like in your estimation? Again, I am going to have an electrition come out and bid this out, and do the work. Just looking at what needs to happen to get power to the shop.

  2. #2
    Join Date
    Jan 2004
    Location
    Lewiston, Idaho
    Posts
    28,556
    John,

    IMO 100 amp service is not enough for today's house and certainly not big enough for a shop and house IMO. I had that arrangement in my home in a Chicago suburb with a basement shop. Running the tablesaw in the basement actually pulled down the size of the television picture in the upstairs living room.

    Check with your local utility company. When I built my shop here in Idaho a few years ago, the utility company added a separate power run to my shop. The shop is on it's own meter and has it's own 200 amp service panel. The utility company didn't charge for running power to the shop. I get one bill with 2 different meter readings.

    My cost was the service entry, meter base, service panel and wiring. I bought the materials locally and wired the shop myself with everything inspected for code compliance.
    Ken

    So much to learn, so little time.....

  3. #3
    Join Date
    Oct 2014
    Location
    Wheat Ridge Colorado
    Posts
    170
    Quote Originally Posted by Ken Fitzgerald View Post
    John,

    IMO 100 amp service is not enough for today's house and certainly not big enough for a shop and house IMO. I had that arrangement in my home in a Chicago suburb with a basement shop. Running the tablesaw in the basement actually pulled down the size of the television picture in the upstairs living room.

    Check with your local utility company. When I built my shop here in Idaho a few years ago, the utility company added a separate power run to my shop. The shop is on it's own meter and has it's own 200 amp service panel. The utility company didn't charge for running power to the shop. I get one bill with 2 different meter readings.

    My cost was the service entry, meter base, service panel and wiring. I bought the materials locally and wired the shop myself with everything inspected for code compliance.
    Thanks Ken,
    Good idea to contact xcell, and see what my options are there. one of the other things I was considering, was a new meter and an upgrade to 200 amp service to the house. Then splitting off what I needed for the sub panel.
    Again, the proposed power requirements for the shop would be sort of "light weight". Nothing on the order of 3hp unisaws or dust collection, everything is 110vac except for the Inca and the table saw.

    So it looks as though a 200 amp service is a minimum I guess?

  4. #4
    Join Date
    Jul 2007
    Location
    Seattle, WA
    Posts
    1,495
    For your shop tools, make sure to look at the amperage as well as the voltage. It's impossible for us to recommend the panel size without it. Make sure to account for start-up amperage too- you need to add some head room since motors often draw a lot more upon startup than they do when they're at cruising altitude.

    At a minimum, I imagine you would be running your lights, an A/C or heater, a dust collector, and one machine at any given time. You need to size your requirements based on that demand, plus probably 20-30%.

    My layman's understanding of a sub-panel is that it's not magic in terms of creating more power. You're still simply limited a total of 100 amps. So I agree with Ken- I really don't see a way for you to run a shop without some kind of total electrical service upgrade. And while you're at it, you really should consider giving yourself a lot more headroom. You may want to upgrade to bigger machinery in the future- it would really stink to have to redo your electrical again to do that.

    I have 200 amp service to my 1,500 sqft and I only have two slots left in my panel. I'm planning moving my shop from an out-building on my parents' property to a "new" shop in the basement. I will have no choice but to get a second meter, but I'm thinking about doing 200 amps to my new basement shop even though my current shop has 100 amp service and running 30 amp circuits and 10 guage wire to each of my 220 volt machines, even though only my DC and heater require that much power (all of the rest only need 20 amps max). This way I can upgrade my outlets for bigger machines that I'll talk my wife into someday. ;-)

  5. #5
    Join Date
    Jan 2010
    Location
    Lafayette, Indiana
    Posts
    1,379
    You should check with someone who knows the codes in your area. You might get the utility company to do as Ken described - run a separate meter to your shop. I doubt that they would run anything less than 100 amps which for what you describe as the plans for your shop is more than adequate. If you are going to run a sub-panel off your main panel in your house, I'm guessing (emphasize guessing) that your local code may require you to upgrade your house service to 200 amp. You could likely get by quite easily with a 60 amp sub-panel in your shop. A 15 amp circuit for your lights, a couple of 20 amp circuits for your outlets. I'd want to size the sub-panel to support expansion to allow for one or two 20 or 30 amp 220v circuitis just in case you grown into a 220v table saw, band saw, planer, jointer or dust collector.

  6. #6
    Also, don't just plan for what you have now, but what you could have in the future. Just because you don't have any terribly power-hungry tools at the moment doesn't mean that in a year or two, you might not. Always get more than you think you need because you never know what tomorrow might hold.

  7. #7
    Join Date
    Oct 2014
    Location
    Wheat Ridge Colorado
    Posts
    170
    Quote Originally Posted by Brian Henderson View Post
    Also, don't just plan for what you have now, but what you could have in the future. Just because you don't have any terribly power-hungry tools at the moment doesn't mean that in a year or two, you might not. Always get more than you think you need because you never know what tomorrow might hold.
    All great responses. Thanks guys. It should me mentioned, that there will be major changes in the not too distant future. A new garage/shop will be in the offing in the next 2 years or so. So the plan I am working on now, is just a stop gap until the new space is built.Still, the 200 amp main service vs. a seperate metered drop is one to ponder. I think that the 200 amp upgrade to the house, with a sub panel to the garage, is probably the best route right now just as Joe described.

  8. #8
    Join Date
    Mar 2007
    Location
    Fort Collins, Colorado
    Posts
    327
    When we moved into our house 30 years ago, it only had 100A service panel. Our builder supposedly cut corners on the last phase, since our model was supposed to have 150 or 200A service, and the smaller models had 100A service. I had room in the main panel, and an electrician put a 60A breaker in the panel to feed a subpanel in the basement for my shop. When we added AC to the home a few years later, the electrician said we needed to upgrade. He installed a much bigger panel, but put in a 150A main breaker. Since he had bid the job, and could not raise his price, I think he settled for what he could get away with (150A vs, 200A). We have several spare slots in the main panel, and my shop has plenty of room in the subpanel, since I went with the double breakers (Square-D, 2 breakers in the space of one) years ago that save space. Our main panel has a lot of the older single breakers, and space could be freed up by going to the new style double breakers. I cannot imagine ever needing to upgrade.

    I have plenty of power for multiple 20A 110VAC circuits (currently 4), and multiple 20A 240VAC circuits for table saw, radial arm saw, and dust collector. My compressor is in the garage, and powered there, with air distribution into the shop. I also have other circuits in the subpanel for lighting and a finished exercise room adjacent to shop. Now if I had a half a dozen people in my shop, all running tools, the panel would likely get overloaded and trip, but I've never popped a breaker in 25 years in my shop from overloads.

    Given the opportunity to redo it, I'd probably go with 200A main, and 100A subpanel, but what I've got works pretty well for me.

  9. #9
    Join Date
    Oct 2014
    Location
    Wheat Ridge Colorado
    Posts
    170
    Quote Originally Posted by Lee Reep View Post
    When we moved into our house 30 years ago, it only had 100A service panel. Our builder supposedly cut corners on the last phase, since our model was supposed to have 150 or 200A service, and the smaller models had 100A service. I had room in the main panel, and an electrician put a 60A breaker in the panel to feed a subpanel in the basement for my shop. When we added AC to the home a few years later, the electrician said we needed to upgrade. He installed a much bigger panel, but put in a 150A main breaker. Since he had bid the job, and could not raise his price, I think he settled for what he could get away with (150A vs, 200A). We have several spare slots in the main panel, and my shop has plenty of room in the subpanel, since I went with the double breakers (Square-D, 2 breakers in the space of one) years ago that save space. Our main panel has a lot of the older single breakers, and space could be freed up by going to the new style double breakers. I cannot imagine ever needing to upgrade.

    I have plenty of power for multiple 20A 110VAC circuits (currently 4), and multiple 20A 240VAC circuits for table saw, radial arm saw, and dust collector. My compressor is in the garage, and powered there, with air distribution into the shop. I also have other circuits in the subpanel for lighting and a finished exercise room adjacent to shop. Now if I had a half a dozen people in my shop, all running tools, the panel would likely get overloaded and trip, but I've never popped a breaker in 25 years in my shop from overloads.

    Given the opportunity to redo it, I'd probably go with 200A main, and 100A subpanel, but what I've got works pretty well for me.
    Thanks Lee....good to know.

  10. #10
    Join Date
    May 2005
    Location
    Highland MI
    Posts
    4,526
    Blog Entries
    11
    With a shop the size of a one car garage, under 300 sf, you can only get so many tools in there and a 60 amp sub panel should serve you nicely, however for almost the same price I would install a 100 amp panel as they are more common. The electric co may allow you to tap into the meter box and run an underground line to the new shop, new and existing panels off one meter. Depending on service drop size, the electric co may need to upgrade your service. That way all you may have to replace is your meter and not get into pulling and rewiring your house panel. Not that it wouldn't be a good idea at some point to do that. At least around here I see a lot of 2 pole 50 amp services run off the meter box for hot tubs and have done it myself twice, not sure it is ok to do that with a new panel. I presume that your panel and meter are only 20 feet away from your shop? That makes it easy.

    I built my 1500 sf home 40 years ago including doing all the electrical under a homeowner permit and I am really glad my engineer buddy, whose dad was an electrician, talked me into a 200 amp panel. Really seemed like overkill at the time, but it is full now. Guess I was ahead of the curve.
    NOW you tell me...

  11. #11
    Join Date
    Oct 2014
    Location
    Wheat Ridge Colorado
    Posts
    170
    Quote Originally Posted by Ole Anderson View Post
    With a shop the size of a one car garage, under 300 sf, you can only get so many tools in there and a 60 amp sub panel should serve you nicely, however for almost the same price I would install a 100 amp panel as they are more common. The electric co may allow you to tap into the meter box and run an underground line to the new shop, new and existing panels off one meter. Depending on service drop size, the electric co may need to upgrade your service. That way all you may have to replace is your meter and not get into pulling and rewiring your house panel. Not that it wouldn't be a good idea at some point to do that. At least around here I see a lot of 2 pole 50 amp services run off the meter box for hot tubs and have done it myself twice, not sure it is ok to do that with a new panel. I presume that your panel and meter are only 20 feet away from your shop? That makes it easy.

    I built my 1500 sf home 40 years ago including doing all the electrical under a homeowner permit and I am really glad my engineer buddy, whose dad was an electrician, talked me into a 200 amp panel. Really seemed like overkill at the time, but it is full now. Guess I was ahead of the curve.
    At some point, the main service panel at the house DOES need to be upgraded to 200 amp or possibly more. I dont know for sure.
    However, My immediate needs require me to bring power over from the exsisting 100 amp service panel. (I have been up late last night researching this, so forgive me if I am not exactly making sense)

    So, in the absense of replacing the main service panel with a 200 amp service, I have been looking hard at putting a 60 amp breaker in the current (no pun) 100 amp service panel, pulling a line over the 20 or so feet to the garage and dropping it into a sub panel (with seperate 60 amp breaker main switch?).

    From there, it would be one 220vac circut with two outlets. One at the table saw, and one at the Jointer/planer. One 15 amp circut for the shop lighting, and one 20 amp circut for the 6 outlets (20 amp plugs) to be spaced along the shops perimeter.

    Questions,
    Is this correct sounding? I am not looking for the "official" thumbs up, just spitballing here. I am looking for someone to either say "yes, you SEEM to be on the right track and would most likely NOT burn your shop/house down if you do it this way" or, " you are a moron forthinking of doing it this way, and any electrition who agrees to do it this way is a moron too".

    Assuming I am NOT a moron, can anyone look at this electrical "map" and give me wire sizes for each portion?

    Thanks,

  12. #12
    Join Date
    May 2005
    Location
    Highland MI
    Posts
    4,526
    Blog Entries
    11
    My concern would be putting a 60 amp 2 pole breaker in what is probably an already fully loaded 100 amp panel. That is why I suggested going from the meter box instead of the panel. Meter box to fused disconnect (may or may not be required) to new panel. Be sure to get a permit so all is done per code and inspected. Only dicey part is working in a hot meter box. Even after you pull the meter, the incoming lugs are still hot.
    NOW you tell me...

  13. #13
    Join Date
    Oct 2014
    Location
    Wheat Ridge Colorado
    Posts
    170
    Quote Originally Posted by Ole Anderson View Post
    My concern would be putting a 60 amp 2 pole breaker in what is probably an already fully loaded 100 amp panel. That is why I suggested going from the meter box instead of the panel. Meter box to fused disconnect (may or may not be required) to new panel. Be sure to get a permit so all is done per code and inspected. Only dicey part is working in a hot meter box. Even after you pull the meter, the incoming lugs are still hot.
    Well, that is a slight concern. Ill need to recheck the service panel, but I seem to recall that the Panel still has several open slots available. That may be a bit like saying "How can I be over drawn? I still have checks left in my checkbook", so some verifying of what is being drawn from the panel is, indeed in order.

  14. #14
    Join Date
    Jun 2008
    Location
    So Cal
    Posts
    3,783
    John, in my shop a have a 100 amp sub panel, a #4 wire runs from my main panel to my sub panel.The wire is protected with a 70 amp breaker at the main.
    The biggest pig machine is a toss up between the bandsaw and jointer.both have 220 30 amp breakers.So I think your on the right track.
    seems like everyone is trying to get you to go as big as you can,Cause it's a pain to do it later if you need to.Hope this helps.Aj
    Last edited by Chris Padilla; 01-11-2015 at 1:25 AM.

  15. #15
    Join Date
    Oct 2014
    Location
    Wheat Ridge Colorado
    Posts
    170
    Quote Originally Posted by Andrew Hughes View Post
    John, in my shop a have a 100 amp sub panel, a #4 wire runs from my main panel to my sub panel.The wire is protected with a 70 amp breaker at the main.
    The biggest pig machine is a toss up between the bandsaw and jointer.both have 220 30 amp breakers.So I think your on the right track.
    seems like everyone is trying to get you to go as big as you can,Cause it's a pain to do it later if you need to.Hope this helps.Aj
    thanks AJ. Yes, I agree that it would be best to go big or go home. But this is just going to be a stopgap shop until the "real shop" gets built. Or, I find shop space at a reasonable price. Either way, there will be plenty of time to go big once one of those two things happen.

    In the mean time, I just need to get appropriate power to the space I do have as best I can with what I have to work with. Thank god, I have at least enough room in the service panel, to bring some power over to the garage.
    Last edited by Chris Padilla; 01-11-2015 at 1:25 AM.