    The house is 10 years old; I have lived here 4 years. Any electrical I have looked at has been competent.

    Today the breaker to the utility room outlets (washer, gas dryer) opened. I reset it and everything was fine. Its been fine for 4 years at least.
    I have never had a breaker just open for no reason.
    What might the reason be?

    Getting behind the machines to look at the outlet wiring will be a chore.
    Thanks.

  2. #2
    Join Date
    Jun 2006
    Location
    The Hartland of Michigan
    Posts
    7,628
    Could be a weak breaker. Go to HF and get a clamp-on amp meter.
    Never, under any circumstances, consume a laxative and sleeping pill, on the same night

  3. #3
    Join Date
    Mar 2012
    Location
    Virginia and Kentucky
    Posts
    3,364
    There might have been something that made the circuit breaker "open." Is this also a newer circuit breaker that also has the neutral (white) wire attached to the circuit breaker? They are arc fault circuit breakers and more conditions cause them to trip than typical circuit breakers.

  4. #4
    Join Date
    Apr 2016
    Location
    Tasmania
    Posts
    2,162
    Could be an intermittent minor overload or anything. It just proves your breaker is working. If it does it again I would call an electrician but not yet. Even a supply surge can do it. Cheers

  5. #5
    Join Date
    Oct 2006
    Location
    New Jersey
    Posts
    1,295
    Were you using the machines?? Did they both come on at the same time?? Could have been a quick surge. As others have said just watch it for now before you make any sudden moves.
    John T.

  6. #6
    It's possible the breaker was like 99% tripped but didn't make it past the 'hump' My big compressor 30amp breaker did that once, kinda. I turn all my work breakers off every night, and when I got to that breaker, the moment my finger barelly grazed the switch, it flipped into the 'tripped' position. It probably would've flipped eventually by itself. Next day the breaker tripped normally half way into the day. Turned out the motor was in need of new bearings...
    ========================================
    ELEVEN - rotary cutter tool machines
    FOUR - CO2 lasers
    THREE- make that FOUR now - fiber lasers
    ONE - vinyl cutter
    CASmate, Corel, Gravostyle


  7. #7
    Join Date
    Sep 2012
    Location
    Greater Manor Metroplex, TX
    Posts
    264
    Was it especially warm in the area you have the breaker?

    If you have one of the infrared thermometers, you can check the relative temp of that breaker verse the other in the panel. If it is running "hotter" than the others, it may be an indication or a problem.

    Aside from some of the reasons already mentioned, if the breaker is not well seated in the panel, you can get these types of trips. Unless it happens again, I would not worry any it. If it does, call an electrician.

  8. #8
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    Nothing is new or changed. The machines are 10 years old, but the previous owner used it as a summer cottage and our children are gone; so they have seen little use.
    My wife says they were both running when she left. When she came back they both seemed done, but when she put the wash into the dryer, it wouldn't start.

    Next time she uses it I will test the voltage and temperature. I appreciate your help.

  9. #9
    Join Date
    Jul 2013
    Location
    Bakerton WV
    Posts
    259
    Is it not normal to use a dedicated circuit for each major appliance, even if the dryer is gas fired?

  10. #10
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    The breaker is well seated. All the breakers a degree above room temperature; nothing odd about the laundry room one.

    The washer draws:
    5.4 to start agitation
    2.6 to agitate
    12 to start spin
    3.4 to spin

    The dryer drew 19.4 to start, and 5.2 to run.
    Just for fun I started the dryer while running an 1800w heat gun on the circuit. No problem.

    The clothes in the dryer were dry when the breaker went, so it wasn't starting.

    I have some spare breakers; I might as well swap it out while the cover is off. Can't hurt.
    Last edited by Wade Lippman; 10-26-2016 at 4:03 PM.

  11. #11
    Could even have been a voltage sag (brown-out) by your electric utility provider. If voltage drops while in use, the amps rise. CB trips.

  12. #12
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    When I pulled the breaker out, the wire just fell out. I have never had that happen before!
    Could that have caused the problem?

    I tried all my breakers and a quarter of wires were loose, as were a quarter of the neutral/ground connections.

  13. #13
    Join Date
    Feb 2003
    Location
    Doylestown, PA
    Posts
    7,577
    Quote Originally Posted by Wade Lippman View Post
    When I pulled the breaker out, the wire just fell out. I have never had that happen before!
    Could that have caused the problem?

    I tried all my breakers and a quarter of wires were loose, as were a quarter of the neutral/ground connections.

    Good thing you checked. Loose connection=higher resistance=more heat? I had similar with a GFCI outlet. Making a change, pulled the device out and the wire pulled out.

  14. #14
    Join Date
    Sep 2007
    Location
    Longview WA
    Posts
    27,520
    Blog Entries
    1
    Quote Originally Posted by Wade Lippman View Post
    When I pulled the breaker out, the wire just fell out. I have never had that happen before!
    Could that have caused the problem?

    I tried all my breakers and a quarter of wires were loose, as were a quarter of the neutral/ground connections.
    Finding something like this would have me wondering if the rest of the connections in the house were loose.

    Is your wiring copper as opposed to aluminum?

    I would want to know why the wires were loose at the breakers.

    jtk
    "A pessimist sees the difficulty in every opportunity; an optimist sees the opportunity in every difficulty."
    - Sir Winston Churchill (1874-1965)

  15. #15
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    Quote Originally Posted by Jim Koepke View Post
    Finding something like this would have me wondering if the rest of the connections in the house were loose.

    Is your wiring copper as opposed to aluminum?

    I would want to know why the wires were loose at the breakers.

    jtk
    It is all copper. The utilities wires are aluminum, but they were tight and well coated.
    The few outlets or switches I have had occasion to look at were connected properly.