    Drilled Wells

    Anyone here know anything about pitless adapters for drilled wells?

    Or even a forum where I an ask questions about them?

    TIA
    Jerry
    Confidence: The feeling you experience before you fully understand the situation

  2. #2
    I just did a quick google search of "pitless adapters for drilled wells" and tons of info came up. Try it if you haven't yet. It may answer your questions. Hope it helps.

    Red
    RED

  3. #3
    Join Date
    Jul 2007
    Location
    NE OH
    Posts
    2,629
    Not sure about etiquette of mentioning other forums here, but there is one that rhymes with doityourself.com.

  4. #4
    Join Date
    Feb 2003
    Location
    McKean, PA
    Posts
    15,662
    Blog Entries
    1
    I have two wells both with pitiless adapters. What is your question.

  5. #5
    Join Date
    May 2008
    Location
    Peshtigo,WI
    Posts
    1,414
    Every winter I pull the pump up off the pitless adapter to drain the water from the well to the cabin.

    Curious if there might be a valve setup where I could open a valve to drain the water instead of lifting the pump.

    In the past I've had the o-ring slip out of it's groove, then it turns into a much bigger job that's a PITA.
    Confidence: The feeling you experience before you fully understand the situation

  6. #6
    Join Date
    Feb 2003
    Location
    McKean, PA
    Posts
    15,662
    Blog Entries
    1
    Quote Originally Posted by Jerry Bruette View Post
    In the past I've had the o-ring slip out of it's groove, then it turns into a much bigger job that's a PITA.
    I've only pulled my pump twice for repairs. I've never had a problem with the o-ring coming out. Do you relieve the pressure in the line before lifting the pump? If not this could be your problem. It is easier to pull once the pressure is gone from the water line. Since the o-ring is in the part you lift, having a spare o-ring on hand should make the job easier. Be sure to lube the o-ring before you try to slide the adapter back in.
    Lee Schierer
    USNA '71
    Go Navy!

    My advice, comments and suggestions are free, but it costs money to run the site. If you found something of value here please give a little something back by becoming a contributor! Please Contribute

  7. #7
    Join Date
    May 2008
    Location
    Peshtigo,WI
    Posts
    1,414
    Yup pressure is bled off, o-ring is lubed. The pitless adapter is welded onto the outside of the well casing, making it harder to put the adapter back together.

    I'd just like to leave the adapter hang there doing it's job and be able to open a valve to drain the water back.
    Confidence: The feeling you experience before you fully understand the situation

  8. #8
    Join Date
    Feb 2003
    Location
    McKean, PA
    Posts
    15,662
    Blog Entries
    1
    You could pull your pump one more time, cut the line to the pump below the adapter, add a Tee with a side outlet and a 1/4 turn ball valve for a drain. You would have to reach down the well (maybe with an extension handle) to move the valve when you want to drain or restore pressure.
    Lee Schierer
    USNA '71
    Go Navy!

    My advice, comments and suggestions are free, but it costs money to run the site. If you found something of value here please give a little something back by becoming a contributor! Please Contribute

  9. #9
    Join Date
    May 2008
    Location
    Peshtigo,WI
    Posts
    1,414
    Quote Originally Posted by Lee Schierer View Post
    You could pull your pump one more time, cut the line to the pump below the adapter, add a Tee with a side outlet and a 1/4 turn ball valve for a drain. You would have to reach down the well (maybe with an extension handle) to move the valve when you want to drain or restore pressure.
    Hadn't thought of that. Could be the solution I'm looking for.

    Thanks Lee
    Confidence: The feeling you experience before you fully understand the situation

  10. #10
    Join Date
    Jul 2007
    Location
    NE OH
    Posts
    2,629
    If you go that route, I'd bridge the Tee with a stainless steel strap tightly clamped below and above the tee to avoid any chance of the tee coming undone and dropping the pump....

  11. #11
    Join Date
    Jul 2009
    Location
    Indiana
    Posts
    46
    I have a cabin that I drain in the winter. What I did was pull the submersible pump and removed the internal check on the bottom. I then added an inline check at the pressure tank which holds the water like you would hold water in a straw with your finger. To drain everything from the check down I drilled and tapped an 1/8" NPT port on the pump side of the check and installed a small ball valve. Opening the valve breaks the vacuum and the water falls back into the well.

    All the water on the house side of the check drains through the valve on the pressure tank.

    I have had this setup for about a dozen years and it works great.

  12. #12
    Join Date
    May 2008
    Location
    Peshtigo,WI
    Posts
    1,414
    Sounds like a nice setup Tim, unfortunately I don't have the room for extra valves by my tank.
    Confidence: The feeling you experience before you fully understand the situation

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •