    I have a Generac 4000EXL generator that has a 120/240 volt AC, 20 amp locking receptacle. The receptacle accepts a NEMA L14-20 plug (included with the generator). Instructions state to use a 4-wire cord set rated for 250 volts at 20 amps and that you can use the same 4-wire cord if you plan to run a 120 volt load. I need this 20 amp souce to run my 120 volt compressor and I'm lost as to how to wire this. It seems counter intuitive to me that one receptacle can run both 120 and 240 volt loads using the same cord. All help is appreciated.

    The operator manual can be viewed from the following link.

    http://www.generac-portables.com/ser...ch_results.cfm

  2. #2
    Join Date
    Mar 2006
    Location
    Kingston, Ontario
    Posts
    390
    Terry:

    The site comes up with an error when attempting to access.

    Greg

  3. #3
    Join Date
    Jan 2004
    Location
    Lewiston, Idaho
    Posts
    28,557
    Terry,

    I went to the Genrac site and looked at the plug and their statement. I'd give Genrac's customer service line a call later today.

    I could see 2 ways you could wire that plug to get 120 but you would only need 3 wires of the 4. Maybe it's senses the load?

    Contact Genrac to verify their statement and meaning.

    Good luck!
    Ken

    So much to learn, so little time.....

  4. #4
    Join Date
    Mar 2008
    Location
    Springfield, Ohio
    Posts
    42
    You might have to go to this link and click on Service/Support tab, then select Operators Manuals and enter 1645-0 for the model number. The site apparently doesn't allow you to go directly to that page. Sorry!

    http://www.generac-portables.com/

  5. #5
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,281
    Hi Terry, the generator supplies 120-0-120 just like your home service.

    If you want 240 volts you use both lines, and ground.

    If you want 120 volts, either line and neutral, plus ground are what you want.

    You could make a cord up with the cap on one end, and a 4 inch square box on the other end. That way you could have a 240 volt receptacle, and a split 120 volt receptacle that would provide two 120 volt circuits.

    Note that you have to monitor the load to make sure that you don't overload either line.

    Regards, Rod.

    P.S. Don't forget to ground the generator when you are using it, instructions should be in your manual.

  6. #6
    Join Date
    Mar 2008
    Location
    Springfield, Ohio
    Posts
    42
    Thank you gentlemen. I have a better idea now on how to make this happen.

  7. #7
    Gene O. Carpenter Guest

    Generator Wiring

    Terry,
    Check this site out for anything you might need to know about your generator. If the link violates TOS then just add the www. to "smokestak.com" ..These guy's can tell you the where's, whens and hows about just about any power plant made from the earliest up to today's unit's.. They're a great bunch of guy's and even a few gal's in there also! If you plan on using the genny for home backup power you would be better informed if you ask them about "back feeding"..
    Gene
    PS: If you like old gas or steam engines, old farm machinery, just any rusty old iron this site will be beneficial for you..

    www.smokstak.com

  8. #8
    Join Date
    Nov 2003
    Location
    Central North Carolina
    Posts
    1,830
    Be careful about trying to do this. An air compressor draws an exceptionally large amount of current when it is starting up. Even though the generator may have enough current capability to run your compressor by the nameplate ratings it may not have enough reserve capacity to start and run your compressor properly. My son and I just ran into this when trying to run his 2 hp 240 volt compressor from our 2 KW 120/240 generator (both are almost new and in perfect condition). The nameplate ratings implied that it could do it, but when we actually tried we found that the compressor never came up to full speed, and it's motor got really hot in only about 30 seconds. I think a generator with about 2X the rated capacity of the compressor's full load rating will be necessary for it to work properly. The only way that the compressor would run from our generator was if there was no pressure in the air tank when it was started. Once it had shut off via the pressure switch and then tried to re-start by itself there was still pressure in the tank and the motor couldn't attain full speed.

    I wasn't able to view your generator's website so I'm just telling you about the problem that we had. Make sure that your generator has enough reserve capacity to handle the long start-up current load of your compressor and watch it carefully in the beginning or you may burn up your compressor motor.

    Charley

  9. #9
    Join Date
    Jun 2007
    Location
    Wichita, Kansas
    Posts
    1,795
    Charles Lent's caution about the starting surge is on point. Your generator has a 6600 watt surge rating (4000 watt continuous) but you didn't mention anything about the compressor load requirements. If your compressor motor's data plate has an LRA (Locked Rotor Amperage) value, that's an order-of-magnitude indication of the instantaneous current the motor will draw on startup.

    Page 14 of your operator's manual shows 5000 watts as an example requirement for starting a 1 1/2 HP compressor. That approximates 30 amps per HP (at 120v) for the start surge, but YMMV.

    Going strictly be the surge wattage of your generator, it should be able to handle a 120v start surge that doesn't significantly exceed 50-55 amps - assuming there's no other load on the generator at the time. Extrapolating from the example in your manual, you should be OK if your compressor is less than about 2HP. More than that, and you're likely to run into problems.
    Tom Veatch
    Wichita, KS
    USA

  10. #10
    Join Date
    Jul 2007
    Location
    Forest Grove, OR
    Posts
    1,167
    I also wouldn't run a single, big 120V load on a generator for long periods of time- You are only using half of the windings in the generator that way, and it will result in thermal stresses that aren't balanced. It would be best to rewire your compressor for 240 V if you can or convert it to gasoline power if it is belt driven.

  11. #11
    Join Date
    Mar 2008
    Location
    Springfield, Ohio
    Posts
    42
    I'm really glad I asked this question, because I had no idea there was so much to learn. The compressor has a 1.5 HP motor and it can be wired for 240 volts, so I'll give serious consideration to making that modification. I really do appreciate the information - and thanks again!

  12. #12
    Join Date
    Jun 2007
    Location
    Wichita, Kansas
    Posts
    1,795
    Quote Originally Posted by Terry Browne View Post
    ...it can be wired for 240 volts, so I'll give serious consideration to making that modification. ...
    If you intend to run your compressor from the generator exclusively, or if you have a 240v outlet convenient to where you normally run the compressor, OR if you're going to use a long extension cord get power to the compressor then I'd switch the leads around to run it on 240. Higher voltage equates to lower amperage and less voltage drop/power loss/heating at a given wattage.

    From page 15 of your owner/operator manual:
    Rated Maximum Continuous Load Current
    At 120 Volts . . . . . . . . . . . . . . . . . . . . . . . 33.3 Amps

    At 240 Volts . . . . . . . . . . . . . . . . . . . . . . . 16.7 Amps
    That implies to me, perhaps incorrectly, that the generator head feeds a center tapped transformer that provides the 120/240 line voltage. If that is the case, the generator head itself won't know whether the load is drawing 120 or 240 volts, it's simply feeding the transformer.

    In either case, running the compressor alone, you're going to be well below the maximum continuous rating of the generator unit. For operation off the generator, if you don't have a convenient 240v outlet and there's no long extension cord involved, then I don't think I would bother converting the motor.
    Tom Veatch
    Wichita, KS
    USA

Similar Threads

  1. Lurker peering thru the door with a rail and stile question? (Long)
    By Chris Wilson in forum General Woodworking and Power Tools
    Replies: 10
    Last Post: 03-13-2007, 5:20 PM
  2. Newbie question about my band saw
    By Tim Solley in forum General Woodworking and Power Tools
    Replies: 4
    Last Post: 04-20-2006, 2:45 PM
  3. Shop moving question?
    By Alan Tolchinsky in forum General Woodworking and Power Tools
    Replies: 20
    Last Post: 02-13-2006, 9:31 AM
  4. HI - New to this forum - got a question 'bout lathes
    By Matthew Dworman in forum General Woodworking and Power Tools
    Replies: 14
    Last Post: 06-01-2004, 10:38 PM
  5. A Different Question re: Old vs. New Planes
    By Lewis Lamb in forum Neanderthal Haven
    Replies: 3
    Last Post: 01-28-2004, 6:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •