My mini split has 15’ lineset; is it best to install total 15’ or can I cut the Lineset shorter?
i can locate outdoor unit to use 8’ to 15’ of line set
My mini split has 15’ lineset; is it best to install total 15’ or can I cut the Lineset shorter?
i can locate outdoor unit to use 8’ to 15’ of line set
Best to cut the line set.
The manufacturer may specify a minimum lineset for whatever reason. Check their documentation or contact them and ask. In mine if you go under 8 feet IIRC you needed to remove one ounce of refrigerant.
Bob is correct...you need to check with the manufacturer. Some units seem to have a 10' minimum. The Daikin being installed in my shop next week can go as low as something like one meter which is about all that will be needed for my install due to the exterior elevations at that corner of my shop and the wall being partially below grade.
--