Thread: A scary discovery, what's going on?

  1. #1
    Join Date
    Sep 2013
    Location
    Wayland, MA
    Posts
    3,668

    A scary discovery, what's going on?

    I went out to my shop to turn the lights off just now; the programmable switch had lost its memory due to a prolonged power outage. To my surprise the switch box was blazing hot. The picture below is what I found inside. Needless to say this scared the wits out of me. I've powered off the circuit to think about what to do. I use the switch every day and have never noticed it being hot before.

    In theory the circuit should not be overloaded. I have 12 two-bulb T5HO fluorescent fixtures for light in the shop. at 54 watts/bulb that should consume 12 X 2 X 54= 1296 watts. The 15A circuit should be able to support safely 80% of 15A or 0.8 X 1800 watts = 1440 watts continuous load. The overhead lights are the only load on that circuit.

    In practice the wire nuts are melting!

    Any insight as to what's happening here? Obviously I could split the lights onto two breakers, but that would be a pain and they really should be safe as-is.

    IMG_6827.jpeg

  2. #2
    Looks like a bad wire connection overheating- very apropos of the arc fault discussion.

  3. #3
    Join Date
    Feb 2003
    Location
    McKean, PA
    Posts
    15,653
    Blog Entries
    1
    I would be interested whether the wires are twisted together or just bunched together and held by the wire nut.
    Lee Schierer
    USNA '71
    Go Navy!

    My advice, comments and suggestions are free, but it costs money to run the site. If you found something of value here please give a little something back by becoming a contributor! Please Contribute

  4. #4
    Join Date
    Feb 2014
    Location
    Lake Gaston, Henrico, NC
    Posts
    9,089
    I was getting ready to ask the same question that Lee asked.

  5. #5
    Join Date
    Sep 2010
    Location
    New England
    Posts
    2,477
    Quote Originally Posted by Lee Schierer View Post
    I would be interested whether the wires are twisted together or just bunched together and held by the wire nut.
    Exactly what I was wondering. Are the wires loose and arcing?

  6. #6
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,008
    I think Wagos are harder to mess up then wire nuts but they take up more room. When you redo those connections you will have to clean and expose the wire to bright copper. Soot is an insulator. I assume no aluminum was involved?
    Bill D

  7. #7
    Join Date
    Sep 2013
    Location
    Wayland, MA
    Posts
    3,668
    I will take a picture and post it when I take it apart later this morning. No aluminum. This was wired about a decade ago. They are almost certainly twisted, as that's how I was taught to do it.

    Is twisting a good thing or a bad thing? The interweb seems to be divided pretty close to 50-50 on the subject. Some manufacturers say it's not necessary, but don't say not to do it.

  8. #8
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,901
    Pre-twisting provides a very positive connection, IMHO. I've also now moved to Wago connectors, but if I do a wire nut, I always pre-twist with lineman's pliers, clean/trim the end and then apply the wire nut followed by tape.

    It will be interesting to see what you find when you peel that apart to see why it's arcing.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  9. #9
    Quote Originally Posted by Jim Becker View Post
    Pre-twisting provides a very positive connection, IMHO. I've also now moved to Wago connectors, but if I do a wire nut, I always pre-twist with lineman's pliers, clean/trim the end and then apply the wire nut followed by tape.

    It will be interesting to see what you find when you peel that apart to see why it's arcing.
    I haven't used the Wago but that's the way I've been doing wire nuts for decades.

  10. #10
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,901
    Quote Originally Posted by Edward Weber View Post
    I haven't used the Wago but that's the way I've been doing wire nuts for decades.
    I "discovered" them when I was wiring the new shop, Edward. They were a game changer, especially with the heavy #10 wire on the machine circuits. They also need to be taped, IMHO, but there's a lot less screwing around with tools...cut, strip, insert and lock, tape. Done.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  11. #11
    Join Date
    Sep 2013
    Location
    Wayland, MA
    Posts
    3,668
    It's going to be embarrassing in all likelihood, but here are my best guesses. I believe strongly in the importance of "near miss" reports for improving safety. I've sure had an important lesson.

    The stranded wire from the timer switch is the principal point of failure. I see several things when inspecting the wire and the connection.
    1) The stranded wire is melted along its length
    2) it appears to be wrapped around the solid wire several times and in good contact with both the solid wire and the spring inside the wire nut.
    3) It appears corroded inside the wire nut
    4) it looks as though several strands (3-5) of the stranded wire were broken off short and possibly not in contact with the solid wire (poor wire stripping technique?)
    5) the other two connections appear similar, but are uncorroded and not melted

    Possible issues:

    1) missing strands will clearly lower the ampacity of the wire, resulting in greater heat; why this only became apparent after a decade is unknown.
    2) the wire nut was one of the lightweight ones that come for "free" with the switch, the others were of much higher quality. A possible source of corrosion? (Circuit was (unusually) out of use for 10 days with very high humidity, a contributing factor?)
    3) stranded wire was not tinned

    Suggested solutions:

    1) Greater care in handling stranded wire
    2) tin the ends of the stranded wire
    3) Employ a clamp-type connector to join stranded to solid wire
    4) Check all other similar installations in the house and shop, correcting as needed

    My tentative conclusion is operator error on installation, and possibly a low quality wire nut.


    IMG_6828.jpeg IMG_6829.jpeg IMG_6830.jpeg IMG_6831.jpeg

  12. #12
    I'm no electrician but I don't think you want tinned wire in a compression connection. I've personally seen two equipment failures (one very expensive) due to a tinned, stranded wire being installed in a screw terminal (i.e., compressed under a screw head). The solder will creep over time and cause the joint to fail. I don't know if this applies to a wire nut also, but since it's a compression fitting as well I would err on the side of not tinning stranded wire.

    No idea why your wire melted though!

  13. #13
    Join Date
    Sep 2013
    Location
    Wayland, MA
    Posts
    3,668
    Oh, something else to learn about. My friend, who is an electrical engineer and an old-time TV/radio repair guy, has been telling me to always tin the ends of stranded wire.


    Quote Originally Posted by Bert McMahan View Post
    I'm no electrician but I don't think you want tinned wire in a compression connection. I've personally seen two equipment failures (one very expensive) due to a tinned, stranded wire being installed in a screw terminal (i.e., compressed under a screw head). The solder will creep over time and cause the joint to fail. I don't know if this applies to a wire nut also, but since it's a compression fitting as well I would err on the side of not tinning stranded wire.

    No idea why your wire melted though!

  14. #14
    Do you mean for wire nuts or for other uses? You definitely don't want to tin wires for crimp connections, and AFAIK you don't want to tin wires in screw terminals (as I mentioned, I've seen them come loose myself). You can probably do it for very small/fine wires to keep them together, but not for the really thick stuff.

    Plus, if the connection heats up and the solder softens then your connection will get even worse.

    You absolutely should tin wires before soldering them, but I don't think you want solder in any "physical" connections (like a crimp, ferrule, or screw terminal). I do think there are some ferrules designed to be crimped on THEN filled with solder, but not the other way around.

  15. #15
    Join Date
    Apr 2005
    Location
    Central MA
    Posts
    1,591
    Quote Originally Posted by roger wiegand View Post
    In theory the circuit should not be overloaded. I have 12 two-bulb T5HO fluorescent fixtures for light in the shop. at 54 watts/bulb that should consume 12 X 2 X 54= 1296 watts. The 15A circuit should be able to support safely 80% of 15A or 0.8 X 1800 watts = 1440 watts continuous load. The overhead lights are the only load on that circuit.
    I suspect your circuit current is a fair bit higher than you think. You haven't accounted for the power consumed by the ballasts, nor have you accounted for the power factor of it. (Watts are never equal to volts x amps in the real world, you must know the power factor to calculate watts) I'd bet an internet buck or two that your circuit current is +/-14 amps.