    With no insulation in the walls or for the rafters, my shop is absolutely blazing in the summer time (I live in upstate NY). I'm specfically wondering what I might do for insulating the rafter areas. There is no "ceiling" - you can see the inside of the roof area from the shop.

    I'd like to keep it open if possible, and I realize that will likely affect how well it can be insulated. To make an actual ceiling would have it be pretty low, not great for moving taller stuff around. Plus my ducting is already at/above the double top plate, complicating that approach. The cavities are not that deep, maybe 7" or so; this is a late-19th century structure.

    I've considered insulating the open cavities (the 45* degree areas) with rockwool, and then covering the cavity. Drywall is pretty heavy, not sure this ancient roof structure could handle all that weight. But rockwool is messy stuff, and I don't want it falling all over the place.

    Also considered spray foam or foam board. So far, foam board with an air gap seems most palatable, but that might require specific covering due to the fire code, and then I'd be back to the potential roof weight issue.

    I've included a couple of images of the roof and cavity area.


    All feedback welcomed --

    Thx,

    Ned
    Attached Images Attached Images

  2. #2
    Join Date
    May 2018
    Location
    Lancaster, Ohio
    Posts
    1,378
    Have a spray foam contractor out to look it over, discuss it and get a quote.
    Ron

  3. #3
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,977
    Closed cell spray foam will not only insulate, it will also make the structure more rigid as well as sealed and provides a moisture barrier. It can be installed directly on the underside of the roof so you lose no space. It will also brighten up the interior over that old dark wood, even after it "mellows" a bit in color as foam does. If your shop is an outbuilding, it's unlikely leaving it exposed would be an issue. Even in a residence, either using an additive or coating with a special paint will often satisfy code if there is a requirement. It's not inexpensive, but it does a great job with multiple benefits as I mentioned. You will likely get a better price from a small operator...that was the case here with my new shop building. Like about 40% less in my case from the larger companies.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  4. #4
    My approach is to fit rigid foam sheet panels between the rafters, leaving an air gap above.Fiberglass can fill the remaining space, covered in your case even by Tyvek.
    Vents are added at the eaves and ridge which exhausts heat and moisture. The shiny foil face helps as a radiant barrier.

    I would leave 1/2 or 5/8" space (furring strips), cut the probably 1 1/2" foam into 4' butts with drywall square and snap-off type knife with a long blade, for a press fit into the bays.

    I've done this quite a few times. It is DIYable, relatively inexpensive, reversable/modifiable, and does not promote moisture or heat degradation, and is not ugly.

  5. #5
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,995
    Blog Entries
    2
    Quote Originally Posted by Cameron Wood View Post
    My approach is to fit rigid foam sheet panels between the rafters, leaving an air gap above.Fiberglass can fill the remaining space, covered in your case even by Tyvek.
    Vents are added at the eaves and ridge which exhausts heat and moisture. The shiny foil face helps as a radiant barrier.

    I would leave 1/2 or 5/8" space (furring strips), cut the probably 1 1/2" foam into 4' butts with drywall square and snap-off type knife with a long blade, for a press fit into the bays.

    I've done this quite a few times. It is DIYable, relatively inexpensive, reversable/modifiable, and does not promote moisture or heat degradation, and is not ugly.
    My shop attic is done this way as well. The shingle manufacturer said they require 3 inches of free air under the sheeting (for full warrantee). I cheated a little and have a 2 inch air gap, then 2 inches of Owens Corning Foamular, + 3.5 inches of fiberglass, + sheetrock. I sealed my rigid foam in place with Great Stuff pro foam. My air gap has gotten as hot as 145 degrees which is very close to the limit for both foam board and shingles. The attic room is easy to heat and cool. It has no walls. The slanted roof goes right down to the floor. The ceiling of the shop below and its 2 x 6 walls have dry pack cellulose. Downstairs is also easy to heat and cool.
    Best Regards, Maurice

  6. #6
    Quote Originally Posted by Maurice Mcmurry View Post
    My shop attic is done this way as well. The shingle manufacturer said they require 3 inches of free air under the sheeting (for full warrantee). I cheated a little and have a 2 inch air gap, then 2 inches of Owens Corning Foamular, + 3.5 inches of fiberglass, + sheetrock. I sealed my rigid foam in place with Great Stuff pro foam. My air gap has gotten as hot as 145 degrees which is very close to the limit for both foam board and shingles. The attic room is easy to heat and cool. It has no walls. The slanted roof goes right down to the floor. The ceiling of the shop below and its 2 x 6 walls have dry pack cellulose. Downstairs is also easy to heat and cool.
    I did an attic conversion like that- 2x4 rafters with additional 2x2 strapping. It became the master bedroom and was (is) amazingly comfortable.

    Do you have the venting above and below?

  7. #7
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,995
    Blog Entries
    2
    I do. The aluminum soffit is all perforated and I have 3 big chicken house spinning vents along the ridge. The solar panels shading the south side make a big improvement regarding heat gain during the summer. We feel very fortunate to have been able to build the shop!

    Screen Shot 2023-12-23 at 7.53.27 PM.png
    Last edited by Maurice Mcmurry; 12-23-2023 at 8:57 PM.
    Best Regards, Maurice

  8. #8
    Join Date
    Nov 2012
    Location
    North Dana, Masachusetts
    Posts
    501
    Spray foam is a terrible thing to do to a building. It has drawbacks, and is non-reversable. Any trades person I know that has had to work in a spray foam building has had to just saw and chisel the stuff out in order to do any work. For example, an old house had a leak in the flashing around a window. No one knew. The water got in around the spry foam, and started a mold farm. The walls came out, the laborers cam in and hacked out the spray foam.

    If the mix isn't right on the spray foam truck, the foam doesn't set up right, and just off gasses. Google "Spray Foam Fail Canada" to read about the failures, illness, and government response to help homeowners out.

    A better route would be to frame a ceiling, sheet rock it, air seal it, and use cellulose insulation. The useless space up high won't need heating.

  9. #9
    Join Date
    Sep 2016
    Location
    Modesto, CA, USA
    Posts
    10,059
    The polyiso foam board doubled in price during covid and never came down. It is $55 for 2". 4x8 sheet. Cuts well on the table saw. My plan is to do the 16" of foam in the rafters at the little triangle near the eaves of the house then switch to fiberglass for most of the attic floor. Go with r30 or r38 on top of existing r-13. Foil under the roof will be perforated for air flow.
    BilL D

  10. #10
    Quote Originally Posted by Bill Dufour View Post
    The polyiso foam board doubled in price during covid and never came down. It is $55 for 2". 4x8 sheet. Cuts well on the table saw. My plan is to do the 16" of foam in the rafters at the little triangle near the eaves of the house then switch to fiberglass for most of the attic floor. Go with r30 or r38 on top of existing r-13. Foil under the roof will be perforated for air flow.
    BilL D

    Ugh, don't saw that stuff. EPS is almost as good R value wise, cheaper, and much more friendly to work with.

  11. #11
    Join Date
    Sep 2013
    Location
    Wayland, MA
    Posts
    3,679
    Spray foam is way easier albeit more expensive than building some kind of structure and/or fitting rigid foam and will provide much better air sealing. Just depends on how you want to spend your time/money. As with anything there are horror stories with any system you might choose (often trumpeted by the folks selling competing products), but bad experiences are rare with each of these approaches. Check with your local code officials if they would be happy with an intumescent coating in this case vs a rigid fire barrier. If you're willing to run joists across the space then blown in cellulose is a very cost efficient choice for an attic.

    Check out the availability of used polyiso (Craigslist is a place to find it). Insulation is commonly replaced when commercial buildings are re-roofed and the panels get recycled in the secondary market, usually cut up into 4 x 4 pieces. Condition can vary a lot, so look for the better quality stuff. I put 12" of polyiso on top of my son's very low pitched roof for pennies on the dollar of what new foam would have cost, and then a new rubber roof over that to solve a difficult insulation situation. The R value of the old foam is slightly lower than new, but the cost of a couple extra inches is very low.

  12. #12
    With respect to polyiso I'm finding some online chatter that in addition to the R value degrading over time it also decreases along with the temperature, not a desirable trait for those of us who live where the winter low temperatures often reach single digits. Which type of rigid panel would be recommended?

    Examples of polyiso literature https://buildingscience.com/document...endent-r-value and https://www.ecohome.net/guides/2254/...not-to-use-it/

  13. #13
    Join Date
    Nov 2021
    Location
    Mid West and North East USA
    Posts
    2,995
    Blog Entries
    2
    It has been a while since I looked at the data on various insulation. For DIY materials, Foamular had the most extensive testing, best data, and best specs 13 years ago. They also claim their products to be a bit more environmentally friendly.

    FOAMULARŪ 250 XPS Foam Board Insulation | Owens Corning Insulation

    Screen Shot 2023-12-24 at 8.56.54 AM.png
    Last edited by Maurice Mcmurry; 12-24-2023 at 10:13 AM.
    Best Regards, Maurice

  14. #14
    Join Date
    Dec 2019
    Location
    The old pueblo in el norte.
    Posts
    1,906
    Quote Originally Posted by Cameron Wood View Post
    My approach is to fit rigid foam sheet panels between the rafters, leaving an air gap above.Fiberglass can fill the remaining space, covered in your case even by Tyvek.
    Vents are added at the eaves and ridge which exhausts heat and moisture. The shiny foil face helps as a radiant barrier.

    I would leave 1/2 or 5/8" space (furring strips), cut the probably 1 1/2" foam into 4' butts with drywall square and snap-off type knife with a long blade, for a press fit into the bays.

    I've done this quite a few times. It is DIYable, relatively inexpensive, reversable/modifiable, and does not promote moisture or heat degradation, and is not ugly.
    This is what I did to my shop as well.
    ~mike

    happy in my mud hut

  15. #15
    Quote Originally Posted by roger wiegand View Post
    Spray foam is way easier albeit more expensive than building some kind of structure and/or fitting rigid foam and will provide much better air sealing. Just depends on how you want to spend your time/money. As with anything there are horror stories with any system you might choose (often trumpeted by the folks selling competing products), but bad experiences are rare with each of these approaches. Check with your local code officials if they would be happy with an intumescent coating in this case vs a rigid fire barrier. If you're willing to run joists across the space then blown in cellulose is a very cost efficient choice for an attic.

    Check out the availability of used polyiso (Craigslist is a place to find it). Insulation is commonly replaced when commercial buildings are re-roofed and the panels get recycled in the secondary market, usually cut up into 4 x 4 pieces. Condition can vary a lot, so look for the better quality stuff. I put 12" of polyiso on top of my son's very low pitched roof for pennies on the dollar of what new foam would have cost, and then a new rubber roof over that to solve a difficult insulation situation. The R value of the old foam is slightly lower than new, but the cost of a couple extra inches is very low.


    I've had spray foam installed on a couple of building projects. In my mild climate zone it's mostly used for tricky areas that are difficult to vent.