    Humidity & low temp in basement shop

    I'm trying to keep the relative humidity (RH) in my basement shop below the level of causing rust and mold/mildew. I've heard I want to keep it at 50% or lower at 70 degrees to accomplish this.

    My question is: I keep the basement unheated at around 46-50 degrees when I'm not working in it. I understand as the temperature goes down the RH rises. So what should my RH goal be at 50 degrees?

    My dehumidifier is running so much trying to keep RH at 50% at 50 degrres that it is freezing up even though it is a low temp model supposedly good down to 43 degrees. Is it broken or just overloaded running constantly to try and reduce RH to an unrealisticly low level?? Would RH at 65% at 50 degrees still prevent rust and mold?

    Thanks, Rick


  2. #2
    Join Date
    Jan 2006
    Location
    Lehigh Valley, PA
    Posts
    410
    Rick, the "relative" in relative humidity accounts for differences in temperature. As far as wood equlibration, mold, and rust are concerned, 50% RH at 70 degrees is equivalent to 50% RH at 50 degrees.

    The problem, as you've found, is that dehumidifcation is tough at low temps. You may have to keep the basement heated up 5 or 10 degrees to achieve your goal.

    The other thing to look at is where the moisture is coming from. In my house, improving the grading and drainage and keeping the gutters clear has made a big differecne in basement dryness.

  3. In my Dungeon in the summer, due to the high humidity here in Tokyo, the aircon/dehumidifier runs 24/7, and I get a lot of water out of there, but I do not have you cool temp problems.

    I wax all of my old iron, and I find taking a shop paper towel, and spraying it with WD-40, folding it up, and putting it in the tool drawers helps keep the rust away.

    Cheers!

  4. #4
    Join Date
    Apr 2006
    Location
    Kansas City, MO
    Posts
    833
    The only problem with the dehumidifier is that the air blowing over the condensate coils is not warm enough to prevent the frost. This can be corrected with higher ambient temperature or higher airflow over the coils. Fans are cheaper than heat so you may try to direct a fan over the coils to keep the frost at bay.
    Chuck

  5. #5
    Join Date
    Feb 2005
    Location
    New Zealand
    Posts
    371
    You may have a fault with your DH unit. I have an old unit here that seems to have the same problem and I have traced to it a sensor on the coils. This should detect when the unit gets too much ice in it and turns off the compressor but leave the fan running. This eventually melts the ice (as long as the ambient is above freezing) and the compressor starts up again. If that sensor is kaput the unit just ices up under heavy use.

    This is obviously going to reduce the amount of water the DH can collect at low temps, but it does let it operate at a lower temp. This de-ice cycle is probably the only difference between the standard and 'low-temp' models.

    Cheers

    Ian

  6. #6
    I had the same problem with ice forming on my dehumidifier. Because I didn't need it to run 24/7, I put it on an electronic timer and cycle it every two hours to prevent ice formation. YMMV

  7. #7
    Join Date
    Apr 2005
    Location
    Appleton, WI
    Posts
    237
    Rick,

    I too have a basement shop and have had luck keeping the RH ~50 with a dehumidifier cycling. My kenmore model wil cycle on and off at 2hr or 6hr intervals. I keep it at 45-55%RH at 60-65degrees and do not get rust and only minimal mildew in the corners of the walls.

    Now on to your question. Rust formation should be better at colder temps. (forgive me if you already know this, but Im a physical chemist so its my thing). The relationship between water, temperature and RH can be a little tricky. %RH is the % of maximum moisture the air can hold. That is, if the air at a given temperature can hold a maximum of 1lb/ft^3 and it actually contains 0.5lb per cubic foot at the same temperature, then the RH=50%. Thats why its relative humidity, its relative to the tempearture. A sealed boz with air and water vapor at 65F will have a higher RH than it will if you heat it up to 85F. This is because cold air cant hold as much moisture as warm air, so for a constant amount of moisture, say 0.25lb/ft^3, as the temperature drops,the RH goes up (until it saturates at the dew point). So, bottom line, the colder you keep your shop the better for rust (less total water in the air), but the harder it is to dehumidify (less of a temperature differential results in more freezeups).

    Hope this helped.
    Jason Morgan

  8. #8
    Join Date
    Mar 2006
    Location
    Kingston, Ontario
    Posts
    390
    Rick:

    Residential dehumidifiers usually work down to 55 grains. Grains is how the actual water content in air is mesured. So that you can only remove a limited amount of water from the air with these units. Commercial dehumidifiers (LGR) Low Grain Refrigerant will work down to 35 grains an down to temperatures of 33 degrees. They also cost about $2,000 US. You could also get into exotics like Desicant Dehumidifiers but they cost even more.

    This is a Psychrometric problem. If you have the time or interest you can study Thermo-dynamics specifically the second law.

    The relative humidity has already been address by one of the posts. What you need to determine is " dew point" this is the point where water vapour will condense out. If you go on the net there are a bunch of site where they have on-line calculators. If you temp and rh are relatively consistent then you can determine dew point. The on-line calculators will give you an idea at what temperature you need to keep your shop so that you do not achieve dew point.

    Hope this helps.

    Greg

  9. #9
    Join Date
    Jan 2005
    Location
    Minnesota
    Posts
    173
    Jason, I'm not sure I understand the last half of your last sentence about colder air being harder to dehumidify. Are you saying it is just difficult mechanically for the dehumidifier because they have to work so hard that they tend to freeze up? Or is it something more complicated?

    Greg, Do you what 55 grains would translate into RH at about 50 degrees?

    Thanks to all so far! Rick


  10. My solution is to get a bad assed dehumidifier. Sadly they are about as expensive as some big stationary tools.

  11. #11
    Join Date
    Mar 2006
    Location
    Kingston, Ontario
    Posts
    390
    Rick:

    Temp Rh GPP

    50 50 26.4

    50 100 53

    You initial post indicated that your temp was about 50 degrees and you were trying to keep your relative humidity at 50%. This gives you a GPP of 26.4. Your dehumidifier only works down to 55 GPP ( Grains per pound). So ineffect your dehumidifier is only making noise and using electricity. AHAM ( American Home Appliance Manufacters) rates dehumidifiers you could check there web site to see what your unit is rated. At 50 degress you would have to have a Rh of slightly over 100% before your dehumidifier would condense water vapour. The reason dehumidifiers work better at warmer temperature is that warm air has more capacity to hold water vapour. We all experience this during July and August where the humidity in the air makes us uncomfortable.

    Greg

  12. #12
    Join Date
    Feb 2003
    Location
    New Orleans LA
    Posts
    1,334
    Rick: IMHO you've been given lot of very good info on dehumidification. But short of dessicant removal of water vapor thus lowering the dew-point and RH you need to heat up the air. This will heat up your tools so they stay above the dew-point and thus there is no condensation deposited on them. This is one heck of a lot cheaper than trying to get a de-humidifier to work in your difficult envirement. I don't have a psycometric (sp?) chart at home, but I guess that raising the dry bulb temperature about ten degrees would do the trick.
    Last edited by Carl Eyman; 05-11-2006 at 3:45 PM.
    18th century nut --- Carl

  13. #13
    Join Date
    Feb 2004
    Location
    Austin, TX
    Posts
    465
    You could try a small heat pump for your basement. This will control temp and humidity and they are relatively inexpensive. Depending on the size of your shop, probably around $1000. This would seem like the best alternative for you.

    Look at the small Sanyo heat Pumps.

    http://www.sanyo.com/industrial/HVAC...ed/Heat_Pumps/
    chris

  14. #14
    Join Date
    Feb 2005
    Location
    Montreal , Canada
    Posts
    759
    Hi Chris......what's involved in installing a system like that in a shop?

    Brent

  15. #15
    Join Date
    Feb 2004
    Location
    Austin, TX
    Posts
    465
    There's not much to setting one up. They come in different styles, but probably a wall unit would work for the shop. So hanging the wall unit and running the 2 copper lines out to the heat pump. You'll want to sit the heat pump on a level pad. You'll also need a dedicated 120V circuit to it. Then adding the refridgerant and bleeding the lines. Probably easiest to get an HVAC person to stop in for that, but should only take a few minutes.

    These units are extremely efficient. So they work great year round and don't cost much to run. You'll just need to clean out the filters on the wall unit.
    chris

Similar Threads

  1. Basement shop construction questions
    By Wes Billups in forum General Woodworking and Power Tools
    Replies: 15
    Last Post: 04-21-2006, 8:12 PM
  2. Picking out the site for my New Shop!
    By Ned Bulken in forum General Woodworking and Power Tools
    Replies: 18
    Last Post: 04-05-2006, 6:56 AM
  3. Best. Shop time. Ever. (Long post, lots of pics)
    By T.J. Mahaffey in forum General Woodworking and Power Tools
    Replies: 8
    Last Post: 01-05-2006, 3:33 PM
  4. Basement shop layout
    By Andy Fox in forum General Woodworking and Power Tools
    Replies: 8
    Last Post: 12-23-2005, 5:31 PM
  5. What are your shop rules?
    By Ron Jones near Indy in forum General Woodworking and Power Tools
    Replies: 38
    Last Post: 05-24-2005, 11:19 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •