    An electric conundrum

    Solved, apparently 4 hours of sleep causes electrical problems.

    I plugged my little Senco compressor into a GFCI outlet and it didn't work. I tried the vacuum also plugged in and it worked fine. I switched the plugs and the results were the same.

    I then tried both at the same time and the compressor worked. Tried everything repeatedly to make sure, and the results were consistent.

    I then plugged the compressor into a non-GFCI outlet and it worked fine. Though the GFCI outlet had nothing else on it, while the non-GFCI outlet was on the same circuit as a number of turned on lights.

    If you can figure this one out you must be brighter than me; it seems impossible to me.
    Last edited by Wade Lippman; 11-20-2007 at 2:24 PM.

  2. #2
    Join Date
    Feb 2003
    Location
    Ft. Thomas, KY
    Posts
    289
    My guess is something is wrong with the GFCI outlet. If you try the compressor in another GFCI outlet, I'll be it works.

  3. #3
    Yep, I'd be looking at the GFCI outlet.
    If sawdust were gold, I'd be rich!

    Byron Trantham
    Fredericksburg, VA
    WUD WKR1

  4. #4
    Join Date
    Oct 2007
    Location
    Minnesota
    Posts
    322
    My guess is that the polarity is backwords on it or something similar. Buy a 5 dollar outlet tester and check it.

    Eric

  5. #5
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,287
    I've had the same problem occasionaly with induction motors on GFCI receptcles.

    In each instance the GFCI has tripped when the centrifugal switch in the starting winding opened.

    I don't have any measurements to back this up, however I would expect that the counter EMF produced in the starting winding when the switch opens, is causing a current that the GFCI thinks is an unbalance, and trips.

    Having another load on the GFCI at the time the start switch opens may reduce the effects, preventing the trip of the GFCI.

    Regards, Rod.

  6. #6
    When you say the compressor doesn't work, is that because the GFCI trips? Or does the compressor just not start without tripping the GFCI?

    In any case, if the problem only happens with that particular GFCI outlet, I'd suspect that GFCI controller. If you can plug the compressor into a different GFCI controlled outlet (controlled by a different GFCI device) and it works, that would be fairly conclusive proof that the problem is that particular GFCI device. It could be that the GFCI device is not wired correctly and that should be checked before replacing it.

    Mike
    Go into the world and do well. But more importantly, go into the world and do good.

  7. #7
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789

    I probably shouldn't admit this...

    I should say that I replaced the GFCI and all is well, but it is much simpler than that.

    The vacuum turns on with a switch; the outlet doesn't have power until it is turned on.

    I am truly sorry for bothering you with this.

Similar Threads

  1. Free loan for my Electric Company.
    By Chris Rosenberger in forum Off Topic Forum
    Replies: 10
    Last Post: 07-06-2007, 12:46 PM
  2. Electric pressure washer
    By Dave Lehnert in forum General Woodworking and Power Tools
    Replies: 11
    Last Post: 05-30-2007, 11:34 AM
  3. Old Electric Wiring :-(
    By Bob Weisner in forum General Woodworking and Power Tools
    Replies: 2
    Last Post: 10-10-2005, 2:09 PM
  4. electric chainsaw choice
    By Dennis Taylor in forum Turner's Forum
    Replies: 4
    Last Post: 05-01-2005, 3:11 PM
  5. OLD!!! Electric wire question
    By Bob Weisner in forum Off Topic Forum
    Replies: 11
    Last Post: 11-30-2004, 10:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •