Thread: Shop Service Panel Question

  1. #1
    Join Date
    Dec 2004
    Location
    Newark, Ohio 43055
    Posts
    89

    Shop Service Panel Question

    Hello Freinds

    I have a quick question about mounting a panel in my garage. I installed a "220 amp pass-through panel" under my meter outside. It feeds a 100 amp panel inside via the pas-through lugs and will be servicing another 100 amp panel in the garage through a 100 amp breaker installed inside this panel outside.

    The question I have is when I bring the feed inside the garage it will be at foot level and then come up. The idea I have is to mount the panel upside down so that the wire can go directly into the panel. All circuit wiring will then come out of the bottom, go up into the attic and then feed wherever I want throughout the garage. I figure this was the cleanest route to get to all the walls, around doors etc and then bring wirind down to appropriate level for an "in-wall" mounting of all boxes. Is this kosher? Can the box be mounted upside down? I may run conduit out of panel and into attic...any ideas on that? Thank you for your input!

    Barry

  2. #2
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,896
    Hmmm...I seem to remember someone posting about mounting their panel upside-down here at SMC some time ago. I would think it doesn't matter as long as the cover can be mounted properly but look forward to the "real" answer!
    --

    The most expensive tool is the one you buy "cheaply" and often...

  3. #3
    Join Date
    Jan 2004
    Location
    Lewiston, Idaho
    Posts
    28,551
    Barry,

    If I was in your shoes, I'd contact my local electrical inspector. Regardless of how difficult it may make things, I always do things to code or better. I know of folks locally who haven't and when they went to sell a home, a home inspector caught the problem and informed the local building codes folks. It's almost always easier and cheaper to do it right the first time.

    JMHO.
    Ken

    So much to learn, so little time.....

  4. #4
    Join Date
    Jun 2007
    Location
    Tipp City, Ohio
    Posts
    41
    Quote Originally Posted by Barry Londrigan View Post
    \
    The question I have is when I bring the feed inside the garage it will be at foot level and then come up. The idea I have is to mount the panel upside down so that the wire can go directly into the panel.
    Barry

    Are you running the panel feed through conduit? Either way there is usually a large knockout at the bottom of the panel as well so that a large connector can be used. Run the cable into the bottom and bring one leg and the nuetral up one side and the other leg up the opposite side.

    Make sure you leave pleanty og extra cable to make "long swooping loops" into the main lugs at the top of the panel. If you ever have a problem (burn one of the lugs out, etc.) and have to remake the main connections you can simply loosen the wires and remove a short amount and hook it back up and not have to pull new feeders back in.


    I did electrical work for several years and I would personally mount the panel upright and not upside down. The post about talking to the local inspector (as that job should require a permit in most areas) would be a good bet also. Especially if you are not sure. Nothing worse than doing a job and then either having to re-do it for the inspector or at some point down the road when you might sell your house, etc.

    Just my 2 cents.....hope this helps.

    JW

  5. #5
    Join Date
    May 2007
    Location
    Summit, New Jersey
    Posts
    70
    Quote Originally Posted by Ken Fitzgerald View Post
    Barry,

    If I was in your shoes, I'd contact my local electrical inspector. Regardless of how difficult it may make things, I always do things to code or better. I know of folks locally who haven't and when they went to sell a home, a home inspector caught the problem and informed the local building codes folks. It's almost always easier and cheaper to do it right the first time.

    JMHO.
    Not to mention the potential liability of doing things that aren't up to code and not permitted, not inspected, etc. If there's a fire sometime in the future and it is traced to electrical work done by unlicensed person(s) without a permit and thus not inspected, you could be in deep do-do.
    Visit Peercon.com

  6. #6
    Join Date
    Sep 2007
    Location
    Upstate NY
    Posts
    3,789
    It is okay if the breakers move side to side. If they move up and down it is not acceptable; as then they would be down when closed, which is the normal position for open.

  7. #7
    Join Date
    Oct 2007
    Location
    St Marys, West Virginia
    Posts
    597
    I mounted mine "upside down" with the lead coming in from the bottom and main breaker at the bottom. It is square D with side to side movement breakers.

    My step father assisted me and he is a retired electrician, still licensed and up with our local codes. No problems here. Doesnt hurt to ask though before you do it. You might get suprised if you dont.
    One good turn deserves another

  8. #8
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,896
    I forgot to mention earlier that the SD subpanel in the addition is mounted with the leads coming in from the bottom. I have no idea if that is upside down or not, however...I didn't look that close.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  9. #9
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    Jim, does it have a main breaker in it? If so and it is at the bottom of the box, it's upside down. I also seem to remember the thread where someone here did this type of wiring. I do know one person that used to be on the Creek that has 2 boxes, both upside down. It wasn't a problem for his area.
    If nothing else, I'd do as others have said and ask the local code people. No matter if it is "ok" by code, if they don't like it, you could still have trouble later on. Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  10. #10
    Join Date
    Mar 2003
    Location
    SE PA - Central Bucks County
    Posts
    65,896
    Jim, a subpanel doesn't get a main breaker...that's back at the main panel.
    --

    The most expensive tool is the one you buy "cheaply" and often...

  11. #11
    Join Date
    Dec 2003
    Location
    West of Ft. Worth, TX
    Posts
    5,815
    My bad! I was in the train of thought of breaker boxes in general and didn't think about it being a sub panel. Jim.
    Coolmeadow Setters...Exclusively Irish! When Irish Eyes are smiling....They're usually up to something!!
    Home of Irish Setter Rescue of North Texas.
    No, I'm not an electrician. Any information I share is purely what I would do myself. If in doubt, hire an electrician!
    Member of the G0691 fan club!
    At a minimum, I'm Pentatoxic...Most likely I'm a Pentaholic. There seems to be no known cure. Pentatonix, winners of The Sing Off, s3.

  12. #12
    Join Date
    Oct 2007
    Location
    Whidbey Island , Wa.
    Posts
    914
    Quote Originally Posted by Jim Becker View Post

    Jim, a subpanel doesn't get a main breaker...that's back at the main panel.
    That is not always the case. A sub panel can have a main breaker as well. So that's a "it depends" thing.

  13. #13
    Join Date
    Oct 2006
    Location
    Mid Michigan
    Posts
    3,559
    Some boxes are designed to be used in both directions. I have a couple of sub panels that are wired where the input is in the base and the output is through the top. The panels are not upside down but are wired that way. I do not know if there is any code that dictates the mounting direction.
    On the outside of my house I have a 200 amp panel with a 200 amp main breaker and 2ea 100 amp breakers that feed two separate 100 amp sub panels in my basement. I had it done this way so I could do wiring on my house and still have power from one of the breaker panels. Each of the 100 amp panels have a 100 amp breaker that cuts power to the individual panels. Not sure if they would be called "main" breakers because when I work in the panels I kill the 100 amp outside breaker. It is overkill but I feel much safer with no power feeding the panel when working in it.
    David B

  14. #14
    Join Date
    Oct 2007
    Location
    Whidbey Island , Wa.
    Posts
    914
    Quote Originally Posted by David G Baker View Post
    On the outside of my house I have a 200 amp panel with a 200 amp main breaker and 2ea 100 amp breakers that feed two separate 100 amp sub panels in my basement. I had it done this way so I could do wiring on my house and still have power from one of the breaker panels. Each of the 100 amp panels have a 100 amp breaker that cuts power to the individual panels. Not sure if they would be called "main" breakers because when I work in the panels I kill the 100 amp outside breaker. It is overkill but I feel much safer with no power feeding the panel when working in it.
    David I have almost exactly the same set up here at my place , only one sub panel CB feeds my shop. So we both have a lot of 100 amp C/B's.

  15. #15
    Rob Will Guest
    Yes, it is ok to mount a panel with the main at either the top or bottom.
    Personally, I try to avoid "upside down" but I have no reason other than asthetics. Of greater importance is the issue of bonding.

    At the first point of service (first distribution panel), the ground and neutral are bonded to the case. This location also gets two ground rods driven 5' apart.

    All panels beyond that point are considered "sub panels". These must be fed with a separate ground and neutral wire. Never bond the ground (equipment ground) and neutral (load carrying grounded conductor) together in a sub panel. The neutral bus is insulated from the case.

    Rob

Similar Threads

  1. Planning for new shop - electrical question
    By Lou Ferrarini in forum General Woodworking and Power Tools
    Replies: 18
    Last Post: 10-29-2007, 9:22 PM
  2. Shop wiring help (I think again =)), 3 phase question as well.
    By Chris Pasko in forum General Woodworking and Power Tools
    Replies: 6
    Last Post: 01-19-2006, 10:27 AM
  3. Shop Tour #1: Le-ca-getty Central. The Power House
    By Dev Emch in forum General Woodworking and Power Tools
    Replies: 24
    Last Post: 10-01-2005, 11:19 PM
  4. Shop power question - who needs 3 phase anyway?
    By lou sansone in forum General Woodworking and Power Tools
    Replies: 31
    Last Post: 04-04-2005, 11:31 AM
  5. raised panel opinion question
    By David Rose in forum General Woodworking and Power Tools
    Replies: 18
    Last Post: 06-06-2004, 11:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •