    Electrical wiring question

    If the power for a light fixture is coming directly into the ceiling box, and I have one (1) 14-2 wire running from the light fixture to the switch, I can't run additional switched light fixtures off that switch, can I? I would have to have another wire running into the switch with a ground and neutral, correct?

    Untitled.jpg

    Thanks,

    Amy

  2. #2
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,281
    No Amy, you cannot since there is no neutral in that switchbox.

    You could run additional switched fixtures from the wiring in the existing switched fixture however.

    If you really want to run other fixtures from the physical switch box, the wire from the exosting switch box to the existing switched fixture would have to be changed to 14/3 to provide a neutral in the switchbox.

    Regards, Rod.
    Last edited by Rod Sheridan; 08-05-2008 at 9:54 AM.

  3. #3
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    I agree with Rod.

    Given the current wiring setup (i.e., without replacing the cable from the fixture to the switch) the only way to add additional switched fixtures is to feed them from the fixture box because you have both the switched hot and neutral in that fixture box.

    FYI, Rod was correct about something else. You would need to replace the 14/2 with 14/3 - you can't just run another single conductor. For the kind of wiring we're doing, all the conductors for a circuit must be in the same cable assembly.

  4. #4
    Join Date
    Jan 2008
    Location
    Auburn, AL
    Posts
    104
    Okay, so I just put up drywall over the fixture and I would really hate to have to take the full sheet down.

    You see the cable that runs power to the next room? Can I run an additional 14-2 from that line to the switch box to power the additional fixtures? I know it might seem a little strange, but I am in the process of a remodel and there's a junction box down the line a little bit and it's closer to the wall in the middle of a half sheet of drywall. That would make it the configuration of the drawing, plus two more switches making it a triple gang box with another 14-2 running into the switchbox through the other two switches and out to power the two new fixtures.

    BTW, I currently have no drywall on the walls. I redid the ceilings first and now the walls.

  5. #5
    Join Date
    Jun 2008
    Location
    Mobile, Alabama
    Posts
    75
    you can run several fixtures from the one switch so long as you don't exceed the amperage rating of that switch... it would take several multi bulb fixtures to do that... however, there may be other items on the same circuit such as outlets, etc.

    There are several ways of doing this. all the switch is doing is connecting the hot wire back to itself... you can run additional hot (usually black wire) back to the switch and from there to the fixture.

    I'm not sure that this is the solution to your question or not... as I'm not sure that what you're asking is practical... you'd be using a switch in one room to control lighting in more than just that room?

  6. #6
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Amy,

    You can sort of do what you want. It's perfectly acceptable to have multiple feeds into a switch box. In this case, they are all on the same circuit, so when you kill power to the circuit - the entire switch box will be dead.

    Are you planning the new switch(es) for wall-mounted lights? If so, do you want to be able to control them individually (is that why 2 new switches)? If "Yes" to the individual control, unless you will have (3) new 14/2 cables (1 to supply power to the switches + a neutral, 2 to run out to the new fixtures with power and neutral for each fixture) - then you will need some 14/3 and we'd need to layout how you're wiring things.

    When you say "junction box", I assume you mean a receptacle or fixture box - not a plain-front box that's in the wall. Is that correct?

    Rob

  7. #7
    Join Date
    May 2008
    Location
    Barnesville, GA
    Posts
    70
    Amy,

    I know this is kind of a standard answer, but do a google search for "wiring diagram", and there are a couple of good sites that come up. I have done a lot of wiring in a renovation in Auburn and another one right down the road in Opelika, and I always have to consult one site or another as electrical work doesn't come naturally to me.

    Wright

  8. #8
    Join Date
    Jan 2008
    Location
    Auburn, AL
    Posts
    104
    Quote Originally Posted by Rob Russell View Post
    Are you planning the new switch(es) for wall-mounted lights? If so, do you want to be able to control them individually (is that why 2 new switches)? If "Yes" to the individual control, unless you will have (3) new 14/2 cables (1 to supply power to the switches + a neutral, 2 to run out to the new fixtures with power and neutral for each fixture) - then you will need some 14/3 and we'd need to layout how you're wiring things.

    When you say "junction box", I assume you mean a receptacle or fixture box - not a plain-front box that's in the wall. Is that correct?

    Rob
    The new sketch should explain everything a little better. The dotted lines are wires I have yet to run. The wire to the porch lights and floodlights will be easy since the drywall is off the walls. Both porch lights will be switched together, and the same for the floodlights. It's the one from the junction box to the switches providing full power to the two additional switches that I forgot and will be a pain.

    So in the final setup the dining room light will be powered by one (1) strand of 14-2 to the switchbox and the power for the porch and floodlights will be run to the switch box with 14-2, then wire to each of the two fixture circuits will be run with 14-2 (or 14-3 just in case I decide to put ceiling fans at the porch lights later on.

    Yes, the junction box I speak of is a receptacle box mounted in the ceiling with a blank plate over it. I couldn't replace the whole run of wire and I wanted to be able to access it later anyway.

    Back porch wiring.jpg

  9. #9
    Join Date
    May 2008
    Location
    Barnesville, GA
    Posts
    70
    Quote Originally Posted by Amy Leigh Baker View Post
    The new sketch should explain everything a little better. The dotted lines are wires I have yet to run. The wire to the porch lights and floodlights will be easy since the drywall is off the walls. Both porch lights will be switched together, and the same for the floodlights. It's the one from the junction box to the switches providing full power to the two additional switches that I forgot and will be a pain.

    So in the final setup the dining room light will be powered by one (1) strand of 14-2 to the switchbox and the power for the porch and floodlights will be run to the switch box with 14-2, then wire to each of the two fixture circuits will be run with 14-2 (or 14-3 just in case I decide to put ceiling fans at the porch lights later on.

    Yes, the junction box I speak of is a receptacle box mounted in the ceiling with a blank plate over it. I couldn't replace the whole run of wire and I wanted to be able to access it later anyway.

    Back porch wiring.jpg
    Amy,

    Is there any reason not to run the power to the outside fixtures and then run switch legs back to the switches? It will not solve your problem of getting back to your junction box above the drywall, but I have found that feeding a circuit through the switch box makes that box get full quick. There usually seems to be more room behind the fixtures than behind the switches. Just my 2 cents.

    Do you think there is any possibility of running a fish tape above your drywall to run the new wire to the junction box so you don't have to pull the drywall down?

    Also, why would you need 14-3 for ceiling fans? As I said before, i'm no electrical engineer, but I think all my fans are run off 14-2.

    Wright

  10. #10
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Amy,

    What you are proposing will work just fine and meets most code requirements. Mind you, I'm not a licensed electrician - just an anal nut who likes to read the National Electric Code (NEC) and has done a lot of wiring (I wired the 1000' sq ft addition to our house including subpanels). Note that by "code", I mean the NEC which is a baseline model. The "code as adopted" by the local "Authorities Having Jurisdiction" (AHJ) varies. Some places are really lenient when it comes to code, others are stricter.



    A few things to be careful about:
    • The "junction box" on your diagram needs to be large enough from a "conductor fill" perspective. #14 needs 2 cubic inches per conductor entering or exiting the box + 2 cubic inches for all of the equipment grounding conductors (EGCs) combined. You have at least (6) #14 conductors + the EGCs, so that's a minimum of:

    ((6) conductors + EGCs) * (2) cu/conductor = 14 cubic inches.
    The smallest boxes you can typically buy now are 14 cu so that just fits, but if you reused an older box - it could be smaller. That would mean digging out that old box and replacing it with something larger. If you have other parts of the circuit that run though that box, you need to check the box size. If you have more than what's shown in your diagram, post a diagram of what you can see entering and exiting the "junction box" and I (or someone else) will give you the box size requirements.

    Another thing to consider is whether or not you will ever want to put a receptacle there for a light that just plugs in to the receptacle or fish a cable through to feed a light. If you have a 14 cu box - it's full now.
    • If you think you may replace the porch lights with ceiling fans, make sure that you use "ceiling fan rated" boxes now. Those are designed for the weight and vibration of a fan. You may never put fans out there (although I wouldn't take that bet considering you're in Alabama), but if you ever want to - code does specifically require boxes rated for fans.
    • If the outside porch is "exposed to weather" or "damp", you may want to check with your local building inspector to see what they require for wiring. It may means direct burial or other "damp location rated" stuff, which would be a real nuisance. The point is that NM-B, isn't rated for "damp" locations. An "open or expsed porch" is considered "damp". If your porch ceiling is covered with anything (plywood, beadboard, etc.) - I believe that becomes a non-issue, but check with the local code weenies.
    • FYI (and this is REALLY picky, so forgive me), a cable isn't called a "strand". That's a single cable. A strand is one of the small wires that's part of a single "stranded" conductor. If you look at NM-cable (aka "Romex"), the conductor is a single "strand" of metal. When you get up to larger stuff like anything larger than #10, the metal inside the insulation is made up of a bunch of smaller wires all twisted together. Those small wires twisted together are individually called "strands".

    I'm only pointing that out so you don't go into a big box store or electrical supply house and ask for a "single strand" of cable because it'll make you look like you don't know what you're doing. You are already tackling WAY more than many guys and most women do. I applaud you for that effort because I, personally, think wiring's fun.
    I'm happy to provide NEC code cites if you want the code references behind what I've cited you here for points #1 and 2.

    Beyond that - you've got a great plan going! Hapy wiring. I really do love this stuff! You should see the wiring diagram for our addition. Our GC told me that it would have been a $10K - 15K job for what I did (very sophisticated lighting and other wiring).
    Last edited by Rob Russell; 08-05-2008 at 5:45 PM.

  11. #11
    Join Date
    May 2004
    Location
    Vancouver, Washington
    Posts
    396
    Quote Originally Posted by Wright Woodall View Post

    Also, why would you need 14-3 for ceiling fans? As I said before, i'm no electrical engineer, but I think all my fans are run off 14-2.

    Wright
    It's not that the fan needs the 3rd wire, but depending on how the rest of the run is wired, it still might be needed to make sure all the loads are run in parallel.

    I learned this a few day ago because I was wiring switch that controls 2 outlets. I ran power to the outlets first, then the switch at the end. To do this, you need a section of 3 wire between the outlets (as in, 14/2 from breaker to outlet 1, 14/3 from outlet 1 to outlet 2, then 14/2 from outlet 2 to switch). Hard to describe why using words, but think of it like running the neutral (white) from breaker to both the outlets directly, then running the hot (black) to the switch first, then back to the outlets.

    Had I ran power to switch first, then everything downstream from it could have used 14/2.

    Shaddy

  12. #12
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Wright Woodall View Post
    Amy,
    Is there any reason not to run the power to the outside fixtures and then run switch legs back to the switches? It will not solve your problem of getting back to your junction box above the drywall, but I have found that feeding a circuit through the switch box makes that box get full quick. There usually seems to be more room behind the fixtures than behind the switches. Just my 2 cents.
    The first reason I can think of is that it would complicate the wiring. Doing it your way would mean running multiple cables out to the outside fixtures - one into the box as a power feed, the second for the switched legs. More cables = more complexity (JMO).

    Quote Originally Posted by Wright Woodall View Post
    Amy,
    Is there any reason not to run the power to the outside fixtures and then run switch legs back to the switches? It will not solve your problem of getting back to your junction box above the drywall, but I have found that feeding a circuit through the switch box makes that box get full quick. There usually seems to be more room behind the fixtures than behind the switches. Just my 2 cents.
    Interesting suggestion. It could work, although it's "normally" (opinion here!) done so power feeds to the switch and then out to the fixture. Doing it backwards can drive an electrician batty, especially with some of the really old "share wire" schemes are used. Note my comments above and imagine that you're the homeowner trying to figure out how something is wired.

    Quote Originally Posted by Wright Woodall View Post
    Amy,
    Do you think there is any possibility of running a fish tape above your drywall to run the new wire to the junction box so you don't have to pull the drywall down?
    Very good question.

    Quote Originally Posted by Wright Woodall View Post
    Amy,
    Also, why would you need 14-3 for ceiling fans? As I said before, i'm no electrical engineer, but I think all my fans are run off 14-2.
    Ceiling fans frequently have a light, so you need (2) hot conductors to the fan (w/light) so you can control the fan and light separately.

  13. #13
    Join Date
    Feb 2003
    Location
    South Windsor, CT
    Posts
    3,304
    Quote Originally Posted by Shaddy Dedmore View Post
    I learned this a few day ago because I was wiring switch that controls 2 outlets. I ran power to the outlets first, then the switch at the end. To do this, you need a section of 3 wire between the outlets (as in, 14/2 from breaker to outlet 1, 14/3 from outlet 1 to outlet 2, then 14/2 from outlet 2 to switch). Hard to describe why using words, but think of it like running the neutral (white) from breaker to both the outlets directly, then running the hot (black) to the switch first, then back to the outlets.

    Had I ran power to switch first, then everything downstream from it could have used 14/2.
    Shaddy,

    I'm glad you posted this.

    The thing to learn from his post is that there MAY be easier ways of doing things - but that's not always true.

    • If the switch Amy describes is on the "other end of the room" from the receptacles, Paddy's way is the cheapest way to wire it.
    • If the wiring is such that you want nothing other than switched receptacles, then hit the switch first and receptacles afterwards.
    • Another option is a combo - hit the switch first and run the 14/3 or 12/3 because it allows you to splitwire the receptacles and have (1) outlet switched and (1) outlet always hot.
    Best,

    Rob
    Last edited by Rob Russell; 08-05-2008 at 8:24 PM.

Similar Threads

  1. Electrical Circuit Breaker Question
    By John Pahl in forum WorkShops
    Replies: 19
    Last Post: 04-29-2008, 4:47 PM
  2. Replies: 26
    Last Post: 03-11-2008, 8:21 AM
  3. Need help easy electrical question Jointer
    By Craig D Peltier in forum General Woodworking and Power Tools
    Replies: 7
    Last Post: 03-30-2007, 10:26 AM
  4. Gast Vacuum Pump Electrical Question
    By Christopher K. Hartley in forum Turner's Forum
    Replies: 7
    Last Post: 03-24-2007, 9:18 AM
  5. Electrical question
    By Joe Bourbois in forum General Woodworking and Power Tools
    Replies: 7
    Last Post: 03-01-2004, 11:45 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •