    Garage Furnace Intallation

    Hi everyone,
    Just want to take a quick poll of any of you who might be famaliar with this...
    Im installing a furnace in my garage to help with these 2° days. The furnace is one of those in-wall units designed for apartment buildings and other small spaces. It does not have an enclosed burner, and my HVAC guy said that often in garages there is a minumum height from the garage floor that the burner must be to avoid incidents with things like gas fumes. He didn't know the required height, so I called our town's building inspector.
    The building inspector (who Im fairly sure I woke up with my call - at 10:30am on a Wed) told me that it would have to be 4 feet from the floor. FOUR FEET?
    I know local codes are going to be different from place to place, but Ive done a lot of searching on the interweb and every other code I can find says 18''. Anyone have any thoughts...?
    Proud to Hate Michigan Athletics Since 1981

    [SIGPIC][/SIGPIC]

  2. #2
    I'm willing to bet the manufacturer or a qualified installer will know your state's/NFPA regs.

    4 feet may not be unreasonable for garage space without an active air change system. 'swhy you don't see these in commercial shops very often. Overhead units are 7'+ off the floor.
    "I love the smell of sawdust in the morning".
    Robert Duval in "Apileachips Now". - almost.


    Laserpro Spirit 60W laser, Corel X3
    Missionfurnishings, Mitchell Andrus Studios, NC

  3. #3
    Join Date
    Jan 2007
    Location
    State Capital, WI
    Posts
    470
    Jason -

    I wanted to install a smaller water heater in my garage in T of Middleton this year. Building inspector said open ignition sources to be a minimum of 18" above garage floor....

    This should be an easy find in the CODE CHECK books that are at Home Depot. I know that they list many of the gas codes in the plumbing book - it may be worth a shot...

    If he insists on 4-ft - ask to see the code - either IBC or UDC

    Lov'in the plowing job on Madison streets Today! - Rob
    oops ....1,2,3,4,5,6,7,8,9,10 - yup all there, whew!

  4. #4
    Furnace -

    International Residential Code -

    G2408.2(305.2)
    Equipment and appliances having an ignition source shall be elevated such that the source of ignition is not less than 18 inches (457mm) above the floor in hazardous locations and private garages. For the purpose of this section, rooms or spaces that are not part of the living space of a dwelling unit and that communicate directly with a private garage through openings shall be considered to be part of the private garage.

    So 18" is the magic #.

    In the case the manufactueres requirements are more stingent, follow there requirements.
    Last edited by Matt Ocel; 12-10-2008 at 8:07 PM.

  5. Local jurisdictions are free to implement more stringent requirements, so regardless of what the national codes say, it's what your jurisdiction says that goes.

    Ask him to show it to you in your city/town's codes.

  6. #6
    Join Date
    Dec 2004
    Location
    NW Indiana
    Posts
    1,050
    I have one in my shop also a garage. Code is for OPEN ignition or flame. My unit a Williams is a close combustion unit. It has a double wall flue that also brings in combustion air though inside pipe. Exhaust out the outside wall of the pipe. The code is mainly for hot water heaters. Code here is 18" also.

  7. #7
    Quote Originally Posted by Russ Massery View Post
    I have one in my shop also a garage. Code is for OPEN ignition or flame. My unit a Williams is a close combustion unit. It has a double wall flue that also brings in combustion air though inside pipe. Exhaust out the outside wall of the pipe. The code is mainly for hot water heaters. Code here is 18" also.
    A regular wall furnace has a open flame.

    BTW, if the water is hot why does it need heating?

  8. #8
    Join Date
    Oct 2008
    Location
    Madison, WI
    Posts
    272
    Well I did some checking on my own, and found my city's building codes posted online... it basically referred me to the WI state building code. Read thru that and it said 18'' for open flame units such as my furnace.
    Called the HVAC guy Im going to have check over the unit (I did the conversion from NG to LP myself, so Im definitely gonna have it looked over and fired up for the first time by a pro) and he said our local code is 18''. Just to verify he called the same building inspector I did, and HE said 18''...
    So yeah, 18'' it is.
    Gonna head out now and raise 'er up!
    Proud to Hate Michigan Athletics Since 1981

    [SIGPIC][/SIGPIC]

  9. #9
    Join Date
    Oct 2008
    Location
    Madison, WI
    Posts
    272

    Liftoff Achieved

    Aaand Done!
    HVAC guy is coming to do final hookup and testing tomorrow morning.
    I can almost feel the heat already.... brrr, almost...
    Attached Images Attached Images
    Proud to Hate Michigan Athletics Since 1981

    [SIGPIC][/SIGPIC]

Similar Threads

  1. Optimal Placement of Garage Heater
    By Andrew Thuswaldner in forum Off Topic Forum
    Replies: 4
    Last Post: 01-04-2008, 10:10 AM
  2. Detached Shop or Extended Garage?
    By Kirk Poore in forum General Woodworking and Power Tools
    Replies: 12
    Last Post: 09-07-2006, 7:13 AM
  3. Question about venting garage furnace
    By Steven J Corpstein in forum General Woodworking and Power Tools
    Replies: 3
    Last Post: 01-17-2006, 9:48 PM
  4. Garage in the winter....
    By Dennis Peacock in forum Off Topic Forum
    Replies: 9
    Last Post: 12-10-2005, 11:47 PM
  5. Heating a garage workshop
    By Bob Weisner in forum General Woodworking and Power Tools
    Replies: 9
    Last Post: 02-03-2004, 1:23 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •