Page 4 of 4 FirstFirst 1234
Results 46 to 56 of 56

Thread: 220 to 110

  1. #46
    Join Date
    May 2009
    Location
    N.W. Missouri
    Posts
    1,564
    I'm going to swat the hornets nest and say yes, you can. I don't think you even need a 220v breaker. 2 single pole breakers can replace the 2 pole 30 amp breaker.

    John

  2. #47
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,306
    Quote Originally Posted by Dennis McDonaugh View Post
    This has gotten a little off topic, but as I understand it I can replace one 30 amp 220 outlet with two 20 amp 110 outlets using one neutral for both outlets if I replace the 30 amp 220 breaker with a 20 amp 220 breaker? Is that the gist of it?
    Yes, if you're sharing the neutral (Multi-Wire Branch Circuit) you need a 2 pole breaker. (That's the proper name for what you're calling a 220 breaker).

    Regards, Rod.

  3. #48
    Join Date
    Dec 2006
    Location
    Toronto Ontario
    Posts
    11,306
    Quote Originally Posted by John McClanahan View Post
    I'm going to swat the hornets nest and say yes, you can. I don't think you even need a 220v breaker. 2 single pole breakers can replace the 2 pole 30 amp breaker.

    John
    Hi John, if he's sharing the neutral, it has to ba 2 pole breaker, not 2 single pole breakers............Regards, Rod.

  4. #49
    Join Date
    Dec 2003
    Location
    SF Bay Area, CA
    Posts
    15,332
    Quote Originally Posted by Rod Sheridan View Post
    Hi John, if he's sharing the neutral, it has to ba 2 pole breaker, not 2 single pole breakers............Regards, Rod.
    Maybe this picture helps?
    multiwire branch circiut graphic.jpg
    Wood: a fickle medium....

    Did you know SMC is user supported? Please help.

  5. #50
    Join Date
    May 2009
    Location
    N.W. Missouri
    Posts
    1,564
    Quote Originally Posted by Rod Sheridan View Post
    Hi John, if he's sharing the neutral, it has to ba 2 pole breaker, not 2 single pole breakers............Regards, Rod.

    Why?


    John

  6. Quote Originally Posted by John McClanahan View Post
    Why?


    John
    It's a code requirement, because if you shut down one breaker, you can backfeed voltage to what would otherwise be a de-energized leg.

  7. #52
    Join Date
    May 2009
    Location
    N.W. Missouri
    Posts
    1,564
    Quote Originally Posted by Rick Christopherson View Post
    It's a code requirement, because if you shut down one breaker, you can backfeed voltage to what would otherwise be a de-energized leg.
    Not trying to argue, but where would the backfeed voltage come from?

    I understand the need for the 2 hot leeds to be on different legs, and a 2 pole breaker would guarantee that.

    John

  8. In the 2005 NEC, the 2-pole breaker requirement applied only if there were 240-volt loads or if any single device (like duplex outlet) connected to both phases. In 2008 this was changed so that all MWBCs require 2-pole breakers no matter how they are used. (NEC 210.4)

    If there are any 240-volt loads on the MWBC and you open only one breaker, it will put 120 volts on the open phase via the load. The same can happen if you lose the neutral and there are 120 volt loads. While that may appear to be unlikely to happen, if someone has a floating neutral condition, opening one of the breakers could very well be one of the first troubleshooting steps an electrician or homeowner takes. An open neutral will exhibit bright lights and dim lights, and people will typically begin flipping breakers to protect those loads.

  9. #54
    Join Date
    May 2009
    Location
    N.W. Missouri
    Posts
    1,564
    OK, thanks, Rick. I once worked for an electrician wiring new houses and duplexes. A few times we would split a duplex outlet up and powered it from 2 breakers at kitchen counters. That way the outlet could power a coffee maker and toaster oven without tripping the breaker. We didn't use 2 pole breakers, but that was in the mid 80"s.

    John

  10. #55
    Quote Originally Posted by Rick Christopherson View Post
    Failing an inspection does not make something a local rule. By your own admission, you deliberately did not challenge the inspector because you didn't want to ruffle his feathers.

    All you had to do was ask the inspector to cite his reference (as any electrician would have done). This is not challenging him. This is what he is required to do.
    You obviously haven't worked with many inspectors. I've seen inspectors make up rules on the spot. I challenged one who was about to cost my company and our client a lot of money and he just spun the written law to be interpreted so it fit the new rule he just made up. I have dozens of accounts like that and those who work in the construction business have countless more.

    When working with an inspector, you have to have a feel for him or her and know when to back down. After you have established a good working relationship with the inspector, he or she usually works with you so as not to cost your or your company money unnecessarily. Those of us in the building trades know this and it's a more important tool in getting the job done than knowing the code verbatim.

    A clause that popped up in more and more contracts over the years was that the sub-contractor not only had to meet the specifications laid out by the drawings and specs, but also was required to meet code. In other words, the architects and engineers no longer accepted responsibility that their drawings and specs met local code. That responsibility was being passed down to the general contractor. And the general contractor would pass that down to the sub-contractors. So anytime I was entering a new municipality, I would call the inspector and inquire about anything that I thought may be a sticky point before submitting our bid. Of course, I would first ask what code they follow. Rarely did I find a municipality that followed the NEC without having any addenda. But that first call to the inspector pretty much guaranteed our work would pass inspection.

    From my experience and the experience of other construction professionals I've talked to over the years, you're always better off being diplomatic (and respectful) with an inspector than challenging him or her and standing firm on your beliefs. Whether I was working with the inspector as a foreman or project manager, I knew the best way to insure the jobs passed inspection was by having a good relationship with the inspector. The code is like a law book, it can be interpreted many ways and the experienced inspector knows how to use this to his or her advantage. And they love doing that especially when they think they are faced with a know-it-all. I've heard more than one say just that. Diplomacy is always the best policy.

  11. #56
    Join Date
    Dec 2003
    Location
    SF Bay Area, CA
    Posts
    15,332
    I think this thread has drifted way off topic. Time to move on, Folks. Thank you.
    Wood: a fickle medium....

    Did you know SMC is user supported? Please help.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •