    Quote Originally Posted by Greg Funk
    While the receptacle I showed supports 30A plugs it's not clear to me why you couldn't put regular 15A receptacles on a 30A circuit. The circuit breaker provides protection for the wiring not the device plugged into it.
    Greg
    Among other things, wire size. Most 15A or even 20A duplex receptacles are not sized to handle the larger incoming and outgoing wires. The wiring box can also get pretty tight. This is more of an issue if you use GFCI outlets, which may be why no GFCI outlets were in use in there.

    More importantly, if that wire has 30A going through it due to being at or near capacity, all the upstream outlets (between you and the breaker box, as they are chained) must be able to survive 30A of current. A 15A outlet is rated to only handle 15A. Outlet go boom.

    Pete

  2. #47
    Join Date
    Jan 2007
    Location
    Gambrills, MD - Near Annapolis
    Posts
    556
    Found this:

    NEC Table 210.21(B)(3)
    Circuit rating (amperes) Receptacle rating (amperes)
    15 not over 15
    20 15 or 20
    30 30
    40 40 or 50
    50 50

  3. #48
    Join Date
    Oct 2006
    Location
    Annapolis MD
    Posts
    44

    a couple of things to think about

    On the 30 amp 120 circuits unless you are the original owner of the house check the wire size feeding the garage. Do not rely on the breaker size, it is possible that a previous owner installed a larger breaker due to nuisance tripping or other needs but the wire in the wall is not #10 or better.

    As for GFCI requirement All general purpose outlets in unfinished basement and garages are required to be GFCI. Dedicated outlets such as those for a freezer, Dust collector, Sump pump do not have that requirement. You can buy double pole GFCI breakers $$$$$ but they are not required for dedicated uses.

    /paul

  4. #49
    Join Date
    Jan 2007
    Location
    Gambrills, MD - Near Annapolis
    Posts
    556
    Quote Originally Posted by paul aubin
    As for GFCI requirement All general purpose outlets in unfinished basement and garages are required to be GFCI. Dedicated outlets such as those for a freezer, Dust collector, Sump pump do not have that requirement. You can buy double pole GFCI breakers $$$$$ but they are not required for dedicated uses.
    /paul
    Also keep in mind that being GFCI protected does not mean you need a GFCI outlet in each box. You only need one on each circuit.

    Pete

  5. #50
    Join Date
    Nov 2006
    Location
    Vancouver, BC
    Posts
    858
    Quote Originally Posted by Pete Brown
    More importantly, if that wire has 30A going through it due to being at or near capacity, all the upstream outlets (between you and the breaker box, as they are chained) must be able to survive 30A of current. A 15A outlet is rated to only handle 15A. Outlet go boom.
    Pete
    I don't really understand what you are saying here. Why would the load be running through an upstream outlet? I suppose if you were using the receptacle to tie the wires together rather than a using a mar connector? I am not an electrician so I don't know if that is proper. In any case I wouldn't do this and I am not recommending it for anyone else.

    I think this discusssion is somewhat interesting but not really germane to the topic so I will bow out now...

    Greg

  6. #51
    Join Date
    Dec 2006
    Location
    Eastern Iowa
    Posts
    37
    Quote Originally Posted by paul aubin
    As for GFCI requirement All general purpose outlets in unfinished basement and garages are required to be GFCI. Dedicated outlets such as those for a freezer, Dust collector, Sump pump do not have that requirement. You can buy double pole GFCI breakers $$$$$ but they are not required for dedicated uses.

    /paul
    Only if they're 120V, 15A or 20A receptacles. Local codes may be more strict, but the NEC doesn't require GFCI protection on 240V general-use receptacles. Or on 120V receptacles at 30A or above.


    Greg:
    I don't think you can plug normal 15A plugs into that 30A receptacle you have pictured. This website has a good description of the various NEMA plug and receptacle configurations, and I don't see anything in 120V, 30A that mates with 'standard' 15A (or 20A) plugs.
    http://www.stayonline.com/reference-...ght-blade.aspx

  7. #52
    Join Date
    Jan 2007
    Location
    Gambrills, MD - Near Annapolis
    Posts
    556
    Quote Originally Posted by Greg Funk
    I don't really understand what you are saying here. Why would the load be running through an upstream outlet? I suppose if you were using the receptacle to tie the wires together rather than a using a mar connector? I am not an electrician so I don't know if that is proper. In any case I wouldn't do this and I am not recommending it for anyone else.

    I think this discusssion is somewhat interesting but not really germane to the topic so I will bow out now...

    Greg
    Line and Load. Load goes to other outlets. Line goes back up the chain to the source. This is most important when working with GFCI outlets.

    I have no idea what a "mar connector" is.

    Pete

  8. #53
    Join Date
    Nov 2006
    Location
    Vancouver, BC
    Posts
    858
    Quote Originally Posted by Brian Tuftee
    Only if they're 120V, 15A or 20A receptacles. Local codes may be more strict, but the NEC doesn't require GFCI protection on 240V general-use receptacles. Or on 120V receptacles at 30A or above.


    Greg:
    I don't think you can plug normal 15A plugs into that 30A receptacle you have pictured. This website has a good description of the various NEMA plug and receptacle configurations, and I don't see anything in 120V, 30A that mates with 'standard' 15A (or 20A) plugs.
    http://www.stayonline.com/reference-...ght-blade.aspx
    Well I don't have one in front of me but I was pretty sure you could plug a 15A plug into a 15A or a 20A receptacle and it looks like it would fit in a 30A receptacle as well.

  9. #54
    Join Date
    Nov 2006
    Location
    Vancouver, BC
    Posts
    858
    Quote Originally Posted by Pete Brown
    I have no idea what a "mar connector" is.

    Pete
    An incorrectly spelled trade name. In Canada it is common to use "Marr" or "Marrette" connectors for twisting wires together. Not sure what they use in the US.
    Attached Images Attached Images

  10. #55
    Join Date
    Jan 2007
    Location
    Gambrills, MD - Near Annapolis
    Posts
    556
    Quote Originally Posted by Greg Funk
    An incorrectly spelled trade name. In Canada it is common to use "Marr" or "Marrette" connectors for twisting wires together. Not sure what they use in the US.
    Ahh. We call them "wire nuts" down here

    Those show up in the boxes, for sure. Most outlets are wired through, though.

    Pete

  11. #56
    Join Date
    Dec 2006
    Location
    Eastern Iowa
    Posts
    37
    Quote Originally Posted by Greg Funk
    Well I don't have one in front of me but I was pretty sure you could plug a 15A plug into a 15A or a 20A receptacle and it looks like it would fit in a 30A receptacle as well.
    Yep, 15A plugs will fit in a 15A or 20A, 120V receptacle. However, if you look at the holes on the 30A, 120V receptacle closely, you'll see they're not compatible with the 20A or 15A plugs.
    Attached Images Attached Images

  12. #57
    Join Date
    Dec 2005
    Location
    Du Bois, PA
    Posts
    69
    Everyone needs to remember that the Electrical Codes are in place to protect the public from itself. If there is code rule covering an installation there is a history to go along with the rule. If you want to do your own wiring use a book that follows the latest code. The articles in non electrical trade publications are not always by the code, so be careful of these. And remember if you are not sure what to do call an electrician to do the work for you.

Similar Threads

  1. 3 phase 20" Jointer Questions
    By Aaron Mills in forum General Woodworking and Power Tools
    Replies: 13
    Last Post: 04-14-2010, 1:24 PM
  2. More Power Feeder Shaper Mounting Help - Please
    By John Weber in forum General Woodworking and Power Tools
    Replies: 4
    Last Post: 05-28-2007, 3:02 PM
  3. Flex Power Lock Disks vs Velcro Foam Pads for power sanding?
    By Bob Opsitos in forum Turner's Forum
    Replies: 0
    Last Post: 10-21-2006, 8:55 PM
  4. Best Handtools to supplement one's power tools?
    By David Dixson in forum General Woodworking and Power Tools
    Replies: 12
    Last Post: 04-15-2005, 5:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •